Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

SMT750I high idle power consumption

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: SMT750I high idle power consumption
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
tormento_apc
tormento_apc
Cadet

Posted: ‎2021-06-30 03:31 AM

0 Likes
12
2342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 03:31 AM

SMT750I high idle power consumption

This was originally posted on APC forums on 1/14/2011


Hi community, first post 😉

I have just bought a SMT750I to replace a SUA1000I that was a bit oversized and old.

I have been enchanted from the "green" word I read in a brochure but the previous model, as far as idle consumption is concerned, was greener indeed.

Test conditions:
-UPS attached to main power
-no load attached
-OFF position
-battery charged and 20 mins wait before test to make it stabilize
-wattmeter between plug and power cord

SUA1000I: ~50W
SMT750I: ~60W

I barely tolerated the idle power consumption of the SUA1000I but, hey, it was some years old when the word "green" was only for dollars and leaves.

Now, the SMT750I bad surprise, almost pi$$ed me off.

Why on hell should a turned-off-battery-charged-nothing-to-do UPS consume so much? Its more than 10% of the power it can output at full load! Even off it continuously produce a humming sound. Not as loud as when inverting power but noticeable.

If any APC technician is reading, please, provide me some sort of explanation and, please, a firmware to correct this bad behaviour.

Oh and, please, do not write green anymore on your products.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Occamsrazor
Ensign Occamsrazor
Ensign

Posted: ‎2021-08-29 12:37 AM

In response to tormento_apc
0 Likes
0
2275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-08-29 12:37 AM

Did you resolve this issue in some way? I'm looking at getting either an SMT750i or SMT3000ic and comparing idle power consumptions. One thing I've noticed is that if you look at the datasheets on the SE site, rather than the APC, site, it lists the idle consumption separately from BTU under "number of tare power" e.g.

 

SMT750i - https://www.se.com/ww/en/product/download-pdf/SMT750I

Number of tare power 15 W

Heat dissipation 90 Btu/H

 

or SMT3000i - https://www.se.com/ww/en/product/download-pdf/SMT3000I

Number of tare power 55 W

Heat dissipation 375 Btu

 

Though your real-world figures seem dramatically higher than that. Did you have a chance to retest?

 

See Answer In Context

  • Tags:
  • english
Reply
Replies 12
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 03:31 AM

0 Likes
0
2337
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 03:31 AM

This reply was originally posted by Llewellyn on APC forums on 12/5/2013


Just a quick question. When you say Idle power consume, do you mean the unit is still running and that you just don't have any load connected or is it actually power down/off and just connected to mains (brain still on)? If the the unit is still on try turning it off; it will still be charging the batteries if it is off but plugged into mains. If the unit is off already though it would be a good idea to check the internal cabling from the socket to the board as there could be a bad connection. Even check the input cable it self it might be fault as the IEC plugs can develop bad connections over time. So test the cable you are using according to your country standards...continuity, insulation, and cable resistance test.

  • Tags:
  • consumption
  • idle
  • off
  • smt750i
Reply
tormento_apc
tormento_apc
Cadet

Posted: ‎2021-06-30 03:31 AM

0 Likes
0
2337
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 03:31 AM

This was originally posted on APC forums on 1/14/2011


Hi community, first post 😉

I have just bought a SMT750I to replace a SUA1000I that was a bit oversized and old.

I have been enchanted from the "green" word I read in a brochure but the previous model, as far as idle consumption is concerned, was greener indeed.

Test conditions:
-UPS attached to main power
-no load attached
-OFF position
-battery charged and 20 mins wait before test to make it stabilize
-wattmeter between plug and power cord

SUA1000I: ~50W
SMT750I: ~60W

I barely tolerated the idle power consumption of the SUA1000I but, hey, it was some years old when the word "green" was only for dollars and leaves.

Now, the SMT750I bad surprise, almost pi$$ed me off.

Why on hell should a turned-off-battery-charged-nothing-to-do UPS consume so much? Its more than 10% of the power it can output at full load! Even off it continuously produce a humming sound. Not as loud as when inverting power but noticeable.

If any APC technician is reading, please, provide me some sort of explanation and, please, a firmware to correct this bad behaviour.

Oh and, please, do not write green anymore on your products.

Reply
marin849_apc
Ensign marin849_apc
Ensign

Posted: ‎2021-06-30 03:31 AM

0 Likes
0
2337
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 03:31 AM

This was originally posted on APC forums on 7/28/2011


Did you measure the idle power consumption after several (24) hours to be sure that the batteries weren't charging?

SMT750I should consume 90 BTU/hr according to spec. which is equal to 26,4 Watts.
SUA1000I should consume 100 BTU/hr which is equal to 29,3 Watts.

For reference, my SUA2200RMI2U is rated as 300 BTU/hr = 88 Watts, but I always measure 36-40W (active power) idle with the batteries fully charged and with management card AP9617 installed.

Given that my unit consumes significantly less than 300 BTU/hr I find it strange if SMT750i and SUA1000I should consume twice their rating!
Does your measurements take into account the power factor?

Reply
Olin_apc
Ensign Olin_apc
Ensign

Posted: ‎2021-06-30 03:31 AM

0 Likes
0
2337
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 03:31 AM

This was originally posted on APC forums on 7/28/2011


Why would you look at power consumed un-loaded? That's like one person in a bus complaining about fuel consumtion! Just like the bus it needs to be loaded for efficiency to increase.

To be green with no load, stop inverter, turn off the supply, very green 😉

Reply
marin849_apc
Ensign marin849_apc
Ensign

Posted: ‎2021-06-30 03:31 AM

0 Likes
0
2337
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 03:31 AM

This was originally posted on APC forums on 7/28/2011


The "idle power" is somewhat constant over the load range and can be said to be the power consumption of the UPS itself or the UPS overhead. Therefore the idle power is interesting to know.

Depending on the application it is not always desirable to have a constant full or near full load on the UPS. For example if
1. The desired backup-time should be more than something like 3-6 minutes (which becomes 2 minutes at the end of the battery service life!)
2. If the UPS must be able to power additional equipment that is not always on (like an administration terminal)
3. If more frequent battery transfers are expected (a fully loaded UPS that often has to switch to battery operation kills the batteries much faster).

If the idle power for SMT750I is in fact 60W (as suggested by the thread starter, but not by the official spec.) it is quite bad. I have a small server, a router/firewall, a switch and a VoIP-gateway which together consumes about 100W. That would be > 40 minutes of backup time with the SMT750I which is just perfect since all three statements above are valid for me. The efficiency would then be just 63% or an additional waste of 60% which is unacceptable. 60W 24/7 would also be 10% of my total power consumption!!!

Reply
marin849_apc
Ensign marin849_apc
Ensign

Posted: ‎2021-06-30 03:31 AM

0 Likes
0
2337
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 03:31 AM

This was originally posted on APC forums on 7/28/2011


According to http://www.apc.com/products/efficiency_loss_chart.cfm?base_sku=SMT750I&chartSize=large the power consumption of SMT750I itself must be 8 W or 12 VA which is 1/3 of the rated BTU/hr of 90.

A similar exercise for SMT750RMI2U gives 9,7W or 14 VA. This unit has a rating of only 46 BTU/hr (14W).

SMT2200RMI2U has a loss of 12W / 15 VA and a rating of 215 BTU/hr (63W).

The SMT750RMI2U is the only unit where the BTU/hr rating and the efficiency chart match. WHY? Are the numbers on the APC-website just made up? 🙂 I don't think so...

(I assumed 100% load in the efficiency chart to be either 500W or 750VA for the 750VA unit, and 1980W/2200VA for the 2200VA unit. The efficiency data is measured with a resistive load according to APC so I guess that the calculate W is the correct one and that 100% in the chart means 500W resistive load).

Reply
Olin_apc
Ensign Olin_apc
Ensign

Posted: ‎2021-06-30 03:31 AM

0 Likes
0
2337
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 03:31 AM

This was originally posted on APC forums on 7/28/2011


Somewhat consistent indeed.

1. Then the battery is poorly sized, not the UPS

2. Majority of UPS applications I deal with are 24/7 but if load were to be removed why not shut down the unit? Battery discharge will be minimal over short duration and have smal if any,l adverse effect on overall life.

3. I don't see the relevance of this point? But I agree standby specific batteries will be damaged by a high number of discharges.

Can we see input waveforms for the unit?

Reply
marin849_apc
Ensign marin849_apc
Ensign

Posted: ‎2021-06-30 03:32 AM

0 Likes
0
2337
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 03:32 AM

This was originally posted on APC forums on 7/28/2011


I don't own any SMT750I, I was just responding to the threadstarters claim that this unit has excessive idle power draw/overhead (which I doubt).
I'm still wondering about the lack of consistency between rated btu/hr and the efficiency chart for several Smart-UPSes.

Reply
Olin_apc
Ensign Olin_apc
Ensign

Posted: ‎2021-06-30 03:32 AM

0 Likes
0
2337
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 03:32 AM

This was originally posted on APC forums on 7/28/2011


I am doubting the results too. Impossible to tell remotely, can't be sure it is offline, not loaded or reliable test equipment is being used.

Reply
marin849_apc
Ensign marin849_apc
Ensign

Posted: ‎2021-06-30 03:32 AM

0 Likes
0
2337
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 03:32 AM

This was originally posted on APC forums on 8/14/2011


Now I have a SUA1000I.
Its idle power is 19.5 W with an AP9617 installed (without it 16.6 W). However the apparent power is 63 VA. Probably the thread starter used a crappy power meter that didn't measure the power factor correctly.

Reply
tormento_apc
tormento_apc
Cadet

Posted: ‎2021-06-30 03:32 AM

0 Likes
1
2337
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 03:32 AM

This was originally posted on APC forums on 1/14/2011


Fan? I noticed no fan... It is an electric noise coming from the unit even when off. However, any firmware upgrade is accepted 😉 Can you address me to a specific version or file name?

I leaved the unit attached all night long. I have used both a H+H SU201 unit (soho) and a professional ampere measure clamp.

I observed the unit for the whole morning ~4h.

P.S: I think it is almost useless to increase efficency for 1-3% and get such a high idle consumption..

Reply
Occamsrazor
Ensign Occamsrazor
Ensign

Posted: ‎2021-08-29 12:37 AM

In response to tormento_apc
0 Likes
0
2276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-08-29 12:37 AM

Did you resolve this issue in some way? I'm looking at getting either an SMT750i or SMT3000ic and comparing idle power consumptions. One thing I've noticed is that if you look at the datasheets on the SE site, rather than the APC, site, it lists the idle consumption separately from BTU under "number of tare power" e.g.

 

SMT750i - https://www.se.com/ww/en/product/download-pdf/SMT750I

Number of tare power 15 W

Heat dissipation 90 Btu/H

 

or SMT3000i - https://www.se.com/ww/en/product/download-pdf/SMT3000I

Number of tare power 55 W

Heat dissipation 375 Btu

 

Though your real-world figures seem dramatically higher than that. Did you have a chance to retest?

 

  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc