SUA2200RM2U and Windows 10

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA2200RM2U and Windows 10
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 12:33 AM . Last Modified: ‎2024-03-11 04:03 AM

0 Likes
4
1303
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:33 AM . Last Modified: ‎2024-03-11 04:03 AM

SUA2200RM2U and Windows 10

I have 16 SUA2200RM2U UPS’s that used to be connected to 1996 vintage Windows 2000 computers running an unknown version of PowerChute PE. It is a serial port connection running through an A9830 UPS Remote Shutoff Device. Also installed is an AP9610 Relay I/O Module.

Now my issue is an upgrade to new computer hardware running Windows 10. The new computer does have a serial port and I would still like to use that so I don’t have to upgrade the accessories to use USB. An outside contractor did the computer upgrade but never installed anything for the APC connection. I’ve tried numerous versions of the PE software from the download site, but so far haven’t been able to get past the required .NET 2.0 warning even though .NET 4.7.1 is installed which Microsoft says is backwards compatible.

What I need to know is what PowerChute Software do I need to make the equipment work again? This shouldn’t be this hard.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:33 AM . Last Modified: ‎2024-03-11 04:02 AM

0 Likes
0
1301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:33 AM . Last Modified: ‎2024-03-11 04:02 AM

Hi,

If you want to use the Serial cable with the SUA you need cable 940-0024. The cable must be connected to the computer and the UPS when PowerChute is installed. If you have install PowerChute previously using USB you must uninstall PowerChute, brain dead the SUA (see Schneider Electric FAQ FA156611) then install with the cable attached.

As for Firefox, that is a really old version. Firefox is now distributing version 60. Being such an old version may explain why you are seeing the SSL errors.

If after a clean install you still see the service control dispatch error open the control panel go to Administrative Tools, Services, and open APC PBE Agent. change the Startup type form Automatic to Automatic (delayed Start) and then reboot the system. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:33 AM . Last Modified: ‎2024-03-11 04:02 AM

0 Likes
0
1301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:33 AM . Last Modified: ‎2024-03-11 04:02 AM

Hi,

PowerChute Personal Edition is compatible with Back-UPS not SUA Smart-UPS. The version of PowerChute for a SUA Smart-UPS is PowerChute Business Edition. PowerChute Business Edition with communicate with a SUA either serially or via USB. 

You can download PowerChute Business Edition from this link  http://www.apc.com/shop/us/en/categories/power/uninterruptible-power-supply-ups-/ups-management/powe...

I recommend you download and read the User's Guide. For your unit you will need User's Guide for type B Smart-UPS. The User's Guide will be found under Manuals and Warranties. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:33 AM . Last Modified: ‎2024-03-11 04:02 AM

0 Likes
0
1301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:33 AM . Last Modified: ‎2024-03-11 04:02 AM

Thanks Bill. That installed a lot better. The install is not able to locate the UPS however, but I'm suspecting that it's the hardware. I'm inclined to think the DB-9 port on the back of the computer is USB emulated and the UPS isn't liking that, but I'll have to research that a bit more. Unfortunately we weren't given the hardware configuration for these new computers so I'm going to have to crack a cover and take a look inside.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:33 AM . Last Modified: ‎2024-03-11 04:02 AM

0 Likes
0
1301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:33 AM . Last Modified: ‎2024-03-11 04:02 AM

I gave up trying to get the DB-9 serial port to work for now since the computer does recognize the UPS when connected with the USB cable and it installs the Agent. However, there are multiple issues. What I have installed is:

  • Windows 10 Enterprise LTSB Build 1607
  • Microsoft .NET Ver 4.7.1
  • Firefox Ver 26.0.0.5087 ( I realize the Firefox is old but it was what was installed for use with the primary application)
  • PowerChute Business Edition Agent Ver 9.5.0.0

If I try connecting locally as the manual describes, I get an error

Secure Connection Failed

An error occurred during a connection to localhost:6547

Can not communicate securely with peer: no common encryption algorithm(s)

(Error code ssl_error_no_cypher_overlap)

The service appears to to be installed but when I try to restart it I get an error message from the APC PBE Agent:

StartServiceControlDispatcher failed!

Everything was installed and run signed in as Administrator. I'm not familiar enough with PowerChute to know what the issue is. Some help would be much appreciated,

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:33 AM . Last Modified: ‎2024-03-11 04:02 AM

0 Likes
0
1302
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:33 AM . Last Modified: ‎2024-03-11 04:02 AM

Hi,

If you want to use the Serial cable with the SUA you need cable 940-0024. The cable must be connected to the computer and the UPS when PowerChute is installed. If you have install PowerChute previously using USB you must uninstall PowerChute, brain dead the SUA (see Schneider Electric FAQ FA156611) then install with the cable attached.

As for Firefox, that is a really old version. Firefox is now distributing version 60. Being such an old version may explain why you are seeing the SSL errors.

If after a clean install you still see the service control dispatch error open the control panel go to Administrative Tools, Services, and open APC PBE Agent. change the Startup type form Automatic to Automatic (delayed Start) and then reboot the system. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of