SUA3000RMXL3U No Capacity after battery replacement
Hello!
I have a SUA3000RMXL3U with 1 external battery pack. All 3 batteries were replaced this week. When I run a self test or a runtime calibration the battery capacity immediately drops to 0%. Seems like I may need to do the battery constant update but I can't find the number I need for this model. Is it possible to get this 'use at your own risk' number?
Thanks!
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:15 PM . Last Modified: 2024-03-01 12:05 AM
Yup - the network management card is on the same communication bus, and tends to go "Hey! That's my job! Stop!" if you try to talk to the UPS while the card is installed.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:15 PM . Last Modified: 2024-03-01 12:05 AM
You can use '89' as the value without the '. And yes, at your own risk. And don't forget to jot down what the value was prior as a backup.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:15 PM . Last Modified: 2024-03-01 12:05 AM
Thanks Angela.
I'm connected to the UPS but I can't seem to get it to do what I need it to, any ideas?
Y
Returns SM
1 (wait 3-4 seconds)
1
Returns nothing... I should get PROG I think?
Thanks! (Of course, use at my own risk...) 😉
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:15 PM . Last Modified: 2024-03-01 12:05 AM
Nevermind, I got it...
I skipped the part that said remove the network management card. 🙂
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:15 PM . Last Modified: 2024-03-01 12:05 AM
Yup - the network management card is on the same communication bus, and tends to go "Hey! That's my job! Stop!" if you try to talk to the UPS while the card is installed.