Posted: 2025-02-05 07:28 AM
Recently replaced batteries and got 2x SMX3000LV up and running trying to update firmware. Cannot find any valid links or topics.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-06 04:36 AM
Hello,
You can find all firmware available for SMX in the below link
https://www.apc.com/ca/en/faqs/FA279197/
check the existing installed firmware update ID and verify if it is available in the firmware table
| SMX | 20 | SMTSMX20UPS_15-0.enc | UPS 15.0 | No | No | No |
| SMX | 23 | SMX23UPS_15-0.enc | UPS 15.0 | No | No | Yes |
| SMX | 1003 | SMX1003UPS_15-0.enc | UPS 15.0 | No | No | No |
| SMX | 1031 | SMTSMX1031UPS_15-5.enc | UPS 15.5 | No | Yes | Yes |
| SMX | 1050 | SMTSMX1050UPS_16-5.enc | UPS 16.5 | No | Yes | Yes |
from the attached firmware files,you will the below firmware version details for your references
Version:
========
UPS 15.0
Previous Released Version:
==========================
UPS 08.1
Applicable Models:
==================
SMX2000LV
SMX2000LVNC
SMX2000RMLV2U
SMX2000RMLV2UNC
SMX2200HV
SMX2200RMHV2U
SMX2200RMLV2U
SMX3000HV
SMX3000HVNC
SMX3000HVT
SMX3000RMHV2U
SMX3000RMHV2UNC
SMX3000LV
SMX3000LVNC
SMX3000RMLV2U
SMX3000RMLV2UNC
and follow the upgrade instructions as explained in the above link
Regards,
Karim
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-06 04:36 AM
Hello,
You can find all firmware available for SMX in the below link
https://www.apc.com/ca/en/faqs/FA279197/
check the existing installed firmware update ID and verify if it is available in the firmware table
| SMX | 20 | SMTSMX20UPS_15-0.enc | UPS 15.0 | No | No | No |
| SMX | 23 | SMX23UPS_15-0.enc | UPS 15.0 | No | No | Yes |
| SMX | 1003 | SMX1003UPS_15-0.enc | UPS 15.0 | No | No | No |
| SMX | 1031 | SMTSMX1031UPS_15-5.enc | UPS 15.5 | No | Yes | Yes |
| SMX | 1050 | SMTSMX1050UPS_16-5.enc | UPS 16.5 | No | Yes | Yes |
from the attached firmware files,you will the below firmware version details for your references
Version:
========
UPS 15.0
Previous Released Version:
==========================
UPS 08.1
Applicable Models:
==================
SMX2000LV
SMX2000LVNC
SMX2000RMLV2U
SMX2000RMLV2UNC
SMX2200HV
SMX2200RMHV2U
SMX2200RMLV2U
SMX3000HV
SMX3000HVNC
SMX3000HVT
SMX3000RMHV2U
SMX3000RMHV2UNC
SMX3000LV
SMX3000LVNC
SMX3000RMLV2U
SMX3000RMLV2UNC
and follow the upgrade instructions as explained in the above link
Regards,
Karim