SMTP alerts no longer working

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMTP alerts no longer working
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 06:00 AM . Last Modified: ‎2024-02-15 12:10 AM

0 Likes
1
1643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:00 AM . Last Modified: ‎2024-02-15 12:10 AM

SMTP alerts no longer working

Long post incoming....

I have a few Smart-UPS RT 6000 RM XL systems on my network that I have configured to send email alerts via a user/mailbox hosted in Office 365. This was working great, however after installing another unit today, my settings no longer work (according to the APC E-mail Test, and the email not reaching my address). I also checked my previously installed units, and they are also receiving the same error now. I'm currently receiving this error: 

Test e-mail failed; SMTP configuration error.
Last Server Response
220 2.0.0 SMTP server ready
My previous settings that were working correctly in the past, were:
SMTP Server: outlook.office365.com
Port: 587
Authentication Enabled (with a user/email with a real mailbox & password)
Use SSL/TLS: If Supported

These settings worked in the past, sending the alert from the specified mailbox to my address hosted within the same o365 org/domain.
Troubleshooting today, I've updated the NMC FW from v6.5.0 to v6.6.4. Also tried changing SMTP servers to smtp.office365.com, different ports (25,465,587), and Use SSL/TLS settings with no luck. Tested DNS, used an internal server and then Google DNS to verify name resolution. I've also referenced the APC documentation hosted here: https://www.apc.com/us/en/faqs/FA164769/ , still no luck.
I've confirmed that my firewall/web filter are not blocking this traffic. I also verified I can sign into this mailbox in o365 with the credentials provided within the Authentication settings on the UPS. 
I've ran out of ideas moving forward to troubleshoot, and why I'm posting, hoping someone can point something out that I may be missing.
Thank you in advance.
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-08 06:00 AM . Last Modified: ‎2024-02-15 12:10 AM

0 Likes
0
1643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:00 AM . Last Modified: ‎2024-02-15 12:10 AM

Oops. Forgot to mention that I have other devices on the same network (copier/scanners), using the same SMTP settings, that are currently functioning properly. These devices use a different o365 user. I even tried using that different account on the UPS, same error.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Anonymous user
Not applicable

Posted: ‎2021-07-08 06:00 AM . Last Modified: ‎2024-02-15 12:10 AM

0 Likes
0
1644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:00 AM . Last Modified: ‎2024-02-15 12:10 AM

Oops. Forgot to mention that I have other devices on the same network (copier/scanners), using the same SMTP settings, that are currently functioning properly. These devices use a different o365 user. I even tried using that different account on the UPS, same error.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore