Intelligence Module Mismatch

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Intelligence Module Mismatch
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
114
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
devnull
devnull
Cadet

Posted: ‎2024-12-07 06:50 AM

0 Likes
1
329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-07 06:50 AM

Intelligence Module Mismatch

We were turning up a new 15kw smart ups modular with both IMs inserted. There were alarms non-stop. Turns out one of the IMs was "programmed" or recognized our system as a 20kw RM.

 

After significant troubleshooting we decided to pull both IMs and insert only the IM that properly recognized the unit as a 15kW unit. All alarms cleared, except the invalid configuration stating we're missing an IM.

 

How do we reconfigure the IM to recognize the system as 15kW? It doesn't matter what position the "20kW" IM is in, it recognizes the UPS as a 20kW system.

 

Thoughts?

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-02-06 03:54 AM

0 Likes
0
230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-06 03:54 AM

Hello,

 

If you refers to Smart UPS modular Ultra 20 KVA We recommends first to update the unit firmware to the latest version


System Package filename: SRYL1225UPS_13-3.enc (attached )

Includes:

Battery Module firmware version: 8.44
Intelligence Module firmware 1 version: IMA 05.8
Intelligence Module firmware 2 version: UPS 13.3 (updated)
Power Module Firmware version: PMA 03.3
External Battery Frame Firmware version: XRC 01.1

Upgrade Instructions:
====================
How to Install the Smart-UPS Modular Ultra NMC/Display Firmware using the USB Port
Web link - https://www.apc.com/us/en/faqs/FAQ000261841/

How to Install Smart-UPS Modular Ultra Firmware Using the Display and USB Port
Web Link - https://www.apc.com/ie/en/faqs/FAQ000261838/

How do I update my Smart-UPS firmware using the web interface of my Network Management Card?
Web Link - https://www.se.com/ca/en/faqs/FA170679/

Power Modules and Battery Modules are packaged separately, and the quantity depends on UPS power rating, so check if any of the power modules are faulty ,you can share the logs and see if any power module faulty ,you will a red LED illuminated on the faulty power module and IMs as well ,as if one PM failed the system power rating is affected as IMs automatically detects the PMs availability ,hence the UPS power ratings are different based on number of power module installed

 

Regards,

 

Karim

See Answer In Context

Attachments
SRYL1225UPS_13-3.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-02-06 03:54 AM

0 Likes
0
231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-06 03:54 AM

Hello,

 

If you refers to Smart UPS modular Ultra 20 KVA We recommends first to update the unit firmware to the latest version


System Package filename: SRYL1225UPS_13-3.enc (attached )

Includes:

Battery Module firmware version: 8.44
Intelligence Module firmware 1 version: IMA 05.8
Intelligence Module firmware 2 version: UPS 13.3 (updated)
Power Module Firmware version: PMA 03.3
External Battery Frame Firmware version: XRC 01.1

Upgrade Instructions:
====================
How to Install the Smart-UPS Modular Ultra NMC/Display Firmware using the USB Port
Web link - https://www.apc.com/us/en/faqs/FAQ000261841/

How to Install Smart-UPS Modular Ultra Firmware Using the Display and USB Port
Web Link - https://www.apc.com/ie/en/faqs/FAQ000261838/

How do I update my Smart-UPS firmware using the web interface of my Network Management Card?
Web Link - https://www.se.com/ca/en/faqs/FA170679/

Power Modules and Battery Modules are packaged separately, and the quantity depends on UPS power rating, so check if any of the power modules are faulty ,you can share the logs and see if any power module faulty ,you will a red LED illuminated on the faulty power module and IMs as well ,as if one PM failed the system power rating is affected as IMs automatically detects the PMs availability ,hence the UPS power ratings are different based on number of power module installed

 

Regards,

 

Karim

Attachments
SRYL1225UPS_13-3.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of