APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-07-08 06:00 AM . Last Modified: 2024-02-15 12:11 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 06:00 AM . Last Modified: 2024-02-15 12:11 AM
I will soon install SRT3000xli + 2 battery pack SRT96BP + AP9631. I have a question about PowerChute behaviour during calibration. How it will consider the status of UPS? It will see that UPS is "on battery"? If I set a delay time for "UPS on battery" event, will PowerChute shutdown the system even if there is no AC fault? I would like to avoid that PCNS will shutdown the servers during calibration.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 06:00 AM . Last Modified: 2024-02-15 12:10 AM
Hello,
PowerChute will ignore the calibration test so the server/s will continue to run normally.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 06:00 AM . Last Modified: 2024-02-15 12:10 AM
Hello,
PowerChute will ignore the calibration test so the server/s will continue to run normally.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.