Connecting USB-to-Serial cable to UPS SUM1500RMXL2U shutdown UPS?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Connecting USB-to-Serial cable to UPS SUM1500RMXL2U shutdown UPS?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:44 AM

0 Likes
12
2522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:44 AM

Connecting USB-to-Serial cable to UPS SUM1500RMXL2U shutdown UPS?

We have UPS deployment going on right now. We are asking the tech to go to branch offices to install UPS SUM1500RMXL2U and configure the UPS with IP address. We ask the tech to bring laptop with serial port or use USB-to-Serial cable to connect to UPS to configure IP address.

I receive report from some tech stating that when they connect USB-to-Serial cable to UPS, the UPS goes offline. I connect USB-to-Serial cable to couple UPS in my office and I can configure the IP address just fine.

Anyone knows what may causing the UPS goes offline when USB-to-Serial cable is being used to configure IP address?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:43 AM

0 Likes
0
2522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:43 AM

the USB-to-Serial cable is not APC cable.* and you are correct about the USB end connect to PC and the Serial end connec to Serial port on UPS.

Laptop these days no longer has built-in Serial port so we connect USB-to-Serial cable to laptop and connect the APC Serial cable on the other end. I don't know what USB-to_RJ45 cable that come with UPS use for.

On the manual, one of the option to configure UPS with IP is to connect UPS to network that provide DHCP. However I never have success in doing that. I was told that after 3 times unsuccessful attempt to obtain IP address, the UPS is locked and the IP can only be configured using Serial cable?

Please let me know if you guys have suggestion to configure UPS IP rather than using Serial cable.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:44 AM

0 Likes
0
2522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:44 AM

We have UPS deployment going on right now. We are asking the tech to go to branch offices to install UPS SUM1500RMXL2U and configure the UPS with IP address. We ask the tech to bring laptop with serial port or use USB-to-Serial cable to connect to UPS to configure IP address.

I receive report from some tech stating that when they connect USB-to-Serial cable to UPS, the UPS goes offline. I connect USB-to-Serial cable to couple UPS in my office and I can configure the IP address just fine.

Anyone knows what may causing the UPS goes offline when USB-to-Serial cable is being used to configure IP address?

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:44 AM

0 Likes
0
2522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:44 AM

Indo,

APC recommends to use to use the 940-0024C or 1524C cable. Never use a different cable or USB to Serial cable. Doing so can result in the UPS turning off or rebooting. The configuration cable is wired specifically to the pinouts of the UPS’ serial port.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:43 AM

0 Likes
0
2523
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:43 AM

the USB-to-Serial cable is not APC cable.* and you are correct about the USB end connect to PC and the Serial end connec to Serial port on UPS.

Laptop these days no longer has built-in Serial port so we connect USB-to-Serial cable to laptop and connect the APC Serial cable on the other end. I don't know what USB-to_RJ45 cable that come with UPS use for.

On the manual, one of the option to configure UPS with IP is to connect UPS to network that provide DHCP. However I never have success in doing that. I was told that after 3 times unsuccessful attempt to obtain IP address, the UPS is locked and the IP can only be configured using Serial cable?

Please let me know if you guys have suggestion to configure UPS IP rather than using Serial cable.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:43 AM

0 Likes
0
2522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:43 AM

Hi JonPro,

How can I reset NMC back to factory default configuration if I don't know what IP address setup on the NMC?

Thanks,
Indo

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:43 AM

0 Likes
0
2522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:43 AM

Indo Manna,

Yes you are correct, 940-0024 and 940-1524 are APC Smart Signaling Cables Serial-to-Serial. We have the same UPS here in the laboratory and looking on it, the UPS does have a Serial and a USB port but it looks like an RJ-45 port.

You've mentioned that they've used USB-to-Serial, I guess the Serial goes to the UPS and the USB goes into the PC. Are these APC cables as well? To check if this is an APC cable it should either have 940-0272 or AP9833 on it.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:43 AM

0 Likes
0
2522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:07 PM . Last Modified: ‎2024-03-14 03:43 AM

Indo,

The USB-to-RJ45 cable that came with the unit is the one that you'll be using in the event that you want to use USB instead of Serial. Quick question, did they tried using this cable to communicate with the UPS? If they did, advise them to perform a braindead on the UPS I'll provide the link on how to do a braindead below. If you can't tell if they did use this cable I suggest that you perform the braindead and then try to re-establish communication with the card.

Going back to the network management card issue, I believe the UPS comes with an AP9619. Where you able to get the MAC address of the card, if you have it you can try using ARP to set an IP address on it. Regarding DHCP, the default settings of our card looks for a certain cookie or Vendor ID on your DHCP server this is what we call option 43, let me know if you have any knowledge on how to put it so that I can give you the key. Please be advised that if the cable that you're using does not work with our UPS, you'll need to get an APC cable.

There are different ways to configure and set an IP address on our management cards and like what I've said the links are provided below.

APC Knowledge Base Articles
Braindead Procedure -- [Whydoesn't the serial communications work on a Smart-UPS SUA model when USB communications has been tried first?|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=2950]
Configuring an NMC -- [How do you make a Network Management Card communicate on a network?|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=3061]

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:08 PM . Last Modified: ‎2024-03-14 03:43 AM

0 Likes
0
2522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:08 PM . Last Modified: ‎2024-03-14 03:43 AM

Hi JonPro,

Yes. I know option 43 on my DHCP server and I can set that up. Please provide the key and thanks for your help.

Thanks,
Indo

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 11:08 PM . Last Modified: ‎2024-03-14 03:43 AM

0 Likes
0
2522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:08 PM . Last Modified: ‎2024-03-14 03:43 AM

Indo,

You can follow the below K-base document instructions to reset the NMC to its factory defaults.
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=7879

I hope that this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:08 PM . Last Modified: ‎2024-03-14 03:43 AM

0 Likes
0
2522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:08 PM . Last Modified: ‎2024-03-14 03:43 AM

Hello Indo,

I just sent you an e-mail on the address that was on your profile regarding the Option 43 that needs to be set on your DHCP server. Regarding your second question I would like to ask first if you have the ability to access your NMC using either HyperTerminal or PuttY. If you do all you have to do is to login to the NMC and then choose the following options:

Once you are on the control console choose 3 (System) and then 4 (Tools) and then you can choose the following.

2 (Reset to Defaults) --> This option would reset all of the settings on the card
3 (Reset to Defaults except TCP/IP) --> If you choose this and you an IP assigned to the card it will leave the IP settings but will reset the other settings
4 (Reset only TCP/IP to Defaults) --> Only the IP settings will be set to defaults.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:08 PM . Last Modified: ‎2024-03-14 03:43 AM

0 Likes
0
2521
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:08 PM . Last Modified: ‎2024-03-14 03:43 AM

Indo,

There is another way for you to reset it but you need to know what is the IP address of the card since you need to be logged in either thru TelNet or Web interface.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:08 PM . Last Modified: ‎2024-03-14 03:43 AM

0 Likes
0
2521
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:08 PM . Last Modified: ‎2024-03-14 03:43 AM

Thanks, Techie. The cable that you mentioned is the cable that came with the UPS, correct?

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 11:08 PM . Last Modified: ‎2024-03-14 03:43 AM

0 Likes
0
2521
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:08 PM . Last Modified: ‎2024-03-14 03:43 AM

Yes, the cable ships with the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore