SMT 3000 settings/options

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT 3000 settings/options
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
JoeK_KDS
JoeK_KDS
Cadet

Posted: ‎2024-02-02 09:47 AM . Last Modified: ‎2024-02-02 09:48 AM

0 Likes
3
516
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-02 09:47 AM . Last Modified: ‎2024-02-02 09:48 AM

SMT 3000 settings/options

Our business (engineering) uses 4x SMT3000RM2UNC to protect the servers and network equipment. We also have a generator and transfer switch that automatically start and switch over after a set duration in the event of an outage.

 

1. Regarding the SMT3000, does one of the settings adjust a 'wait period' when returning from battery to line power? If able, I am looking to stagger the switching times so that all 4x do not switch to generator power at the same time. I believe this may be the 'Turn On Delay' setting, but the documentation is not abundantly clear.

 

2. We have also had issues with the SMT3000s not returning to 'Online' when supplied by power from the generator. This did work when 1st commissioned. But as of a recent test all 4x UPSs would only momentarily go online before returning to battery. Electricians and ourselves have verified that the power looks quite clean (120v, 60hz, etc), we've adjusted the sensitivity to 'low' but are still not successful. Is the UPS capable of indicating why it refuses to go online?

 

Note: I did try to find other posts similar to my issue, but was unsuccessful. Also, I am facility maintenance and do not have open access to the UPSs. All tests and requests need to go through and be supported by our IT department.

 

Thanks in advance,

Joe

Labels
  • Labels:
  • Smart-UPS & Symmetra LX-RM
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Spock Teken
Spock

Posted: ‎2024-02-05 08:01 AM

0 Likes
2
491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-05 08:01 AM

The turn on delay is for the connected load(s) this option has no affect on the UPS transferring from AC line vs battery. You can adjust the upper and lower (voltage) transfer range of the unit.

 

Doing so will force the unit to accept higher / lower voltage before engaging its AVR circuit. Keeping in mind this doesn’t directly address the UPS transferring from AC to battery.

 

The (low) quality setting is the only thing that tells the UPS when to transfer over. I’d suggest you review the internal logs from the UPS to see what it thinks it sees in terms of voltage / frequency. Compare that to the actual UPS outlet when the lights out (generator) test is underway.

 

It’s not enough to just measure voltage & frequency. You must measure THD and view the sine wave on a scope. This will provide you the information as to how clean vs dirty the generator power is. A generator like any other motor requires ongoing maintenance and monitoring and as they age often times begin to output dirty power. More often than not it’s a timing issue, RPM, stator, generator, brush, to fuel related issues: Pressure, volume, filter etc.

At the end of the day it really doesn’t matter because the UPS is doing what it’s designed to do - and that’s provide clean uninterrupted power to the connected loads. 👍

 

Interested to see what the power looks like with a power quality meter attached when on generator at the UPS outlet. 

Reply

Link copied. Please paste this link to share this article on your social media post.

JoeK_KDS
JoeK_KDS
Cadet

Posted: ‎2024-02-06 01:31 PM

In response to Teken
0 Likes
1
473
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-06 01:31 PM

Hey Teken,

 

Thanks for the response.

 

In our ongoing efforts we had discovered that the generator (outside of audible range) was struggling to maintain its speed set-point while cold. A technician has adjusted the fuel pressure and cleaned the throttle body which greatly help with this. The UPSs now accept the power ~98% of the time when set to 'low' sensitivity.

 

Thanks for the info about THD. I believe we have a decent oscilloscope onsite, just waiting on someone to assist with using it. I will see about a power quality meter.

I will also inquire about the logs.

 

Thanks,

Joe

 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: ‎2024-02-07 05:30 AM

In response to JoeK_KDS
0 Likes
0
465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-07 05:30 AM

Hi Joe,

 

Great to hear and please do mark this question answered or solution provided if so.

 

Rock On . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of