SMX750I Outputpower turned off
  • SMX750I Outputpower turned off
5060
142
Posted: ‎2021-06-28 06:11 AM . Last Modified: ‎2024-03-18 02:38 AM
803
Hi have several SMX750I
just having this issue with one of them,
they're all brand new haven't been installed on site yet, this was discovered from initial testing.
 08/19/2016 22:27:33 Device UPS: The output power is turned off.
 08/19/2016 22:27:33 Device UPS: The graceful shutdown period has ended.
 08/19/2016 22:27:33 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.
 08/19/2016 22:27:33 Device UPS: The power for the main outlet group, UPS Outlets, is now turned off.
 08/19/2016 22:27:28 Device UPS: The output power is now turned on.
 08/19/2016 22:27:28 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on.
 08/19/2016 22:27:28 Device UPS: The power for the main outlet group, UPS Outlets, is now turned on.
 08/19/2016 22:27:03 Device UPS: The output power is turned off.
 08/19/2016 22:27:03 Device UPS: The graceful shutdown period has ended.
 08/19/2016 22:27:03 Device UPS: The power for the main outlet group, UPS Outlets, is now turned off.
 08/19/2016 22:26:58 Device UPS: The output power is now turned on.
 08/19/2016 22:26:58 Device UPS: The power for the main outlet group, UPS Outlets, is now turned on.
this happens whether the battery is in or not, i can force the power on but it will only stay on for seconds
  • outputpower
  • smx750i
You should contact local support. The unit should not report output on output off as it is. Since the unit is new local support will ask you to run a few tests and if needed will provide a replacement. Contact information will be found at this link.  http://www.apc.com/uk/en/support/contact-us/index.jsp