SMT1000 fan and firmware

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT1000 fan and firmware
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:28 AM . Last Modified: ‎2024-03-15 05:37 AM

0 Likes
10
2856
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:28 AM . Last Modified: ‎2024-03-15 05:37 AM

SMT1000 fan and firmware

Hello.

I was wondering if anyone knows the latest firmware available for the SMT1000 and whether it fixes the continuously running fan issue.  I have heard rumors of a fabled 9.x firmware for this device but have not been able to find it on the APC website.

Thanks for any assistance.

---Mark

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • smt1000
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Occamsrazor
Ensign Occamsrazor
Ensign

Posted: ‎2021-08-29 08:48 PM

In response to BillP
0 Likes
0
2827
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-29 08:48 PM

On 7/23/2020 11:20 AM, Liam said:

https://www.apc.com/us/en/faqs/index?page=content&id=FA281865

 

+1 The link to this is dead, would be helpful to have correct one

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:28 AM . Last Modified: ‎2024-03-15 05:37 AM

0 Likes
0
2857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:28 AM . Last Modified: ‎2024-03-15 05:37 AM

Hi Mark - 

The lastest firmware available would be dependent on your device ID. You can find this under the "about" menu on your LCD.

The firmware Upgrade wizard will update your unit to whatever is the latest revision available for your specific device ID:

https://www.apc.com/us/en/faqs/index?page=content&id=FA281865

 

There have been several updates to fan behaviors, but in most instances your fans will be running, just at the slow speed.

 

Thanks

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:28 AM . Last Modified: ‎2024-03-15 05:37 AM

0 Likes
0
2857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:28 AM . Last Modified: ‎2024-03-15 05:37 AM

Liam,

Thanks for the reply.

There is no "device ID" in the about menu---only the following:

  • Model:  Smart-UPS 1000
  • Part No:  SMT1000
  • Serial No: AS1040230498

The Firmware versions are:

  • UPS 07.1
  • MCU 05.0
  • UBL 7.20
  • MBL 05.0

When I ran the firmware update wizard (4.2.0) the only firmware that came with it was the one that is currently installed (7.1).

The reason I am asking is because I have had several of these SMT1000s for some time.  Unfortunately, these have all met various fates over the years and I am down to the last one.  However, this one unit is the only one that has a fan that runs all of the time when not using the battery or charging the battery.

Regards,

Mark

  • Tags:
  • fan
  • smt1000
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:28 AM . Last Modified: ‎2024-03-15 05:37 AM

0 Likes
0
2857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:28 AM . Last Modified: ‎2024-03-15 05:37 AM

Ahh, yes thats a very old unit. Unfortunately 7.1 is the last firmware release for that unit. Given its age, it is possible that a temperature sensor is out of calibration and that is why the fan is running all the time. There isn't much that can be done unfortunately.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:28 AM . Last Modified: ‎2024-03-15 05:37 AM

0 Likes
0
2857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:28 AM . Last Modified: ‎2024-03-15 05:37 AM

Indeed, it is old.  Got the bulk of them in the end of 2010 and beginning 2011.  All of them did very well (much better than the SMC1000-2U units that are giving me fits in the server room).  I just wish I hadn't replaced the batteries last month---before I noticed the fan problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:28 AM . Last Modified: ‎2024-03-15 05:37 AM

0 Likes
0
2857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:28 AM . Last Modified: ‎2024-03-15 05:37 AM

Well, I did find a use for the UPS.  We had a bunch of power outages the past few weeks and my secretary mentioned that whenever the Xerox Colorqube printer loses power it dumps a bunch of the $olid ink into the waste tray.  Seems appropriate to have a loud UPS next to a loud printer.

For all of the other Xerox Colorqube owners out there, you need a big UPS for them.  Don't go by the power consumption fiction in the product safety data sheets.  During the warm-up cycle (e.g. coming out of power saver mode and fires-up the heaters to melt the solid ink) the peak power is much higher than the stated "active" power consumption.  This is not a short-duration spike.  Rather it maintains a high load for the better part of a minute.  I have a 8580DN and it stabilizes at around 625W during this time occasionally spiking at 825W).

In our situation, the UPS only needs to hold power until the backup power generator starts (typically less than 30 seconds), so the SMT1000 seems an ideal fit.

  • Tags:
  • 8580dn
  • colorqube
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:28 AM . Last Modified: ‎2024-03-15 05:37 AM

0 Likes
0
2857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:28 AM . Last Modified: ‎2024-03-15 05:37 AM

Mark,

 

I just bought a new SMT1000 off somebody that is brand new never used but it does not seem to have a fan installed in the back. Your units had fans in the backside? Please advise just so i can confirm if that is an issue or something i need to install in my unit if at all possible.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:28 AM . Last Modified: ‎2024-03-15 05:37 AM

0 Likes
1
2857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:28 AM . Last Modified: ‎2024-03-15 05:37 AM

On 7/23/2020 11:20 AM, Liam said:

https://www.apc.com/us/en/faqs/index?page=content&id=FA281865

On 7/23/2020 11:20 AM, Liam said:

https://www.apc.com/us/en/faqs/index?page=content&id=FA281865

Hi Liam, I get a 404 error when trying to access this FA.  Can you please provide the correct link?

Thank you!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:28 AM . Last Modified: ‎2024-03-15 05:37 AM

0 Likes
0
2856
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:28 AM . Last Modified: ‎2024-03-15 05:37 AM

On 3/25/2021 1:59 PM, Tyler said:

Your units had fans in the backside?

No, It has the receptacles, card slot, power cord, etc. on the backside.  Holes for the fan are on either side.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:29 AM . Last Modified: ‎2024-03-15 05:37 AM

0 Likes
0
2856
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:29 AM . Last Modified: ‎2024-03-15 05:37 AM

Ah ok. Thanks for the clarification. I am just trying to see if I am able to install a fan in that spot like the SMT has on it just for heat concerns. Do you think that would be possible?

  • Tags:
  • smt1000
  • smt1500
Reply

Link copied. Please paste this link to share this article on your social media post.

Occamsrazor
Ensign Occamsrazor
Ensign

Posted: ‎2021-08-29 08:48 PM

In response to BillP
0 Likes
0
2828
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-29 08:48 PM

On 7/23/2020 11:20 AM, Liam said:

https://www.apc.com/us/en/faqs/index?page=content&id=FA281865

 

+1 The link to this is dead, would be helpful to have correct one

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore