SUA1500RM2U - AP9617 - APC 940-0020C serial cable not communicating, cant reset AP9617

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA1500RM2U - AP9617 - APC 940-0020C serial cable not communicating, cant reset AP9617
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Spazhead_apc
Spazhead_apc
Cadet

Posted: ‎2021-07-08 06:01 AM . Last Modified: ‎2024-02-15 12:10 AM

0 Likes
2
2297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:01 AM . Last Modified: ‎2024-02-15 12:10 AM

SUA1500RM2U - AP9617 - APC 940-0020C serial cable not communicating, cant reset AP9617

Hi, I bought a used SUA1500RM2U that came with the AP9617 management card.  I read in the manual that i need a APC serial cable to connect to PC to reset the AP9617.  I bought a new cable off ebay APC 940-0020C.  

I hooked up the serial and set my only serial port to 2400-8-N-1-N COM1 in windows

I used putty and set it to the same serial speed above.

pressed enter in putty, nothing on the screen.

tried different speeds 9600-8-N-1-N

reconnect with putty, no output on screen.

then i tried to do the reset procedure anyways.

pressed and released the reset button on AP9617 card,  LED flash quickly, I pressed and released the reset button again.

i then pressed my enter button continuously until the LED stop flashing and remained steady pressed some more.

Still no prompt on my PUTTY.

I then removed the AP9617 card out of the UPS think it may be defective.

try connecting serial with putty again, nothing on screen.

then i removed the battery from the AP9617 and left it alone for a week, hoping it would lose it settings, but still nothing.

any help is appreciated, or do i have a defective serial port an/or AP9617?

BTW, when I plug the UPS using the USB cable to my UNRAID server, it reads everything about the UPS no problem.

I just want to try to get the AP9617 card working

Thanks

 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 06:02 AM . Last Modified: ‎2024-02-15 12:10 AM

0 Likes
0
2296
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:02 AM . Last Modified: ‎2024-02-15 12:10 AM

Hi,

You need smart signalling cable 940-0024. Cable 940-0020 is simple signalling meaning it is one way communications. From UPS to computer. The smart signalling cable is two way. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-08 06:01 AM . Last Modified: ‎2024-02-15 12:10 AM

0 Likes
0
2296
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:01 AM . Last Modified: ‎2024-02-15 12:10 AM

I believe on that UPS using USB disables the serial port. To re-enable the serial port, unplug the UPS and its battery, wait for a few seconds for the fan to stop spinning and the lights to go out, and then re-assemble the unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 06:02 AM . Last Modified: ‎2024-02-15 12:10 AM

0 Likes
0
2297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:02 AM . Last Modified: ‎2024-02-15 12:10 AM

Hi,

You need smart signalling cable 940-0024. Cable 940-0020 is simple signalling meaning it is one way communications. From UPS to computer. The smart signalling cable is two way. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore