Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

SMX1500RM2UNC firmware

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: SMX1500RM2UNC firmware
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
ikps_apc
Crewman ikps_apc
Crewman

Posted: ‎2021-06-28 07:20 AM

0 Likes
26
2054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:20 AM

SMX1500RM2UNC firmware

This was originally posted on APC forums on 1/20/2018


Hi, trying to upgrade a older unit SMX1500RM2UNC 04/12/2010 AS1016120133 UPS 02.2 (ID11)  /  AP9631  sumx aos 6.5 bootmon 1.08, After spending much time reading through the forums it looks like I cannot upgrade the ups firmware any of the normal ways, is there a workaround for this?  I'm trying to fix switching to battery and right back over and over which I found in one thread "it will be UPS firmware 03.8 for SMX units to address frequent clicking and transferring back and forth to battery/AVR".

Could I ftp and move SMX11UPS_03-8.enc to it?

Thanks

Kevin

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:21 AM

0 Likes
1
2051
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:21 AM

This reply was originally posted by Mike on APC forums on 4/28/2021


Hello Robert,

Here you go https://schneider-electric.box.com/s/gy9jd1aebwjtydrdax5sj935t0dnto33

On 4/28/2021 2:51 PM, Roberto said:

Hi: would be possible to update this link ( is not working) since I have the same problem with a very old SMX1000 , there is not  a APC customer service available here and I would like to try the firmware upgrade by myself,  following carefully of course,  all the steps and I got the required serial cable

 

Regards

 

Robert

 

See Answer In Context

Reply
Replies 26
ikps_apc
Crewman ikps_apc
Crewman

Posted: ‎2021-06-28 07:20 AM

0 Likes
0
2051
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:20 AM

This was originally posted on APC forums on 1/22/2018


Well hunting around more I found a procedure for using a wizard and a serial cable, so once I find where the serial cable has ran off to I will give that a whirl.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:20 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:20 AM

This reply was originally posted by Angela on APC forums on 1/23/2018


Hi Kevin,

What does your UPS report for its CBL (bootloader) version? Is it 1.0? I think it might be if you have UPS 02.2.

If this is the case, then there is a special process to update that older bootloader to facilitate the update to UPS 03.8. You won't be able to go straight to UPS 03.8.

I can send you this process or you can contact tech support and tell them you need the instructions for updating from CBL 1.0 bootloader, once we confirm it is CBL 1.0 that you have currently with UPS 02.2.

Reply
ikps_apc
Crewman ikps_apc
Crewman

Posted: ‎2021-06-28 07:20 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:20 AM

This was originally posted on APC forums on 1/23/2018


  This all started with the network wizard unable to upgrade my original AP9631 card JA1010037314 hanging at the bootmon upgrade, looking in the forums I saw where  this particular date code AP3916 has an issue, ( if you have a procedure to fix my old AP3916 please let me know), I have other AP3916 cards here  so I put another more recent AP3916 into this UPS and  re-ran the network wizard and it ran updating everything to the levels I listed. 

  Looking at ABOUT UPS  all it says is UPS 02.2 (ID11) for firmware, where is CBL listed?

Like I said I also found the serial version of the wizard and will try that once my serial cable comes back to me, or is there something else I will need to do? if that is the special process you mentioned then yes please send it to me.

Thanks Kevin

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:20 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:20 AM

This reply was originally posted by Angela on APC forums on 1/23/2018


On 1/23/2018 2:12 PM, kevin said:

This all started with the network wizard unable to upgrade my original AP9631 card JA1010037314 hanging at the bootmon upgrade, looking in the forums I saw where  this particular date code AP3916 has an issue, ( if you have a procedure to fix my old AP3916 please let me know),

OK, yes, we had a problem with this date code. There is no fix to get this to upgrade the firmware. The card has to be replaced. We can replace this through RMA for you since it was a defect, regardless of warranty status on the AP9631. You can contact support and mention this forum thread and let me know if you run into problems. So, a new AP9631 is needed for any that sart with JA1010 through JA1015.

On 1/23/2018 2:12 PM, kevin said:

Looking at ABOUT UPS  all it says is UPS 02.2 (ID11) for firmware, where is CBL listed?

Like I said I also found the serial version of the wizard and will try that once my serial cable comes back to me, or is there something else I will need to do? if that is the special process you mentioned then yes please send it to me.

I think you may have to check via the UPS LCD and it does not show CBL in the NMC unfortunately. I think you're UPS LCD menu also needs to be in "advanced" mode which you can change under configuration menu in the LCD menu.

The special process I can send to you once you verify it is CBL 1.0. It will require that serial cable and it is just a special wizard version and script required to update the older bootloader. I don't want to send it and confuse you if we won't need it so I'd like to really confirm that CBL is at 01.0 and I'll private message you a link with the files you need and the process. It will require the UPS output to be turned off as well to upgrade the UPS firmware, just so you can plan accordingly that you're attached equipment needs to be turned off. 

Reply
ikps_apc
Crewman ikps_apc
Crewman

Posted: ‎2021-06-28 07:20 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:20 AM

This was originally posted on APC forums on 1/23/2018


Yup Duh... I forgot it is also in the LCD display, CBL 1.0 UBL 5.0 COM 2.3 UPS2.2

CBL 1.0 so yes I need the other procedure.

Thank You for the fix info on the AP9631

Kevin

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:20 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:20 AM

This reply was originally posted by Angela on APC forums on 1/23/2018


No problem! Ok, let me send you a private message here within a few minutes and it will have the details you need.

Reply
ikps_apc
Crewman ikps_apc
Crewman

Posted: ‎2021-06-28 07:20 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:20 AM

This was originally posted on APC forums on 1/25/2018


RMA for the 9631 card is in process, the procedure for the smx1500 worked perfectly and everything is at the latest code now.

Thank You Angela very much for the great service!

Reply
tdunks_apc
tdunks_apc
Cadet

Posted: ‎2021-06-28 07:21 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:21 AM

This was originally posted on APC forums on 8/4/2018


Hello Angela, would you be able to send me those instructions? I have an SMX1500 which I am having the same difficulty. Firmware version 02.2 and CBL 1.0. Thanks.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:21 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:21 AM

This reply was originally posted by Angela on APC forums on 8/6/2018


Hi Tanner, I will send but for anyone else in the future, these instructions should be available through tech support. Just tell them you need the CBL 1.0 update procedure for the SMX and you can reference this: http://www.apc.com/us/en/faqs/FA241461

Reply
Glendale2x_apc
Glendale2x_apc
Cadet

Posted: ‎2021-06-28 07:21 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:21 AM

This was originally posted on APC forums on 11/20/2019


Replying to this old thread because I have the same problem...

Except I can't get help from tech support. They're stuck asking me if I'm trying to upgrade through the NMC or firmware wizard, neither of which are supported methods for SMX750 units with firmware UPS 02.x or lower and a date code earlier than 1037 (mine is AS1036 and UPS 02.2). When I opened the request I even started out by referencing FA241461 to try and make it easy.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:21 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:21 AM

This reply was originally posted by Mike on APC forums on 11/21/2019


On 11/20/2019 4:32 PM, Seth said:

Replying to this old thread because I have the same problem...

Except I can't get help from tech support. They're stuck asking me if I'm trying to upgrade through the NMC or firmware wizard, neither of which are supported methods for SMX750 units with firmware UPS 02.x or lower and a date code earlier than 1037 (mine is AS1036 and UPS 02.2). When I opened the request I even started out by referencing FA241461 to try and make it easy.

Hi Seth,

If in any case that you do not hear from tech support asap, click on the link below to download the CBL Updater. It is imperative that you follow directions exactly to avoid bricking the UPS. Read the Read Me file first. But we strongly recommend that you call tech support (800 800 4272 option 1 > 1 and be with them on the line while doing the upgrade so they can guide you step by step. 

https://schneider-electric.box.com/s/ny5641euz22pv2fzktjbja4h7zanxjon

Reply
robmir_apc
Lieutenant robmir_apc
Lieutenant

Posted: ‎2021-06-28 07:21 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:21 AM

This was originally posted on APC forums on 4/28/2021


Hi: would be possible to update this link ( is not working) since I have the same problem with a very old SMX1000 , there is not  a APC customer service available here and I would like to try the firmware upgrade by myself,  following carefully of course,  all the steps and I got the required serial cable

 

Regards

 

Robert

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:21 AM

0 Likes
1
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:21 AM

This reply was originally posted by Mike on APC forums on 4/28/2021


Hello Robert,

Here you go https://schneider-electric.box.com/s/gy9jd1aebwjtydrdax5sj935t0dnto33

On 4/28/2021 2:51 PM, Roberto said:

Hi: would be possible to update this link ( is not working) since I have the same problem with a very old SMX1000 , there is not  a APC customer service available here and I would like to try the firmware upgrade by myself,  following carefully of course,  all the steps and I got the required serial cable

 

Regards

 

Robert

 

Reply
robmir_apc
Lieutenant robmir_apc
Lieutenant

Posted: ‎2021-06-28 07:21 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:21 AM

This was originally posted on APC forums on 4/28/2021


Thank you Mike !!!!

Will prepare a big pitcher of a  nice iced tea, cookies and a lot patience , read and read the text before sitting  in front of the computer and the UPS, cross my fingers and hope for the best !!!!

Reply
robmir_apc
Lieutenant robmir_apc
Lieutenant

Posted: ‎2021-06-28 07:21 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:21 AM

This was originally posted on APC forums on 4/29/2021


Hi Mike:  the update to CBL 02.2 was a success and the firmware update to 3.8  went smoothly !!!!

Thanks a lot. You didn't make my day but my whole month   LOL laughing 

 

Reply
robmir_apc
Lieutenant robmir_apc
Lieutenant

Posted: ‎2021-06-28 07:21 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:21 AM

This was originally posted on APC forums on 4/29/2021


Hi Mike: It seems a gremlin appeared because when I try to turn it off through the front display , when the menu asked for confirmation  as for the delay off, the up and down select buttons froze. The only way I could order the UPS to turn off was sending commands through the AP9630.

Any thoughts ? 

Reply
robmir_apc
Lieutenant robmir_apc
Lieutenant

Posted: ‎2021-06-28 07:21 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:21 AM

This was originally posted on APC forums on 4/29/2021


Only the power button responds to commands. Menu / Escape , Return, Up and Down buttons are completely useless frown  

Reply
robmir_apc
Lieutenant robmir_apc
Lieutenant

Posted: ‎2021-06-28 07:21 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:21 AM

This was originally posted on APC forums on 4/30/2021


Downgraded to UPS 03.7 (ID11) and same problem, all the buttons except power are unresponsive

Reply
robmir_apc
Lieutenant robmir_apc
Lieutenant

Posted: ‎2021-06-28 07:21 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:21 AM

This was originally posted on APC forums on 5/3/2021


Hi:  do you have any idea why after the upgrade to 03.8 all the control buttons except power are unresponsive ? 

I downgraded to 03.7 and the problem remains.  The only way to check the UPS status and settings are through the network card

Is there a way to test if there is a electric  problem with the display control or is a firmware issue ?

Reply
Glendale2x_apc
Glendale2x_apc
Cadet

Posted: ‎2021-06-28 07:21 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:21 AM

This was originally posted on APC forums on 5/3/2021


Mine was successful, so unfortunately I don't have any insight into what the problem could be.

Reply
robmir_apc
Lieutenant robmir_apc
Lieutenant

Posted: ‎2021-06-28 07:21 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:21 AM

This was originally posted on APC forums on 5/3/2021


What puzzle me is that this is not my first rodeo. On this case  I followed all the steps by the t, the output messages stated  that all the upgrades were successful.

Since all the 4 LED's are working fine,  the display is working and the power button is responsive could mean the display board is ok.

I have a newer SMX1000 so I will plug the  display on it as to discard electrical problems.

Reply
robmir_apc
Lieutenant robmir_apc
Lieutenant

Posted: ‎2021-06-28 07:21 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:21 AM

This was originally posted on APC forums on 5/4/2021


Did you do all the firmware upgrade up to 3.08 or just the basic included in the SMX_v1.0_Firmware_Updater ?

I reflashed it again from the start and with the included firmware UNPz02.6  (ID11) I regained all the buttons function so I guess the latest 3.08 is NOT compatible with my old SMX-1000 so I will pass on it !!!

Reply
Glendale2x_apc
Glendale2x_apc
Cadet

Posted: ‎2021-06-28 07:21 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:21 AM

This was originally posted on APC forums on 5/4/2021


I'm running UPS 03.8 (ID11) on my date code 1036 UPS.

Model Smart-UPS X 750
SKU SMX750
Serial Number AS1036XXXXXX 
Firmware Revision UPS 03.8 (ID11) 
Manufacture Date 09/05/2010
Reply
robmir_apc
Lieutenant robmir_apc
Lieutenant

Posted: ‎2021-06-28 07:22 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:22 AM

This was originally posted on APC forums on 5/4/2021


Perhaps I will give it a new try since your manufacture date is is very close to mine, worst case scenario I will flash it back again laughing

Reply
robmir_apc
Lieutenant robmir_apc
Lieutenant

Posted: ‎2021-06-28 07:22 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-28 07:22 AM

This was originally posted on APC forums on 5/4/2021


Same problem, has to downgrade the firmware again to unpz02.6

Reply
technocn
technocn
Cadet

Posted: ‎2022-08-20 02:24 AM

In response to BillP
0 Likes
0
1334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-08-20 02:24 AM

Hi Bill/Robert,

 

I am just looking to see if you have access to the update procedure for the above mentioned APC unit. Seems to be a well hidden gem.

 

Thank you in advanced for your assistance.

 

Jamie

  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc