SUA1000i - Battery discharged, insufficient runtime, comms lost etc etc

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA1000i - Battery discharged, insufficient runtime, comms lost etc etc
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:44 AM

0 Likes
6
839
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:44 AM

SUA1000i - Battery discharged, insufficient runtime, comms lost etc etc

One of our SUA1000i UPSs has been reporting some odd things over the past few days. It is connected to a dedicated machine by RS232, and has a total load not exceeding 20%. The UPS is less than a year old, but has not until now exhibited any issues.
Below are the last few log entries:

03/11/09 11:57:16 Insufficient Runtime Available
03/11/09 11:57:16 Battery Discharged
03/11/09 11:57:11 Communication Established
03/11/09 11:57:03 Communication Lost
02/11/09 08:11:43 Communication Established
02/11/09 08:11:34 Monitoring Started
28/10/09 19:29:08 Communication Established
28/10/09 19:29:00 Communication Lost
28/10/09 19:28:29 Battery Charge In Range
28/10/09 19:21:20 Insufficient Runtime Available
28/10/09 19:21:19 Battery Discharged
28/10/09 19:21:14 Communication Established
28/10/09 19:21:07 Communication Lost
28/10/09 09:56:47 Self Test Passed
28/10/09 09:56:39 Self Test Initiated
28/10/09 02:15:51 Sufficient Runtime Available
28/10/09 02:15:43 Insufficient Runtime Available
28/10/09 02:12:34 Sufficient Runtime Available
28/10/09 02:12:26 Insufficient Runtime Available
28/10/09 02:12:18 Sufficient Runtime Available
28/10/09 02:12:10 Insufficient Runtime Available
28/10/09 02:12:02 Sufficient Runtime Available
28/10/09 01:48:36 Battery Charge In Range
28/10/09 01:41:43 Insufficient Runtime Available
28/10/09 01:41:42 Battery Discharged
28/10/09 01:41:37 Communication Established
28/10/09 01:41:18 Communication Lost
26/10/09 15:20:50 Self Test Passed
26/10/09 15:20:35 Self Test Initiated

Thoughts? I'm not far off calling APC tech support, but I thought I'd give the forum a go first.

Thanks

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:44 AM

0 Likes
0
839
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:44 AM

Hi,

Late response, I have been busy.

The UPS has done this again a couple of times. This weekend it returned to "Battery Discharged" and ceased power output without initiating a shutdown sequence at 7:15am this morning. When I went to physically fix the issue, I found the UPS displaying the "Battery Needs Replacing" LED (red) and the top and middle of the battery charge level LEDs (some kind of error code?).
It has therefore been branded unreliable and taken out of service - we aren't in the habit of using equipment which turns our servers off at its will.

We have loads of cables, however in light of the above, I don't see how it is any longer relevant. The same applies for installing the latest version of PCBE although I will look into it as a matter of course now I know it exists!

Going to call support now...

Thanks.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:44 AM

0 Likes
0
839
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:44 AM

This situation can occur when the runtime remaining is at or close to the Low Battery Signal Time. What was the runtime and battery capacity when the Insufficient Runtime event was recorded? Could you please let us know the serial number of the UPS? Were the battery bar lights flashing at the right side of the UPS when this occurred? And also let us know the following details:

Version of the Power Chute
Operating System
What is the UPS runtime showing on Power Chute?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:44 AM

0 Likes
0
839
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:44 AM

Hi,

Thanks for your response.

The runtime remaining while in the "battery discharged/insufficient runtime" state was either 0 or 1 minute. However, it has now returned to a normal state and reports 73 minutes.
The serial number is AS0840121367
I'm afraid I cannot say how the LEDs on the UPS responded as the unit is at a remote site. This is not something which I will be able to check, as this fault is intermittent.

PCBE V7.0.5, XP SP3, 73 minutes as mentioned above!

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:44 AM

0 Likes
0
839
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:44 AM

Was there a Power Failure before this event? Could you please check the data logs and check if there were power failures before these events?

Secondly, you may check the below K-base document which addresses this issue.
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=2819

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:44 AM

0 Likes
0
839
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:44 AM

No power failures, though there have been several instances of overvoltage and subsequent AVR trimming.

I have read the KB article listed:

UPS load is not above 70% and runtime IS accurately reflected.

This leaves us with requiring a larger UPS (I think this only applies if the load is over 70%...), A new battery (for a 9 month old UPS?) or an issue with firmware...

Any more ideas before I contact support?

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:44 AM

0 Likes
0
839
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:44 AM

Rob,

I believe that the UPS and the battery are fine as the runtime is accurately reflected. Are you still getting the same insufficient runtime messages from the Power Chute? If possible, could you please post the recent data and event logs which was recorded by the Power Chute software? Do you have another 940-0024 or 1524 cable? If so, please change the cable and see if it works fine.

Secondly, please upgrade the PCBE software to the latest version and see if that makes difference.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:44 AM

0 Likes
0
840
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:44 AM

Hi,

Late response, I have been busy.

The UPS has done this again a couple of times. This weekend it returned to "Battery Discharged" and ceased power output without initiating a shutdown sequence at 7:15am this morning. When I went to physically fix the issue, I found the UPS displaying the "Battery Needs Replacing" LED (red) and the top and middle of the battery charge level LEDs (some kind of error code?).
It has therefore been branded unreliable and taken out of service - we aren't in the habit of using equipment which turns our servers off at its will.

We have loads of cables, however in light of the above, I don't see how it is any longer relevant. The same applies for installing the latest version of PCBE although I will look into it as a matter of course now I know it exists!

Going to call support now...

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of