Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

SMX2200HV Firmware update failure and recovery

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMX2200HV Firmware update failure and recovery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5059
voidstar_apc
voidstar_apc
196
Teken
Teken
162
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Related Products
product field
Schneider Electric
Smart-UPS

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
CdeJonge
CdeJonge
Explorer

Posted: ‎2025-06-20 04:42 AM

0 Likes
0
1898
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-20 04:42 AM

SMX2200HV Firmware update failure and recovery

Just posting this since I could not find similar solutions online and I hope that someone who finds themselves in the same situation can use this information to hopefully fix their machine.

 

Recently we had to replace the battery pack in our SMX2200HV unit, so we planned a maintenance window for this and I thought it would be a great opportunity to get all the firmware up to date. Especially since we had not updated anything since first installment. We manage the device over a network management card 3 and the process seemed pretty straightforward. 

  • Power off the outlet groups.
  • Upload the firmware file to the management card and let it do the update.
  • Restore power to the outlet groups.

 

Sadly things did not go according to plan. Met with a "Firmware Update in Progress" screen.

FUIP.jpg

 

 

 

 

 

 

 

 

And the NMC not registering any connected UPS anymore and also rebooting every 2-3min or so I feared the worst.

 

Looking at resources online like:

  • SMX3000HV stuck in reboot loop firmware update in progress 
  • How do I update the firmware using the Firmware Upgrade Wizard? 

I tried to update the firmware this way. Sadly the wizard failed to make a connection using the serial connection and the readme file specifically states: 

1. USB upgrade not supported in SMTSMX20 and SMX1003.Please try with Serial Cable that comes with the UPS

 Using Putty to connect over serial gave me a blank screen that did not seem to respond to any input as well.
After triple checking the 940-0625A cable was indeed correct this blank screen did not fill me with hope.  

 

Reading and viewing some more resources:

  • unbricking an apc smt3000 ups after a failed firmware update 
  • Enabling the Smart interface on an APC SMT2200I 
  • Finding the hidden Smart protocol in an APC SMT2200 

This made me think I would have to re-flash the chip with a ST-Link adapter using an image captured from a second unit we have. Pending the arrival of the hardware to do so I wanted to make sure the COM port on my computer was actually not receiving any data.
So I installed the trail version of Serial Port Monitor and at first did not get any output that I could interpret. The default view is almost like a wireshark pcap, so I would recommend using the terminal view. SPM checks if any other programs are using the serial port when you start a capture, the easiest way to make it work is to disable the COM port in device manager and re-enable it.
I disconnected the front panel from the main board since in the YouTube vids it seemed to influence the behavior of the serial connection. And got Extra Putty installed since I would need the XModem function to upload the firmware file as per the SMT3000 unbrick guide.

 

Wanting to see if I could get any output like UPS-Link I fired up a SPM capture. But since the trail does not allow you to send commands, I opened up ExtraPutty to see if I would get any response to sending a "Y".
The "Y" did not display but instead I was getting something shown else:

extraputty.png

Ok, progress. It seems the download manager is active, but it does not have the firmware file from the NMC. It sends a "C" ever few seconds then when it has 20 of them the UPS reboots and starts again with the download manager info.


At this point I must admit I did a bit of a "Hail Mary" and just used File Transfer --> XModem --> Send and pushed the 15.0 firmware file I had. When after a minute or 2 the UPS still had not rebooted I began to feel a little bit more at ease. After about 10 minutes the upload was done and the UPS rebooted, I heard some of the relays click and it worked again.

 

 

 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX-RM
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore