Fault: Batt Soft Start on SMX3000RMLV2U which support can not seem to resolve.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Fault: Batt Soft Start on SMX3000RMLV2U which support can not seem to resolve.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:01 AM . Last Modified: ‎2024-03-13 12:09 AM

0 Likes
16
7011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:01 AM . Last Modified: ‎2024-03-13 12:09 AM

Fault: Batt Soft Start on SMX3000RMLV2U which support can not seem to resolve.

Hello,

Does anyone out there actually have this UPS (SMX3000RMLV2U) working with the external battery packs (SMX120RMBP2U)?

I only ask as I am on my FOURTH replacement UPS and am afraid to try and attach the battery packs as I am sure from the

previous three experiences it will do the same thing.

Problem:

As soon as the SMX040 or the SMX039-2 battery cable is attached to the UPS it gives the fault BATT Soft Start.  This is with nothing attached to the other end of the extension cable.  It has happened THREE times to far.

"Insanity: doing the same thing over and over again and expecting different results."

  Albert Einstein 

Detail:

Brand new SMX3000RMLV2U.  Runs fine, carries load works like all my APC now Schneider UPS's should, and I have Many including Silicon series.

We purchased NEW battery packs SMX120RMBP2U for the NEW SMX3000RMLV2U UPS's because these are in remote closets and we wanted longer run times.  These have been mounted in an APC NetShelter Half Height racks.  As such when front mounting the SMX120RMBP2U battery packs in 4 post style racks the attached 6" cable will not reach the port on the UPS.  Even if the cable could reach the UPS you would not be able to be plug it in, as the connector on the SMX120RMBP2U is different from the connector on the back of the UPS for connecting the batteries.  It has little tabs on it.  Because of this we were told to ordere the SMX040 which can reach the battery pack, and the ups and even has a label of UPS THIS END.

Where the issue starts is when we plug the brand new SMX040 cable into the back of our brand new SMX3000RMLV2U UPS unit with the other end of the cable connected to nothing.  As soon as we turn on the UPS we get the message to contact APC support and the Fault of Batt Soft Start.  And now the internal battery reads .03v.  Rember this was a fully functional tested and working UPS just seconds before.

Please any suggestions?  Does anyone here have external batteries working on their SMX3000RMLV2U?

My Fourth UPS will be here shortly and I would really like to use the 2500.00 in batteries we have for it 3x SMX120RMBP2U but would really like to have a working UPS.

Charles.


Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:01 AM . Last Modified: ‎2024-03-13 12:09 AM

0 Likes
0
6998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:01 AM . Last Modified: ‎2024-03-13 12:09 AM

Was this problem able to be resolved? We are now experiencing the same fault.

SMX3000RMLV2U with 4x SMX120RMBP2U's. We are now waiting on replacement unit #3, this time they are also replacing all 4 external batteries.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:08 AM

0 Likes
0
6998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:08 AM

As we are about to receive the 4th UPS, we tried the cable only option

after we broke the first ups trying it with the battery connected.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 16
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:01 AM . Last Modified: ‎2024-03-13 12:09 AM

0 Likes
0
6999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:01 AM . Last Modified: ‎2024-03-13 12:09 AM

Was this problem able to be resolved? We are now experiencing the same fault.

SMX3000RMLV2U with 4x SMX120RMBP2U's. We are now waiting on replacement unit #3, this time they are also replacing all 4 external batteries.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:01 AM . Last Modified: ‎2024-03-13 12:09 AM

0 Likes
0
6998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:01 AM . Last Modified: ‎2024-03-13 12:09 AM

In both of these user's cases, have they made sure they are at the latest firmware Revision on the SMX 3000 UPS before connecting all these external batteries ?

  ( which are UPS 6.0 or UPS 2.1 depending on whether its ID:23 or ID: 10 )

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:01 AM . Last Modified: ‎2024-03-13 12:09 AM

0 Likes
0
6998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:01 AM . Last Modified: ‎2024-03-13 12:09 AM

I have PMed the case numbers

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:01 AM . Last Modified: ‎2024-03-13 12:09 AM

0 Likes
0
6998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:01 AM . Last Modified: ‎2024-03-13 12:09 AM

UPS Firmware 2: MCU 06.1

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:01 AM . Last Modified: ‎2024-03-13 12:08 AM

0 Likes
0
6998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:01 AM . Last Modified: ‎2024-03-13 12:08 AM

Hello,

Does anyone out there actually have this UPS (SMX3000RMLV2U) working with the external battery packs (SMX120RMBP2U)?

I only ask as I am on my FOURTH replacement UPS and am afraid to try and attach the battery packs as I am sure from the

previous three experiences it will do the same thing.

Problem:

As soon as the SMX040 or the SMX039-2 battery cable is attached to the UPS it gives the fault BATT Soft Start.  This is with nothing attached to the other end of the extension cable.  It has happened THREE times to far.

"Insanity: doing the same thing over and over again and expecting different results."

  Albert Einstein 

Detail:

Brand new SMX3000RMLV2U.  Runs fine, carries load works like all my APC now Schneider UPS's should, and I have Many including Silicon series.

We purchased NEW battery packs SMX120RMBP2U for the NEW SMX3000RMLV2U UPS's because these are in remote closets and we wanted longer run times.  These have been mounted in an APC NetShelter Half Height racks.  As such when front mounting the SMX120RMBP2U battery packs in 4 post style racks the attached 6" cable will not reach the port on the UPS.  Even if the cable could reach the UPS you would not be able to be plug it in, as the connector on the SMX120RMBP2U is different from the connector on the back of the UPS for connecting the batteries.  It has little tabs on it.  Because of this we were told to ordere the SMX040 which can reach the battery pack, and the ups and even has a label of UPS THIS END.

Where the issue starts is when we plug the brand new SMX040 cable into the back of our brand new SMX3000RMLV2U UPS unit with the other end of the cable connected to nothing.  As soon as we turn on the UPS we get the message to contact APC support and the Fault of Batt Soft Start.  And now the internal battery reads .03v.  Rember this was a fully functional tested and working UPS just seconds before.

Please any suggestions?  Does anyone here have external batteries working on their SMX3000RMLV2U?

My Fourth UPS will be here shortly and I would really like to use the 2500.00 in batteries we have for it 3x SMX120RMBP2U but would really like to have a working UPS.

Charles.


Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:01 AM . Last Modified: ‎2024-03-13 12:08 AM

0 Likes
0
6998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:01 AM . Last Modified: ‎2024-03-13 12:08 AM

I know at least for a start I will be looking up your cases and escalate as necessary. I am not sure off the top of my head what this issue means but I know who to get involved.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:01 AM . Last Modified: ‎2024-03-13 12:08 AM

0 Likes
0
6998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:01 AM . Last Modified: ‎2024-03-13 12:08 AM

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:01 AM . Last Modified: ‎2024-03-13 12:08 AM

0 Likes
0
6998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:01 AM . Last Modified: ‎2024-03-13 12:08 AM

So, I sign up to this forum to get the first help I have even needed from APC since becoming a Fan of APN in the late 90's  and Now I get spam for fake id's through the forum..  Great.

"

justine0 sent a direct message to You 

hello sir

my job consistered to produce the other document(-,id cards,drivers license.....) tell me your problem i disponible to you.

thanks

"

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:08 AM

0 Likes
0
6998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:08 AM

Sorry! You can adjust your email preferences if you want (but I know you shouldn't have to deal with spam) but we are constantly trying to find ways to combat spam like CAPTCHA and requiring email verification/activation and unfortunately, some spam does get through once in a while.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:08 AM

0 Likes
0
6998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:08 AM

What happens if you first plug the SMX040 into the External battery module (SMX120 ) and then plug it into the SMX 3000 ?  That process would make more sense to me due to the auto-sensing the SMX's have. If you plug the SMX040 into the UPS with nothing at the end of it perhaps the UPS thinks it has NO batteries connected period !

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:08 AM

0 Likes
0
6999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:08 AM

As we are about to receive the 4th UPS, we tried the cable only option

after we broke the first ups trying it with the battery connected.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:08 AM

0 Likes
0
6998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:08 AM

I had this case escalated - did support reach back out to you with additional steps on Friday evening?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:08 AM

0 Likes
0
6998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:08 AM

Yes, they contacted me for additional information and had me try one more

thing that did not work.

Hopefully the can look at the returned units and figure out what is going

on if that is even possible.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:08 AM

0 Likes
0
6998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:08 AM

Thank you again.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:07 AM

0 Likes
1
6998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:07 AM

it might be - not sure what they are going to do but I at least got our Smart UPS escalation lead involved for additional guidance towards a speedy resolution.

Reply

Link copied. Please paste this link to share this article on your social media post.

Lockjaw666
Lockjaw666
Cadet

Posted: ‎2022-08-19 05:12 AM

In response to BillP
0 Likes
0
6114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-19 05:12 AM

I had this same error code. I fixed it by opening up the SMX3000RMLV2U and taking out the one battery that was inside it. I replaced the battery with APC replacement battery, PCRBC117. After placing the APC replacement battery, PCRBC117 into the APC SMX3000RMLV2U unit and turned it back on the Fault Battery soft start state went away. 

 

When I plugged in just the SMX120RMBP2U unit, without changing the PCRBC117 replacement battery. I got the Fault Battery soft start state error.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of