SUA3000UXI Configuration

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA3000UXI Configuration
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 12:49 AM . Last Modified: ‎2024-03-11 03:36 AM

0 Likes
3
1050
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:49 AM . Last Modified: ‎2024-03-11 03:36 AM

SUA3000UXI Configuration

Hi Friends
I have sua3000uxi ups in my network with 13 pc with all 15" led monitor load.
My ( 1 ) problem is last day I install 4 x 100ah new battery install ( 48v) Battery is fully charged by company but every morning ups charged from 1 light to last light indication on front panel.

(2 ) problem is on full load front indicator shown only 2 indicator light. I seen in apc-fix & Powerchute software 200w showing In load menu. And my model number is also shown incorrect ( Smart-UPS 3000xl ) but I have SUA-3000Uxi ( is configuration mistake in ups install ? )
Can anyone give me proper calibration constant details for above model

Thx
Prashant Pathak

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:50 AM . Last Modified: ‎2024-03-11 03:36 AM

0 Likes
0
1050
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:50 AM . Last Modified: ‎2024-03-11 03:36 AM

ok, it sounds like you need to do a calibration potentially here.

did you discharge the UPS completely when you did your test?

a manual calibration requires at least 30% of stable load that does not fluctuate more than 5% and any communication cables to the serial or USB ports should be removed. let the UPS run like this until it turns off (assuming you start with a full charge), and check the results.

It seems like though this could potentially go for several hours..

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:49 AM . Last Modified: ‎2024-03-11 03:36 AM

0 Likes
0
1050
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:49 AM . Last Modified: ‎2024-03-11 03:36 AM

hello.

1.) what types of batteries are connected to this system? are these APC batteries or third party? was the battery bar graph indicator full previously? do these batteries have any communication to the UPS?

2.) the model is correct with Smart UPS 3000 XL. The Network Management Card or PowerChute cannot report the exact model. Yours is a 3000VA XL model so no problem there. this also cannot be modified.

what is apc-fix? also, how do you know it is on full load when the indicator only shows 2 bars? how do we know the UPS is not reporting correctly? Did it used to?

how old is this system by the way?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:50 AM . Last Modified: ‎2024-03-11 03:36 AM

0 Likes
0
1050
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:50 AM . Last Modified: ‎2024-03-11 03:36 AM

thx for reply

1. This is exide make 100ah new 4 Nos battery.
2. My Model is SUA3000UXI
3. Yes battery bar graph indicator full after i charged 2 hrs in morning ( every morning ).
4. Demo apc fix prog is develop by programmer for check your APC status ( Battery backup time, input-output voltage, Model No. Etc... )
5. My Apc is 3 year old.

sir my problem is i need exactly backup time after Ups on Battery Backup. I have attached 17 systems with 15” Led monitor.
When I checked is always show 1685 Min remaining and after on backup it shown 5min left but still running more than hour on full load

please see attached image file


thanking You

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:50 AM . Last Modified: ‎2024-03-11 03:36 AM

0 Likes
0
1051
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:50 AM . Last Modified: ‎2024-03-11 03:36 AM

ok, it sounds like you need to do a calibration potentially here.

did you discharge the UPS completely when you did your test?

a manual calibration requires at least 30% of stable load that does not fluctuate more than 5% and any communication cables to the serial or USB ports should be removed. let the UPS run like this until it turns off (assuming you start with a full charge), and check the results.

It seems like though this could potentially go for several hours..

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore