Power-cycling server outlet without OS shutdown via PowerChute?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Power-cycling server outlet without OS shutdown via PowerChute?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
hpadm
Crewman hpadm
Crewman

Posted: ‎2022-05-09 03:52 AM

0 Likes
4
2231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-09 03:52 AM

Power-cycling server outlet without OS shutdown via PowerChute?

The server has 2 power supplies. I need to cut power from the APC Smart-UPS for a moment to test the server's failover behavior.. In the PCBE web UI, I can see 'Shutdown Now' with an option for automatic delayed wakeup, which is exactly what I want. However, it appears to be tied to 'OS Shutdown'. I do not want the OS to shut down, since I want the failover test to happen under load. Can this specific thing be done via the remote UI?

Labels
  • Labels:
  • Business Power UPS
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2022-05-10 05:59 AM

In response to hpadm
1 Like
1
2168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-10 05:59 AM

@hpadm 

 

If you are running PowerChute 9.5 or above you will find the UPS information on the About page. 

SMT1500C About page.png

 

If the model is SMT1500, you can power cycle the outlets 

SMT1500C Outlet Control page.png

 

NOTE: IF you power cycle, the outlet group PowerChute is associated with PowerChute will trigger the OS shutdown. To prevent the OS shutdown associate the PowerChute Agent with another outlet group.

Example: PowerChute is connected to Group 1; however, I associated it with the Unswitched Group and then powered cycled Group 1.

SMT1500C Outlet Setup page.png

If the UPS does not have switchable outlets, you can not test without PowerChute triggering shutdown. That is by design as PowerChute main purpose is to protect the OS in the event of a power failure.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

hpadm
Crewman hpadm
Crewman

Posted: ‎2022-05-10 07:39 AM . Last Modified: ‎2022-05-10 07:46 AM

In response to BillP
0 Likes
0
2164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-10 07:39 AM . Last Modified: ‎2022-05-10 07:46 AM

Thank you for the extensive clarification.

 

Older APC UPSes seem to not be able to report the "UPS SKU" field, it is missing from the about page.

This UPS unfortunately only has one outlet group, the "Main outlet group", so the maneuver you described is not possible. I can however confirm that our new UPSes do allow this. I will remember this in case it comes up again.

If I remember right, the UPS front panel display has an option to immediately cut power to all outlets. So the function is there, but I suppose it makes sense for PowerChute to not include it, since it is a very niche thing, and it could cause damage if used improperly.

I have come up with a potential workaround. I could tell PowerChute to "shutdown now with delayed wakeup", set the delay to 12 minutes, then remotely turn the server back on and quickly do the test while the UPS outlet is still off. It would involve unneccessary server downtime, but that's not a problem in this case.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2022-05-09 10:43 AM

0 Likes
3
2212
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-09 10:43 AM

@hpadm 

 

What is the UPS model? 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

hpadm
Crewman hpadm
Crewman

Posted: ‎2022-05-09 11:12 AM

In response to BillP
0 Likes
2
2208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-09 11:12 AM

The model is unknown. It identifies as "Smart-UPS 1500" and shows a serial number implying mfg 07/2008, It does not list its model in the web UI. The UI looks the same as our 2020 UPSes, with maybe a few things missing. The shutdown options look the same.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2022-05-10 05:59 AM

In response to hpadm
1 Like
1
2169
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-10 05:59 AM

@hpadm 

 

If you are running PowerChute 9.5 or above you will find the UPS information on the About page. 

SMT1500C About page.png

 

If the model is SMT1500, you can power cycle the outlets 

SMT1500C Outlet Control page.png

 

NOTE: IF you power cycle, the outlet group PowerChute is associated with PowerChute will trigger the OS shutdown. To prevent the OS shutdown associate the PowerChute Agent with another outlet group.

Example: PowerChute is connected to Group 1; however, I associated it with the Unswitched Group and then powered cycled Group 1.

SMT1500C Outlet Setup page.png

If the UPS does not have switchable outlets, you can not test without PowerChute triggering shutdown. That is by design as PowerChute main purpose is to protect the OS in the event of a power failure.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

hpadm
Crewman hpadm
Crewman

Posted: ‎2022-05-10 07:39 AM . Last Modified: ‎2022-05-10 07:46 AM

In response to BillP
0 Likes
0
2165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-10 07:39 AM . Last Modified: ‎2022-05-10 07:46 AM

Thank you for the extensive clarification.

 

Older APC UPSes seem to not be able to report the "UPS SKU" field, it is missing from the about page.

This UPS unfortunately only has one outlet group, the "Main outlet group", so the maneuver you described is not possible. I can however confirm that our new UPSes do allow this. I will remember this in case it comes up again.

If I remember right, the UPS front panel display has an option to immediately cut power to all outlets. So the function is there, but I suppose it makes sense for PowerChute to not include it, since it is a very niche thing, and it could cause damage if used improperly.

I have come up with a potential workaround. I could tell PowerChute to "shutdown now with delayed wakeup", set the delay to 12 minutes, then remotely turn the server back on and quickly do the test while the UPS outlet is still off. It would involve unneccessary server downtime, but that's not a problem in this case.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore