SMT1500C and loss of USB connection?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT1500C and loss of USB connection?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
139
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Psychor
Ensign Psychor
Ensign

Posted: β€Ž2021-08-28 02:54 PM . Last Modified: β€Ž2021-08-28 03:21 PM

0 Likes
13
5901
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-08-28 02:54 PM . Last Modified: β€Ž2021-08-28 03:21 PM

SMT1500C and loss of USB connection?

I just purchase a new SMT1500C. I have it connected to the Internet and connected to my PC via USB. I installed PCBE v10.0.02  on my PC to communicate with the UPS via USB.

 

If I disconnect and reconnect the USB cable the APC will be detected by PowerChute. But within a few minutes PowerChute will report a lost connection with the APC. The only way to fix this it to disconnect and reconnect the cable again. I tried connecting the USB cable to different ports on my PC.

 

I've looked this up via the Internet and this appears to be a common issue for other APC UPS owners. I didn't expect this to be an issue with their latest SMT series.

 

Does anyone know what's going on here? I've owned many SUA and SMT units and I've never had this issue.

 

Thank you.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX-RM
  • UPS Management Devices & PowerChute Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 13
Psychor
Ensign Psychor
Ensign

Posted: β€Ž2021-08-30 03:13 PM

0 Likes
10
5883
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-08-30 03:13 PM

So what I've found is that if you go under Device Manager and manually change the UPS APC driver to "HID UPS Battery" Windows will at least let you manage the UPS. However, this means that you can no longer use PowerChute as that requires a specific APC driver.

 

This is not an ideal fix. APC really needs to figure out what's going on with their USB hardware and/or their driver. But based on the above solution it leads me to believe the issue is more with their USB driver.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Psychor
Ensign Psychor
Ensign

Posted: β€Ž2021-09-05 03:57 PM

In response to Psychor
0 Likes
9
5804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-09-05 03:57 PM


@Psychor wrote:

So what I've found is that if you go under Device Manager and manually change the UPS APC driver to "HID UPS Battery" Windows will at least let you manage the UPS. However, this means that you can no longer use PowerChute as that requires a specific APC driver.

 

This is not an ideal fix. APC really needs to figure out what's going on with their USB hardware and/or their driver. But based on the above solution it leads me to believe the issue is more with their USB driver.


So I thought this was a valid workaround, bit it isn't. Windows will see the UPS, but think's you're on a laptop instead of a desktop. It keeps sending my desktop into sleep mode due to "low battery" warnings even though the UPS is at 98% battery.

 

I've been waiting over a week to hear from APC on this matter. πŸ˜

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-09-07 09:33 AM

0 Likes
1
5779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-09-07 09:33 AM

@Psychor 

 

What firmware is the SMT1500C running? You will find the firmware information via the LCD panel under About, UPS Firmware.

 

As for the computer going to sleep, what are the battery setting? Go to Control Panel, Power Options, Advanced Settings.

Power Option Settings.png

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Psychor
Ensign Psychor
Ensign

Posted: β€Ž2021-09-14 08:10 PM . Last Modified: β€Ž2021-09-14 08:52 PM

In response to BillP
0 Likes
0
5727
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-09-14 08:10 PM . Last Modified: β€Ž2021-09-14 08:52 PM


@BillP wrote:

@Psychor 

 

What firmware is the SMT1500C running? You will find the firmware information via the LCD panel under About, UPS Firmware.

 

As for the computer going to sleep, what are the battery setting? Go to Control Panel, Power Options, Advanced Settings.

Power Option Settings.png

 

 


@BillP,

 

I can only access the Windows battery configuration screen for the APC if I switch the USB driver within Windows to the generic Windows USB driver. If I use the APC USB driver the screen you display is disabled by Windows and you have to use PowerChute. However, I should be able to use PowerChute and not continue to have my USB connection drop.

 

APC sent me a second new SMT1500C. Both units shipped with firmware version 0.41. Both units do the exact same thing. Communication between the APC and PC, via USB, will work when first connecting the units and then the USB connection will randomly be lost. If I remove the USB cable and reconnect it connection between the APC and PC will be reestablish for a time and then it will drop out again.

 

It doesn't matter what USB port I use on my PC. I even posted a video of the issue below.

 

I really wish you all could forward this to the engineering team. This is an issue all over the APC forum.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Psychor
Ensign Psychor
Ensign

Posted: β€Ž2021-09-14 08:23 PM

In response to Psychor
0 Likes
8
5725
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-09-14 08:23 PM

So I can replicate the exact same issue on two band new APC UPS SMT1500C units. It doesn't matter what USB port I use on my PC - old (2) or new (3). But this issue isn't unique to me... people have posted this same exact issue on this forum for years. πŸ˜‘

 

I even captured a video of the issue occurring. I installed a fresh copy of the latest version of PowerChute Business for Windows with the UPS connected to my PC via USB. All went well and the UPS was detected. I navigated PowerChute for a little over a minute and around the 1:08 minute mark you can clearly see the USB connection randomly being lost.

 

https://youtu.be/kP_JEPXnyHY

 

Something is either wrong with the APC USB controller or their APC USB driver - maybe both.

 

If I connect my APC to my PC via a serial RJ45 to USB cable the UPS doesn't lose it's connection - go figure.

 

This is ridiculous!!!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-09-15 05:44 AM

In response to Psychor
0 Likes
6
5704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-09-15 05:44 AM

@Psychor 

 

Would you turn off Green Mode on the UPS. Then install PowerChute using USB comm and report back? To turn off Green Mode from the UPS LCD panel go to, Configuration, Green Mode, press enter, press the up or down arrow to change from Enabled to Disabled, press enter to save the setting. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Psychor
Ensign Psychor
Ensign

Posted: β€Ž2021-09-15 03:15 PM

In response to BillP
0 Likes
5
5691
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-09-15 03:15 PM


@BillP wrote:

@Psychor 

 

Would you turn off Green Mode on the UPS. Then install PowerChute using USB comm and report back? To turn off Green Mode from the UPS LCD panel go to, Configuration, Green Mode, press enter, press the up or down arrow to change from Enabled to Disabled, press enter to save the setting. 


Thanks for the suggestion, but it made no difference.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Vorlon13
Vorlon13
Cadet

Posted: β€Ž2022-01-07 04:47 AM

In response to Psychor
0 Likes
4
5120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2022-01-07 04:47 AM

Hello @Psychor ,

 

As i have exactly the same problem with my SMT1500 unit, did you find any solution to the loss of USB connection?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2022-01-10 01:50 PM

In response to Vorlon13
0 Likes
0
5098
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2022-01-10 01:50 PM

@Psychor 

 

From the LCD panel of the UPS, scroll to Configuration - Green Mode and disable Green Mode. Then hold the Up and Down arrows for 5 to 6 seconds. The UPS communications bus will reset. The UPS will provide output during the reset, so you do not need to power anything off. Once reset, install PowerChute. The UPS and system should communicate.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Psychor
Ensign Psychor
Ensign

Posted: β€Ž2022-01-10 03:29 PM

In response to Vorlon13
0 Likes
2
5092
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2022-01-10 03:29 PM

No. Though APC is aware of the issue. They had me run some test program to gather logs and I was told they're working on it. It's my hope that they actually are doing so.

 

I'm glad that more people are posting here to show that the issue is NOT in fact our computers, but the APC UPS itself.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2022-01-12 12:53 PM

In response to Psychor
0 Likes
1
5066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2022-01-12 12:53 PM

@Psychor 

 

Does the APC UPS battery driver load when PowerChute is installed as explained in FAQ FA164514?  

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Psychor
Ensign Psychor
Ensign

Posted: β€Ž2022-01-12 12:59 PM

In response to BillP
0 Likes
0
5063
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2022-01-12 12:59 PM

@BillP, we've been working together directly via email and phone. πŸ˜

 

Mind posting a link here though just in case this is something new we haven't tried?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Frozen
Frozen
Cadet

Posted: β€Ž2022-02-02 10:59 PM

In response to Psychor
0 Likes
0
4883
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2022-02-02 10:59 PM

Hello Psychor
I'm wondering if "serial RJ45 to USB cable the UPS" communication works normally?
We have been using apc ups in our company for years and there is a constant problem with interrupting communication via usb-usb.
UPS is powered by a computer that runs a large cooling system. It has already happened that the ups went out and consequently the cooling system stopped and intervention was needed.

Thx

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore