I will soon install SRT3000xli + 2 battery pack SRT96BP + AP9631. I have a question about PowerChute behaviour during calibration. How it will consider the status of UPS? It will see that UPS is "on battery"? If I set a delay time for "UPS on battery" event, will PowerChute shutdown the system even if there is no AC fault? I would like to avoid that PCNS will shutdown the servers during calibration.
Posted: 2021-07-08 06:00 AM
This reply was originally posted by Bill on APC forums on 1/2/2019
Hello,
PowerChute will ignore the calibration test so the server/s will continue to run normally.