SUA3000RMXL3U and AP9617

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA3000RMXL3U and AP9617
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:36 AM . Last Modified: ‎2024-03-14 12:39 AM

0 Likes
7
1377
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:36 AM . Last Modified: ‎2024-03-14 12:39 AM

SUA3000RMXL3U and AP9617

Hello All,

I have a client who has several AP9617 management cards and wish to use them in new (year old) SUA3000s. I checked APC's site and it mentions the AP9617 is discontinued. My recollection is the card did work in the older SUA3000s, but am not sure if it will work in this model (noted in subject).

Please let me know if it will work, or if APC has made changes to the internal of the UPS that will negate the operation of the card.

TIA.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 3000
  • ap9617
  • card
  • management
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:36 AM . Last Modified: ‎2024-03-14 12:39 AM

0 Likes
0
1377
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:36 AM . Last Modified: ‎2024-03-14 12:39 AM

Thanks all.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:36 AM . Last Modified: ‎2024-03-14 12:39 AM

0 Likes
0
1377
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:36 AM . Last Modified: ‎2024-03-14 12:39 AM

You are welcome.

For your kind of UPS, we strongly suggest that you perform the braindead procedure. To do the procedure you need to turn the unit off, unplug it from the wall and then press and hold the off button until you hear a click or the LED's flash on the UPS. After doing this you are now free to install/ remove the card.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:36 AM . Last Modified: ‎2024-03-14 12:39 AM

0 Likes
0
1376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:36 AM . Last Modified: ‎2024-03-14 12:39 AM

Leo,

Yes you are correct, the APC NMC AP9617 and AP9619 are already discontinued has been replaced with newer cards. But these kind of cards would still work with the UPS that you have mentioned from your post.

We now have a new set of network management cards that can be used on old UPS models like yours and with the latest Smart-UPS that we have the SMX and SMT units.

JonPro

Message was edited by: JonPro

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:36 AM . Last Modified: ‎2024-03-14 12:39 AM

0 Likes
0
1376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:36 AM . Last Modified: ‎2024-03-14 12:39 AM

AP9617 will still work in both of the UPSs that you mentioned without problem. When you install them, it may be a good idea to find and download the latest firmware version available on the website for Smart UPS, part number SFSUMX372.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:36 AM . Last Modified: ‎2024-03-14 12:39 AM

0 Likes
0
1377
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:36 AM . Last Modified: ‎2024-03-14 12:39 AM

if you need to schedule it instead, you can just hot swap the card in there if its going to cause you downtime. the procedure JonPro mentioned is preferred but most likely nothing will happen - the manufacture date of the UPS and the card does not matter - the two will work fine together.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:36 AM . Last Modified: ‎2024-03-14 12:39 AM

0 Likes
0
1377
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:36 AM . Last Modified: ‎2024-03-14 12:39 AM

Hello All,

I have a client who has several AP9617 management cards and wish to use them in new (year old) SUA3000s. I checked APC's site and it mentions the AP9617 is discontinued. My recollection is the card did work in the older SUA3000s, but am not sure if it will work in this model (noted in subject).

Please let me know if it will work, or if APC has made changes to the internal of the UPS that will negate the operation of the card.

TIA.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:36 AM . Last Modified: ‎2024-03-14 12:39 AM

0 Likes
0
1377
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:36 AM . Last Modified: ‎2024-03-14 12:39 AM

Thanks JonPro.

Looks like this will need to be scheduled.

Best regards.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:36 AM . Last Modified: ‎2024-03-14 12:39 AM

0 Likes
0
1378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:36 AM . Last Modified: ‎2024-03-14 12:39 AM

Thanks all.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore