SMX3000RMHV2U run Calibration Runtime Test always Pending Status.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMX3000RMHV2U run Calibration Runtime Test always Pending Status.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

0 Likes
4
1225
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

SMX3000RMHV2U run Calibration Runtime Test always Pending Status.

The self test is success but the calibration runtime test status keeps pending then refused.

I tried to fix the problem. e.g., update the latest firmware of the NMC, to follow the procedure (https://community.se.com/t5/APC-UPS-Data-Center-Enterprise/bd-p/datacenter-forum, ) but I cannot fix the problem.

I am not sure that it caused by hardware or software. Does anyone can help me to diagnose and to solve it?

Attachments
  • Tags:
  • calibration
  • refused
  • runtime
  • smart
  • test
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

0 Likes
0
1225
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

On 28/10/2015 10:19 PM, Jordan said:

Wing,

I would not recommend replacing anything, rather I think it would be beneficial to call into local technical support and troubleshoot the NMC since the UPS itself can run the calibration and the battery is healthy and working fine after calibrations and self tests.

Regards,

Hi Jordan,

Thank you for your advise.

After the resetting NMC, the UPS still cannot run calibration test via web interface.

Should I need to replace the NMC or to modify the configuration?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

0 Likes
0
1225
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

Wing,

Are you able to successfully run a calibration via the LCD panel on the front of the unit?  How often are you running these calibrations?  We do not recommend running a calibration more than once every 6 months.  What is your load on the unit?  What is the battery capacity when you attempt to start the runtime?  Have you tried rebooting the management interface of the NMC?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

0 Likes
0
1225
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

Jordan,

I can run a calibration runtime test successfully via LCD panel.

I have tried to reboot the management interface of NMC and to reboot the card before starting the test. 

When I attempt to start the runtime test, the battery capacity is 100% and loading up to 10%.

Should I need to replace the battery, the UPS or the NMC card?

Many Thanks!

On 10/27/2015 10:33 PM, Jordan said:

Wing,

Are you able to successfully run a calibration via the LCD panel on the front of the unit?  How often are you running these calibrations?  We do not recommend running a calibration more than once every 6 months.  What is your load on the unit?  What is the battery capacity when you attempt to start the runtime?  Have you tried rebooting the management interface of the NMC?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

0 Likes
0
1225
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

Wing,

I would not recommend replacing anything, rather I think it would be beneficial to call into local technical support and troubleshoot the NMC since the UPS itself can run the calibration and the battery is healthy and working fine after calibrations and self tests.

Regards,

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

0 Likes
0
1226
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

On 28/10/2015 10:19 PM, Jordan said:

Wing,

I would not recommend replacing anything, rather I think it would be beneficial to call into local technical support and troubleshoot the NMC since the UPS itself can run the calibration and the battery is healthy and working fine after calibrations and self tests.

Regards,

Hi Jordan,

Thank you for your advise.

After the resetting NMC, the UPS still cannot run calibration test via web interface.

Should I need to replace the NMC or to modify the configuration?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of