SUA1500i - shuts down without apperent reason

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA1500i - shuts down without apperent reason
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:31 PM . Last Modified: β€Ž2024-03-15 12:26 AM

0 Likes
7
1358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:31 PM . Last Modified: β€Ž2024-03-15 12:26 AM

SUA1500i - shuts down without apperent reason

Hi,

We have two SMART UPSs in our lab. The problem is that both of them behave strange. Sometimes they just shut themselves down without apparent reason and following LEDs on the left are blinking: AVR TRIM, ON-LINE, AVR BOOST and all 5 LOAD LEDS. The ups then needs to be reset by switching it off and back on again.

Sometimes this fault occurs after short power cut but not always. It is worth mentioning that UPS runs on 3/4 load so it is not overloaded.

I'm not using powershute because I don't have any COM and USB port free.

Please help me with this issue as it is very important for our research to have uninterrupted measurements.

ps. I cant provide serial numbers as yet but both units are still on warranty.

Message was edited by: liko

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:31 PM . Last Modified: β€Ž2024-03-14 11:52 PM

0 Likes
0
1358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:31 PM . Last Modified: β€Ž2024-03-14 11:52 PM

Hi again,

I'm at the site now and, unfortunately, the procedure with brain-dead and cold start didn't help...I have noticed the following thing: When I simulate power cut the UPS goes to battery. The battery level goes down at a rate of one led per 20-30 seconds. Load indicator shows 3 out of 5 leds. Then after around 30 seconds the UPS shuts itself down with above mentioned leds flashing.

I really don't know what might be the cause of it....It isn't overloaded, is it?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:31 PM . Last Modified: β€Ž2024-03-15 12:26 AM

0 Likes
0
1358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:31 PM . Last Modified: β€Ž2024-03-15 12:26 AM

But the same problem with two separate units?? Can it be that it is just overloaded despite the led indicator showing otherwise? I don't have new batteries, the units are out-of-the-box new. And if I open it won't I void the warranty?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:31 PM . Last Modified: β€Ž2024-03-15 12:26 AM

0 Likes
0
1358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:31 PM . Last Modified: β€Ž2024-03-15 12:26 AM

Could you elaborate on this DC imbalance for us curious people?

Thanks,
Stew

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 09:31 PM . Last Modified: β€Ž2024-03-15 12:26 AM

0 Likes
0
1358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:31 PM . Last Modified: β€Ž2024-03-15 12:26 AM

hm, okay sounds like something related to the DC imbalance i was mentioning. it COULD be related to the batteries so do you have a spare set you can swap in before you buy new batteries? it may be also the unit but you could try spare batteries first.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 09:31 PM . Last Modified: β€Ž2024-03-14 11:52 PM

0 Likes
0
1358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:31 PM . Last Modified: β€Ž2024-03-14 11:52 PM

Hi,

It might be best to monitor these UPSs via software so that we can see exactly what is going on.

As far as your configuration right now, even though you are not using any of our software, do you have the serial cable connected at the UPS end?

Are both of these Smart-UPS entering this state at the same time? or Randomly?

Are these units plugged in directly to its own dedicated outlet? Directly to the wall or a power strip?

I would also recommend that you perform a braindead and coldstart procedure just so that we can eliminate any hiccups that the UPS is currently exhibiting.

BrainDead
-turn off the UPS
-unplug the UPS
-Press and hold the off button/circle button. (o) for about 3-8 seconds until you hear it click.

This will set the unit to a default state.

ColdStart
-after doing the BrainDead Procedure, press and hold the On button. You will hear a short beep, follow by a secondary longer beep. As soon as you hear the secondary long beep please release. The unit will boot up from its internal battery power and go to battery.

Once it is on battery you can plug the UPS in to introduce utility power. The unit will go back online.

Hope this helps πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:31 PM . Last Modified: β€Ž2024-03-14 11:52 PM

0 Likes
0
1358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:31 PM . Last Modified: β€Ž2024-03-14 11:52 PM

Thanks for reply πŸ™‚

1. No, I don't have any cable attached to COM port of the UPS now since I don't have any ports free in my computer.
2. I haven't used them simultaneously. I just swapped one with another when I noticed the problem. And they switch off randomly.
3. The UPS is connected directly to the mains. Would it make any difference if it was connected to the extension instead?

I will try the BrainDead πŸ˜„ procedure followed up by the cold start. Then I will wait for the problem to appear again (I hope it won't...). It can run for weeks without problems and then the issue can appear several times a week. I will try to simulate power failure by switching the breaker of the mains off and we will see what will happen.

BTW: have you heard about similar problems with SMART UPSs so far?

Thanks

Message was edited by: liko

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 09:31 PM . Last Modified: β€Ž2024-03-14 11:52 PM

0 Likes
0
1358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:31 PM . Last Modified: β€Ž2024-03-14 11:52 PM

one thing i just came across indicates this may be a DC imbalance on the unit.

definitely try that brain dead procedure to see if it clears up and i would maybe just double check and see what the battery voltage is if you can. you'd have to use a voltmeter i guess since you dont have the software available. the batteries are hot swappable so if you remove them to double check the voltage, the replace battery LED will flash when you remove them and obviously you dont have any battery back up time with the batteries connected. we could make sure there isnt something strange with the battery voltage but i am not sure.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:31 PM . Last Modified: β€Ž2024-03-14 11:52 PM

0 Likes
0
1359
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:31 PM . Last Modified: β€Ž2024-03-14 11:52 PM

Hi again,

I'm at the site now and, unfortunately, the procedure with brain-dead and cold start didn't help...I have noticed the following thing: When I simulate power cut the UPS goes to battery. The battery level goes down at a rate of one led per 20-30 seconds. Load indicator shows 3 out of 5 leds. Then after around 30 seconds the UPS shuts itself down with above mentioned leds flashing.

I really don't know what might be the cause of it....It isn't overloaded, is it?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore