SMT1500RMI2U output short on selftest or power trip
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-2212:14 AM
SMT1500RMI2U output short on selftest or power trip
Hello,
I have a UPS which is nearly 1 year old, and 1 month ago it started having issue when the self test runs or when I pull the plug.
The UPS will vibrate with loud noise for around 5 secs before cutting the output. It will log that the output has a short and the battery will drop to 60+ %.
When I reduce the load (by not turning on some equip) it does not have this issue.
I have a video, but unable to upload it here.
I have replaced the unit with RMA and the problem is still there.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-2204:40 AM
Based on what you stated up above one of the connected loads is shorted. Start off by removing all connected equipment. Plug in one load at a time until the system faults.
You may upload the video to YouTube and then provide the link here for review. 👍
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-2207:31 PM
I have actually asked the electrician to check and there is no short. This only happens when there is a self test or when I pull the plug to the UPS. I will check how to upload to youtube as I do not have youtube account