SUA1500I power supply
Hi all,
on my SUA1500I I replaced the battery (fully functional) is due to the following problem;
even though the battery charged to 100%, in the absence of 220 volt UPS does not properly handle continuity '.
In practice, despite new battery APC RBC7, with a load of 200 watts (about) in the absence of 220V the battery drops of 80/90% in about 2 minutes.
Recommended thing to do for this problem?
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:39 AM . Last Modified: 2024-03-12 03:28 AM
Hello,
Did you translate this by chance? because I am not sure I understand what "even though the battery charged to 100%, in the absence of 220 volt UPS does not properly handle continuity" means - was this a translated event from PowerChute or a Network Management Card?
It is possible that the UPS just needs to be calibrated to appropriately update the on battery runtime and also to operate properly during a power failure.
Have you done a calibration at all yet? There are instructions here to help with that - you could try a manual runtime calibration and let the UPS turn off fully and charge back up -> Why are the battery charge LEDs flashing on a Smart-UPS? | FAQs | Schneider Electric US (perhaps you also do see the battery charge LEDs flashing?)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:39 AM . Last Modified: 2024-03-12 03:28 AM
Hello,
Did you translate this by chance? because I am not sure I understand what "even though the battery charged to 100%, in the absence of 220 volt UPS does not properly handle continuity" means - was this a translated event from PowerChute or a Network Management Card?
It is possible that the UPS just needs to be calibrated to appropriately update the on battery runtime and also to operate properly during a power failure.
Have you done a calibration at all yet? There are instructions here to help with that - you could try a manual runtime calibration and let the UPS turn off fully and charge back up -> Why are the battery charge LEDs flashing on a Smart-UPS? | FAQs | Schneider Electric US (perhaps you also do see the battery charge LEDs flashing?)
Link copied. Please paste this link to share this article on your social media post.