SU 750 XL dropped load after self test

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SU 750 XL dropped load after self test
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: β€Ž2021-06-28 11:33 PM . Last Modified: β€Ž2024-03-14 02:45 AM

0 Likes
5
1289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:33 PM . Last Modified: β€Ž2024-03-14 02:45 AM

SU 750 XL dropped load after self test

Have a SU 750 XL (Partial SN QS01363233) which performed a self test, dropped the load, and said replace the batteries.

01/19/2010 16:55:42 UPS: Batteries need immediate replacement.
01/19/2010 16:55:38 UPS: Communications established.
01/19/2010 16:55:28 System: Warmstart.
01/19/2010 16:48:06 System: Email failure to trouble2@
01/19/2010 16:47:52 System: Email failure to trouble@
01/19/2010 16:47:36 System: Email failure to trouble2@
01/19/2010 16:47:22 System: Email failure to trouble2@
01/19/2010 16:47:08 UPS: Failed internal diagnostic self-test.
01/19/2010 16:47:06 System: Email failure to trouble@
01/19/2010 16:46:56 UPS: Turned off.
01/19/2010 16:46:52 UPS: Batteries need immediate replacement.
01/18/2010 19:23:48 System: Web user root logged in from
01/12/2010 16:47:54 System: Email failure to trouble2@
01/12/2010 16:47:40 System: Email failure to trouble2@
01/12/2010 16:47:24 System: Email failure to trouble@
01/12/2010 16:47:20 UPS: Communications established.
01/12/2010 16:47:10 System: Coldstart.
01/05/2010 16:47:16 UPS: Passed internal self-test.
12/29/2009 16:47:20 UPS: Passed internal self-test.


The UPS stayed off until I accessed it via the AP9606. I swapped batteries, performed one self test, and UPS reports everythings fine.

I don't understand why the UPS dropped the load. I thought UPS's were supposed to keep the equipment up, not take them down. The previous self test's passed. I read another thread where this situation is know to happen, it would seem I am not the only one that has seen this. I suspect it has happened to me a time or two in the past (recently, actually.)

APC--what causes this, and how do I prevent this from happening again?

I also am dismayed that the e-mail notification tried three times in a period of seconds, then gave up. I would rather the notification attempts continue indefinetly, or at least try again after a minimum of a few minutes. I realize these cards are old, but...

Thanks,

Jeff

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: β€Ž2021-06-28 11:34 PM . Last Modified: β€Ž2024-03-14 02:45 AM

0 Likes
0
1289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:34 PM . Last Modified: β€Ž2024-03-14 02:45 AM

Not sure what happened with the text to the right, sorry. I don't see an edit button. If someone wants to edit, I would appreciate it.

Jeff

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: β€Ž2021-06-28 11:33 PM . Last Modified: β€Ž2024-03-14 02:45 AM

0 Likes
0
1289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:33 PM . Last Modified: β€Ž2024-03-14 02:45 AM

Buzz,

Thanks. I am so suprised that APC has a product, however old, that can drop the load due to failing a self test. I have placed a lot of trust in APC, promoted the product as THE product we should use to protect the company I work for, and told all relatives to buy APC.

Follow on...

The product in question is not a 750, it's a SU 700 XL. Oppps, not sure how I mixed that one up.

Most important, what should I do to protect the loads attached to the APC UPS's? Dropping a load for failing a self test is not acceptable. One option is to turn off the self test. However this option would leave the question of how do I know when it''s time to replace the batteries and/or how do I know the UPS will function as intended. Do I perform manual tests (during non-production time)? I wouldn't want to perform a self test even during non-production time, with a server running on the UPS. Would I have to test using a load of some type? If so,what size load would I need?

I feel like I am going to need to purchase a quanity of pepper and salsa to go along with the egg I am going to be eating. I told the higher ups we need to protect our servers, switches and other equipment, and the best protection is APC. They followed my suggestions/advice, and we have a purchased only APC UPS over the years. I haven't seen any offical news from APC indicating this situation could be a problem--granted the unit is nine years old, but while PC's might be old after a few years, I didn't think that would be a problem with a UPS. And since I haven't seen any notification about the problem scenario, how do I know the newer units do not have this problem?

I am thinking my rear end may be much smaller after I inform the higher ups about this situation, and feeling like APC should have notified users of this potential problem.

APC, please comment!

I would appreciate suggestions on how I can reduce this potential problem. Turn off the self test? What should I do to ensure the UPS's are working if I turn off the self test? I really don't want to perform a test on all our UPS's, it's going to take time, and require additional oversight to ensure everything is working.

Does anyone have some nice pepper jack cheese?

Thanks,

Jeff

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 11:33 PM . Last Modified: β€Ž2024-03-14 02:45 AM

0 Likes
0
1289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:33 PM . Last Modified: β€Ž2024-03-14 02:45 AM

Jeff,

To answer the simplest question first, you need about a 25-30% load to receive accurate results for a self-test.

On to the more nitty-gritty stuff. I realize it probably isn't ideal, but it may help to explain the typical life expectancy is about 7-10 years. You're getting close to 10 years, at which point the internal circuitry can get worn out due to absorbing minor surges over the years, just regular wear and tear. So that alone is a good reason to consider upgrading. On top of that, the improved intelligence is a bonus - I've only ever heard of one SUA unit dropping a load on a self-test and that was commanded manually via the front panel, so I actually think someone may have pressed the wrong button to be honest.

In that regard, I realize budget restraints are often a more significant factor. The only way to be 100% sure the unit won't drop the load on a self-test is by disabling it, in which case you're right; you won't know when the batteries need to be replaced without manually running self-tests. While a dropped load is hardly common, since typically the unit will be able to detect a battery going bad long before it's at the point of dropping your load during a ~10 second self-test, it is possible.

Please note that the battery must be very old/discharged for this to happen. It's not a matter of failing the self-test, it's not even getting to that stage of evaluation, as it's likely dropping as it immediately transfers to battery. The only way I can think of a battery getting that bad and not triggering a replace battery alarm earlier would be if the load on the unit is quite low. This goes back to the 25-30% load for a self-test. If the load is low, for example around 10%, the unit may falsely pass the self-test because it can't accurately test the battery with such a low load.

Other factors may be invalid self-tests. For example, if the battery charge is below 75%, the unit will consider conditions invalid for testing and will abort the test, which does not result in a failure indication. It doesn't even do the test at the risk of something going wrong.

Hope some of that info helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: β€Ž2021-06-28 11:33 PM . Last Modified: β€Ž2024-03-14 02:45 AM

0 Likes
0
1289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:33 PM . Last Modified: β€Ž2024-03-14 02:45 AM

Matt,

Thanks for the reply, good information. Not what I wanted to hear, but that's life.

I checked the load on the UPS and it says 36%. The load is a Cisco switch, three Cisco wireless bridges and a Linksys AP. Pretty steady load. The batteries were old, but I don't know the date. The self tests were run weekly, according to the log. I think that means either the battery wasn't charged fully, which you said wouldn't show a failure upon self test (I dislike objects that lie!), the 36% load isn't sufficent or the load isn't indicated accurately. Time to haul out a heater or a halogen light (load) and spend time testing.

I'm an idealist, and would like to think that UPS's should last more than two battery changes, but I had better put on my realist pants and work on replacing some of the older UPS's. As an Idealist, I would also like to have seen APC letting users know that dropping a load during a self test is possible. I would then be able to make an informed choice, and would have probably chosen to replace a few UPS, and move the older units to less critical applications. My confidence in APC products is diminished.

Thanks for the information,

Jeff

Reply

Link copied. Please paste this link to share this article on your social media post.

JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: β€Ž2021-06-28 11:34 PM . Last Modified: β€Ž2024-03-14 02:45 AM

0 Likes
0
1289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:34 PM . Last Modified: β€Ž2024-03-14 02:45 AM

Have a SU 750 XL (Partial SN QS01363233) which performed a self test, dropped the load, and said replace the batteries.

01/19/2010 16:55:42 UPS: Batteries need immediate replacement.
01/19/2010 16:55:38 UPS: Communications established.
01/19/2010 16:55:28 System: Warmstart.
01/19/2010 16:48:06 System: Email failure to trouble2@
01/19/2010 16:47:52 System: Email failure to trouble@
01/19/2010 16:47:36 System: Email failure to trouble2@
01/19/2010 16:47:22 System: Email failure to trouble2@
01/19/2010 16:47:08 UPS: Failed internal diagnostic self-test.
01/19/2010 16:47:06 System: Email failure to trouble@
01/19/2010 16:46:56 UPS: Turned off.
01/19/2010 16:46:52 UPS: Batteries need immediate replacement.
01/18/2010 19:23:48 System: Web user root logged in from
01/12/2010 16:47:54 System: Email failure to trouble2@
01/12/2010 16:47:40 System: Email failure to trouble2@
01/12/2010 16:47:24 System: Email failure to trouble@
01/12/2010 16:47:20 UPS: Communications established.
01/12/2010 16:47:10 System: Coldstart.
01/05/2010 16:47:16 UPS: Passed internal self-test.
12/29/2009 16:47:20 UPS: Passed internal self-test.


The UPS stayed off until I accessed it via the AP9606. I swapped batteries, performed one self test, and UPS reports everythings fine.

I don't understand why the UPS dropped the load. I thought UPS's were supposed to keep the equipment up, not take them down. The previous self test's passed. I read another thread where this situation is know to happen, it would seem I am not the only one that has seen this. I suspect it has happened to me a time or two in the past (recently, actually.)

APC--what causes this, and how do I prevent this from happening again?

I also am dismayed that the e-mail notification tried three times in a period of seconds, then gave up. I would rather the notification attempts continue indefinetly, or at least try again after a minimum of a few minutes. I realize these cards are old, but...

Thanks,

Jeff

Reply

Link copied. Please paste this link to share this article on your social media post.

JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: β€Ž2021-06-28 11:34 PM . Last Modified: β€Ž2024-03-14 02:45 AM

0 Likes
0
1290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:34 PM . Last Modified: β€Ž2024-03-14 02:45 AM

Not sure what happened with the text to the right, sorry. I don't see an edit button. If someone wants to edit, I would appreciate it.

Jeff

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore