We have just purchased a new SRT6KRMXLT that will be replacing an old SUA3000RMX3U with external pack. I was also able to find a SRT192BP2 unit from a local company that was installed into a rack but never put into service as they had an 8K unit and more packs then they needed. I did not realize that there were 2 different 192v battery packs and was wondering if there was a kit to modify the BP2 into a straight BP with the correct cable and harness?
Thanks.
Erik
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:54 AM . Last Modified: 2024-03-18 03:59 AM
Hi Erik,
There reason that the SRT192BP2 is not compatible with the SRT6KRMXLT is because the BP2 requires a communication cable to be plugged in going from the battery pack to the UPS. The SRT6KRMXLT does not have a communication port to allow for this to be possible. Unfortunately, there is no way to modify the BP2 to allow communication with the SRT6K.
Regards,
Nicole
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:54 AM . Last Modified: 2024-03-18 03:59 AM
Hi Erik,
There reason that the SRT192BP2 is not compatible with the SRT6KRMXLT is because the BP2 requires a communication cable to be plugged in going from the battery pack to the UPS. The SRT6KRMXLT does not have a communication port to allow for this to be possible. Unfortunately, there is no way to modify the BP2 to allow communication with the SRT6K.
Regards,