AP7902 and SNMP oid issues

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP7902 and SNMP oid issues
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
134
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

0 Likes
3
2129
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

AP7902 and SNMP oid issues

I recently ran into an issue with a handful of AP7902's and an SNMP script I use to manage them and I was wondering if anyone had any ideas...

Basically, I have a PHP script that uses snmpset to send either a "1", "2" or "3" integer to oid 318.1.1.4.4.2.1.3.[outlet number] -so the end result looks something like this:

snmpset -v1 -c private 10.0.0.2 1.3.6.1.4.1.318.1.1.4.4.2.1.3.08 i 2

However, I've noticed on some of my PDU's this returns an invalid oid error and I can only get it to work if I drop the leading "0" from the outlet number, ex:

snmpset -v1 -c private 10.0.0.2 1.3.6.1.4.1.318.1.1.4.4.2.1.3.08 i 2
Unknown Object Identifier (Sub-id not found: iso -> 08)
snmpset -v1 -c private 10.0.0.2 1.3.6.1.4.1.318.1.1.4.4.2.1.3.8 i 2
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.3.8 = INTEGER: 2

My other PDU's don't seem to make this distinction. I can send a request to either "8" or "08" and it works. This is the preferred behavior.

Is there any way I can get these PDU's to not make a distinction between port "x" and port "xx"? Or at least be consistent in always expecting "xx"? Am I missing something?

The AP7902 PDU that accepts either a single digit or two digit port number is running:

Network Management Card AOS v2.2.7
Rack PDU APP v2.2.0

The AP7902 PDU that only accepts single digit numbers for certain ports is running:

Network Management Card AOS v2.6.4
Rack PDU APP v2.6.5

Thanks.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • ap7902
  • oid
  • snmp
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

0 Likes
0
2126
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

I recently ran into an issue with a handful of AP7902's and an SNMP script I use to manage them and I was wondering if anyone had any ideas...

Basically, I have a PHP script that uses snmpset to send either a "1", "2" or "3" integer to oid 318.1.1.4.4.2.1.3.[outlet number] -so the end result looks something like this:

snmpset -v1 -c private 10.0.0.2 1.3.6.1.4.1.318.1.1.4.4.2.1.3.08 i 2

However, I've noticed on some of my PDU's this returns an invalid oid error and I can only get it to work if I drop the leading "0" from the outlet number, ex:

snmpset -v1 -c private 10.0.0.2 1.3.6.1.4.1.318.1.1.4.4.2.1.3.08 i 2
Unknown Object Identifier (Sub-id not found: iso -> 08)
snmpset -v1 -c private 10.0.0.2 1.3.6.1.4.1.318.1.1.4.4.2.1.3.8 i 2
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.3.8 = INTEGER: 2

My other PDU's don't seem to make this distinction. I can send a request to either "8" or "08" and it works. This is the preferred behavior.

Is there any way I can get these PDU's to not make a distinction between port "x" and port "xx"? Or at least be consistent in always expecting "xx"? Am I missing something?

The AP7902 PDU that accepts either a single digit or two digit port number is running:

Network Management Card AOS v2.2.7
Rack PDU APP v2.2.0

The AP7902 PDU that only accepts single digit numbers for certain ports is running:

Network Management Card AOS v2.6.4
Rack PDU APP v2.6.5

Thanks.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

0 Likes
0
2126
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

Thanks for the reply. At first, I thought I might be able to get around this by downgrading the FW -just like you suggested. In fact, the PDU in question was running a recent version of the AOS until I downgraded it to 2.6.4. The reason I didn't go down to 2.2.7 (the version on the PDU that is working) is because it looks like APC has discontinued this version and I can't find a copy anywhere.

I also thought about modifying the PHP script to send single digits -but this is where it gets weird... some ports on the same PDU insist on being called by "x" while others insist on "0x"... and still others are okay with either format! That's what I meant about consistency... different ports seem to require different formats on the same PDU... and I'm not sure how to make my script "smart enough" to know when it needs to differentiate between the two formats.

For example:

snmpset -v1 -c private 10.0.0.2 1.3.6.1.4.1.318.1.1.4.4.2.1.3.06 i 1
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.3.6 = INTEGER: 1

snmpset -v1 -c private 10.0.0.2 1.3.6.1.4.1.318.1.1.4.4.2.1.3.6 i 1
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.3.6 = INTEGER: 1

snmpset -v1 -c private 10.0.0.2 1.3.6.1.4.1.318.1.1.4.4.2.1.3.08 i 1
1.3.6.1.4.1.318.1.1.4.4.2.1.3.08: Unknown Object Identifier (Sub-id not found: iso -> 08)

snmpset -v1 -c private 10.0.0.2 1.3.6.1.4.1.318.1.1.4.4.2.1.3.8 i 1
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.3.8 = INTEGER: 1

Notice how port 6 is okay with either format -while port 8 requires a single digit.

For what it's worth -the PDU that seems to be functioning properly is running MB:v3.6.4 and the PDU that is giving me troubles is running MB:v3.6.8. I'm under the impression that this is the MIB DB revision number, but I'm not sure how to step this down... I thought this was usually changed whenever you update the AOS, but I could be wrong.

... any help? This is driving me crazy.

Message was edited by: vuduchikin

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

0 Likes
0
2126
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

They have the firmware available on the FTP site 220/227:

ftp://ftp.apcc.com/apc/public/hardware/mswitch/firmware/rpdu/v220/

I would try downgrading the firmware, this should change your MB version on the PDU to the rev. that you allows you to perform your gets/sets properly.

Another thing to try would be the latest revisions of the firmware. There is currently a release of 3.5.5/3.5.6 available to attempt. If you have global outlets enabled, disable them before upgrading and while using this revision of firmware. Another release is expected to be out soon that will address that issue.

It doesn't sounds like a configuration issue on the PDU, but you could try resetting the card to defaults except it's IP settings to rule something of that nature out.

Let us know if the firmware downgrade or upgrade fixes the issue.

Message was edited by: Grenade

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

0 Likes
0
2127
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

I recently ran into an issue with a handful of AP7902's and an SNMP script I use to manage them and I was wondering if anyone had any ideas...

Basically, I have a PHP script that uses snmpset to send either a "1", "2" or "3" integer to oid 318.1.1.4.4.2.1.3.[outlet number] -so the end result looks something like this:

snmpset -v1 -c private 10.0.0.2 1.3.6.1.4.1.318.1.1.4.4.2.1.3.08 i 2

However, I've noticed on some of my PDU's this returns an invalid oid error and I can only get it to work if I drop the leading "0" from the outlet number, ex:

snmpset -v1 -c private 10.0.0.2 1.3.6.1.4.1.318.1.1.4.4.2.1.3.08 i 2
Unknown Object Identifier (Sub-id not found: iso -> 08)
snmpset -v1 -c private 10.0.0.2 1.3.6.1.4.1.318.1.1.4.4.2.1.3.8 i 2
SNMPv2-SMI::enterprises.318.1.1.4.4.2.1.3.8 = INTEGER: 2

My other PDU's don't seem to make this distinction. I can send a request to either "8" or "08" and it works. This is the preferred behavior.

Is there any way I can get these PDU's to not make a distinction between port "x" and port "xx"? Or at least be consistent in always expecting "xx"? Am I missing something?

The AP7902 PDU that accepts either a single digit or two digit port number is running:

Network Management Card AOS v2.2.7
Rack PDU APP v2.2.0

The AP7902 PDU that only accepts single digit numbers for certain ports is running:

Network Management Card AOS v2.6.4
Rack PDU APP v2.6.5

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore