Hi all,
on my SUA1500I I replaced the battery (fully functional) is due to the following problem;
even though the battery charged to 100%, in the absence of 220 volt UPS does not properly handle continuity '.
In practice, despite new battery APC RBC7, with a load of 200 watts (about) in the absence of 220V the battery drops of 80/90% in about 2 minutes.
Recommended thing to do for this problem?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:39 AM . Last Modified: 2024-03-12 03:28 AM
Hello,
Did you translate this by chance? because I am not sure I understand what "even though the battery charged to 100%, in the absence of 220 volt UPS does not properly handle continuity" means - was this a translated event from PowerChute or a Network Management Card?
It is possible that the UPS just needs to be calibrated to appropriately update the on battery runtime and also to operate properly during a power failure.
Have you done a calibration at all yet? There are instructions here to help with that - you could try a manual runtime calibration and let the UPS turn off fully and charge back up -> Why are the battery charge LEDs flashing on a Smart-UPS? | FAQs | Schneider Electric US (perhaps you also do see the battery charge LEDs flashing?)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:39 AM . Last Modified: 2024-03-12 03:28 AM
Hello,
Did you translate this by chance? because I am not sure I understand what "even though the battery charged to 100%, in the absence of 220 volt UPS does not properly handle continuity" means - was this a translated event from PowerChute or a Network Management Card?
It is possible that the UPS just needs to be calibrated to appropriately update the on battery runtime and also to operate properly during a power failure.
Have you done a calibration at all yet? There are instructions here to help with that - you could try a manual runtime calibration and let the UPS turn off fully and charge back up -> Why are the battery charge LEDs flashing on a Smart-UPS? | FAQs | Schneider Electric US (perhaps you also do see the battery charge LEDs flashing?)