Using HP OpenView to monitor UPS SUM1500RMXL2U

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Using HP OpenView to monitor UPS SUM1500RMXL2U
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 11:07 PM . Last Modified: β€Ž2024-03-14 03:44 AM

0 Likes
2
818
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:07 PM . Last Modified: β€Ž2024-03-14 03:44 AM

Using HP OpenView to monitor UPS SUM1500RMXL2U

We are replacing UPS in branch offices with UPS SUM1500RMXL2U. We are going to use HP OpenView to monitor the new UPS.

Any suggestion what to monitor besides monitoring battery status? Is there any documentation regarding what to monitor? I don't want to overwhelm our Help Desk with more alerts than they already receive from other devices but I want to be sure that if the UPS needs attention, we can get to it on-time.

Also is SUM1500RMXL2U battery is hot swappable?

I appreciate your input.

Thanks,

Indo

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: β€Ž2021-06-28 11:07 PM . Last Modified: β€Ž2024-03-14 03:44 AM

0 Likes
0
818
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:07 PM . Last Modified: β€Ž2024-03-14 03:44 AM

You can use HP OpenView to monitor the UPS, as it is SNMP capable. You can route the unit to communicate with any NMS or SNMP agent on a network, or limit to an individual NMS address. You will need our APC MIB (available via our website downloads section, SFPMIB398 is the latest rev.) to allow polling of UPS OID data. You can poll any piece of information that is available in the NMC GUI, and yes this includes battery status, unit status, faults, etc.

I would recommend on deciding what you think is important for a help desk to know, then browse the MIB to find the OIDs for those items.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Techie_apc
Sisko Techie_apc
Sisko

Posted: β€Ž2021-06-28 11:07 PM . Last Modified: β€Ž2024-03-14 03:44 AM

0 Likes
0
818
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:07 PM . Last Modified: β€Ž2024-03-14 03:44 AM

Smart UPS SUM1500RMXL2U UPS does have a pre-installed Network Management Card. By configuring an IP address for the NMC, you can monitor the UPS status such load power draw, UPS runtime, Power Problems event logs, data logs and a lot more...So please login to the NMC web interface to see what all you can monitor πŸ™‚

You may view the NMC demo on APC testdrive web site: [http://testdrive.apc.com/]

More ever, the NMC events can be configured individually. So it is up to you to decide what are the events that you would like to receive from the NMC through email. And also the logs will be stored by the NMC which you can view under event and data logs.

Yes, the SUM1500RMXL2U's Battery Module is hot swappable. This UPS is separated into 3 parts: Battery Module, Power Module, and Chassis. For your information, Power and Battery Modules can be replaced individually and have their own serial numbers. This Unit goes to bypass automatically when power module is removed or when it is faulty. It has 3 User controllable outlet groups that can be power cycled using the network management card interface.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: β€Ž2021-06-28 11:07 PM . Last Modified: β€Ž2024-03-14 03:44 AM

0 Likes
0
819
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:07 PM . Last Modified: β€Ž2024-03-14 03:44 AM

You can use HP OpenView to monitor the UPS, as it is SNMP capable. You can route the unit to communicate with any NMS or SNMP agent on a network, or limit to an individual NMS address. You will need our APC MIB (available via our website downloads section, SFPMIB398 is the latest rev.) to allow polling of UPS OID data. You can poll any piece of information that is available in the NMC GUI, and yes this includes battery status, unit status, faults, etc.

I would recommend on deciding what you think is important for a help desk to know, then browse the MIB to find the OIDs for those items.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore