SUA1000i Battery disconnected error (Update: New battery overheated)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA1000i Battery disconnected error (Update: New battery overheated)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:24 AM

0 Likes
15
5699
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:24 AM

SUA1000i Battery disconnected error (Update: New battery overheated)

I was woken up by the bleeping of my APC Smart-UPS 1000va SUA1000i. It suddenly indicates that the battery is disconnected. (Replace battery LED blinks and the unit keeps beeping) I opened up the unit to check the battery connections but they are firmly attached. The unit fails to charge now but it detects that there still is some load in the battery. (around 12%)

When I pull the power cord the unit shuts down immediately. The battery connector on the rear of the unit is connected. What is wrong here and how do I solve it?

Update: The new battery, less than a month old, became very hot and failed. (See under)

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery
  • disconnected_battery_message
  • smart-ups
  • sua1000i
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:55 PM . Last Modified: ‎2024-03-11 04:23 AM

0 Likes
0
5692
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:55 PM . Last Modified: ‎2024-03-11 04:23 AM

You're very welcome! smile

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 15
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:24 AM

0 Likes
0
5693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:24 AM

The issue just returned. I noticed the battery disconnect LED was blinking red. I opened the UPS and noticed the unit was very warm. The (new) batteries are very hot to touch (Cannot touch them for a longer time) and making a slight hissing sound.

Update: The battery in the behind position is quite a bit hotter then the other one. It may be possible that only one of the two batteries (the behind one) actually produced all the heat.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:24 AM

0 Likes
0
5693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:24 AM

Where did you get it from?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:24 AM

0 Likes
0
5693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:24 AM

From an online retailer: (Max ICT)

APC REPLACABLE BATTERY RBC6 - Max ICT

It has a label on it: RBC6-OEM-130311

The individual batteries are these ones:

http://www.powertec-energy.de/WebRoot/Store4/Shops/15514666/4EC5/188E/CEDD/0BD1/84A2/C0A8/28B9/4536/...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:24 AM

0 Likes
0
5693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:24 AM

if it is a genuine APC RBC battery, these have a one year warranty is why I ask if it is already heating up and failed. If it is, it should have an APC serial number on it.

I am not sure if it is a genuine battery as I have never heard of that vendor but the serial number would be on the box or the battery you received.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:24 AM

0 Likes
0
5692
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:24 AM

It does not appear to be genuine APC then. It was advertised as one but it does not have any APC brand labels on it. The box does not have a serial number.

The label on the box reads:

RBC6-OEM

Ersatsbatterie für USV System

BP1000I, SUVS1000I, SU1000INET, SUA1000I, SU1000RMINET, IBMR1000I

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:24 AM

0 Likes
0
5692
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:24 AM

Did my UPS turn into a battery killing machine?

The new battery was very hot and hissing. Was it being overcharged?

Or was the new battery faulty?

Now I have two battery sets that are detected with a red "battery disconnect" LED.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:24 AM

0 Likes
0
5692
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:24 AM

If one (or both) of the 12 volt cells in the battery module (RBC 6 equivalent) developed an premature internal short / or breakdown, the UPS'

battery charging circuits may have abnormally high current pulled from them by the battery module and it would indeed heat up both battery cells as they are in series like old-school christmas lights. The UPS would heat up as well. The hissing sound is caused by gas buildup inside the cells being released - you may  find the batteries have swelled and cracked open. I'd say it sounds like you should return these batteries to the vendor for a refund !!!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:24 AM

0 Likes
0
5692
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:24 AM

I was woken up by the bleeping of my APC Smart-UPS 1000va SUA1000i. It suddenly indicates that the battery is disconnected. (Replace battery LED blinks and the unit keeps beeping) I opened up the unit to check the battery connections but they are firmly attached. The unit fails to charge now but it detects that there still is some load in the battery. (around 12%)

When I pull the power cord the unit shuts down immediately. The battery connector on the rear of the unit is connected. What is wrong here and how do I solve it?

Update: The new battery, less than a month old, became very hot and failed. (See under)

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:24 AM

0 Likes
0
5692
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:24 AM

this can happen for two reasons usually:

  1. the battery is physically disconnected (which you verified)
  2. the battery voltage is so low that the UPS cannot see it attached and believes it is disconnected. this can happen after a deep battery discharge on an older battery.

my questions are - how old is this battery? if it is the original battery, can you give us the first 6 characters of the UPS serial number please to give us an idea on the age? if it is newer, then i'd be concerned that the second reason is the root cause here. it also could be an issue with the charger based on what you've described - perhaps it failed.

do you have any PowerChute software installed and running for monitoring/logging purposes or a Network Management Card installed so we can review log data? i ask because you know the charge percentage is 12% so where did you see that? i'd then be interested in any event logs you have and data logs.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:23 AM

0 Likes
0
5693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:23 AM

I requested an RMA / warranty on the new battery pack and sent it back for replacement.

Still I'm a bit worried about the possibility that the UPS itself may be faulty.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:23 AM

0 Likes
0
5693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:23 AM

The battery is original and has never been replaced so far. My UPS serial number is: AS0843231474.

I currently do not have any PowerChute software in use. The charge percentage is indicated by the Windows 7 battery indicator. When I came home from work I noticed that the UPS is in normal operation state now. At least the LED indicators are normal. But when I pulled the power cord the "battery disconnected" warning appeared again for a short while.

Current state: Plugged in, 91% charge available, charging and counting up.

Update: I pulled the plug again to test and the UPS shut down immediately without supplying power to the system. When I pressed the test button for a few seconds to initiate a self-test it came with a red "Replace battery" LED. (Not blinking this time) The charge percentage plummeted to zero immediately during these actions and it now says "charging" again.

Does replacing the battery fix the conditions I mentioned?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:23 AM

0 Likes
0
5693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:23 AM

It sounds like it, yes. Since its from mid-late 2008, a battery replacement sounds about right. The behavior also indicates that with solid Replace Battery LED. And OK, so you are using Windows 7 OS Native UPS support. Once you get the new battery and install it if you go that route, just give it about 8-10 hours minimum to charge at least so that you can then run another test via the run panel and the test button to clear that replace battery LED as it won't clear on its own.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:23 AM

0 Likes
0
5693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:54 PM . Last Modified: ‎2024-03-11 04:23 AM

Thanks. I ordered a new battery pack for my UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:55 PM . Last Modified: ‎2024-03-11 04:23 AM

0 Likes
0
5693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:55 PM . Last Modified: ‎2024-03-11 04:23 AM

The new battery pack arrived today and the unit is working fine again. Thanks for the support.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:55 PM . Last Modified: ‎2024-03-11 04:23 AM

0 Likes
0
5693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:55 PM . Last Modified: ‎2024-03-11 04:23 AM

You're very welcome! smile

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore