SUA2200 reporting it a Smart-UPS 500 and 24volt not 48volt

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA2200 reporting it a Smart-UPS 500 and 24volt not 48volt
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:27 AM . Last Modified: ‎2024-03-12 03:41 AM

0 Likes
1
830
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:27 AM . Last Modified: ‎2024-03-12 03:41 AM

SUA2200 reporting it a Smart-UPS 500 and 24volt not 48volt

SUA2200 reporting it a Smart-UPS 500 and 24volt not 48volt,

below unit 1 is working fine ,, unit 2 is reporting it's a ups500

seems to be a logic prob, inverter fuction working on battery

wont switch to line reporting no volts (false)

i can't seem to change voltage with g +- in terminal

or model string with ^A +- in treminal, z no effect

sorry using linux no  powershute

is there a key combo in terminal

to change model string back to Smart-UPS 2200 ??

   sorry or the long post

[UNIT 1 sua2200] working fine

UPS Status: 08

Line quality: FF

Reason for last transfer to batteries: S

Self-Test Status: NO

Line Voltage: 122.4

Line Voltage Max: 122.4

Line Voltage Min: 121.6

Output Voltage: 122.4

Batt level percent: 100.0

Batt voltage: 55.35

UPS Load: 000.0

Line freq: 60.00

Runtime left: 0095

UPS Internal temp: 016.6

Dip switch settings: NA

Register 1: 00

Register 2: 00

Register 3: 00

Sensitivity: H

Wakeup delay: 000

Sleep delay: 090

Low transfer voltage: 106

High transfer voltage: 127

Batt charge for return: 00

Alarm status: 0

Low battery shutdown level: 02

UPS Name: 2200_1

UPS Self test interval: 336

UPS manufacture date: 11/16/04

UPS serial number: JS0447004854

Date battery replaced: 11/16/04

Output voltage when on batteries: 120

Nominal battery voltage: 048

Percent humidity: NA

Ambient temperature: NA

Firmware revision: 654.12.D

Number of external batteries installed: 000

Number of bad batteries installed: NA

UPS model as defined by UPS: Smart-UPS 2200

UPS EPROM capabilities string: uD43127130133136uA43108110112114uI43253257261265uM43225229233237lD43106103100097lA43092090088086lI43208204200196lM43182178174170e47200153045607590oD13120oA13100oI33230240220oM13208s431HMLq4820205081114172023p483090180270360450540630000k4310TNr483000060120180240300360420E443336168ON OFF

The EPROM string is 286 characters long!

---------------------------------------------------------------

[UNIT 2 sua2200] reporting model 500

UPS Status: 10

Line quality: 00

Reason for last transfer to batteries: S

Self-Test Status: OK

Line Voltage: 000.0

Line Voltage Max: 000.0

Line Voltage Min: 000.0

Output Voltage: 120.1

Batt level percent: 031.0

Batt voltage: 23.89

UPS Load: 000.0

Line freq: 60.00

Runtime left: 0029

UPS Internal temp: 013.9

Dip switch settings: NA

Register 1: 00

Register 2: 00

Register 3: 00

Sensitivity: H

Wakeup delay: 000

Sleep delay: 090

Low transfer voltage: 106

High transfer voltage: 127

Batt charge for return: 00

Alarm status: 0

Low battery shutdown level: 02

UPS Name:

UPS Self test interval: 336

UPS manufacture date:

UPS serial number:

Date battery replaced:

Output voltage when on batteries: 120

Nominal battery voltage: 024

Percent humidity: NA

Ambient temperature: NA

Firmware revision: FWD

Number of external batteries installed: 000

Number of bad batteries installed: NA

UPS model as defined by UPS: Smart-UPS 500

UPS EPROM capabilities string: uD43127130133136uA43108110112114uI43253257261265uM43225229233237lD43106103100097lA43092090088086lI43208204200196lM43182178174170e47200153045607590oD13120oA13100oI33230240220oM13208s431HMLq4820205081114172023p483090180270360450540630000k4310TNr483000060120180240300360420E443336168ON OFF


Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:27 AM . Last Modified: ‎2024-03-12 03:41 AM

0 Likes
0
829
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:27 AM . Last Modified: ‎2024-03-12 03:41 AM

This is outside the scope of APC/Schneider Electric Technical support but if anyone else wants to chime in and help and provide instructions to use at their own risk, please feel free to do so.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:27 AM . Last Modified: ‎2024-03-12 03:41 AM

0 Likes
0
830
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:27 AM . Last Modified: ‎2024-03-12 03:41 AM

This is outside the scope of APC/Schneider Electric Technical support but if anyone else wants to chime in and help and provide instructions to use at their own risk, please feel free to do so.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore