seeSURTD6000RMXLP3U EPO draining battery?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • seeSURTD6000RMXLP3U EPO draining battery?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
tpangburn
tpangburn
Cadet

Posted: ‎2024-02-05 09:14 AM . Last Modified: ‎2024-02-05 09:16 AM

0 Likes
3
460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-05 09:14 AM . Last Modified: ‎2024-02-05 09:16 AM

seeSURTD6000RMXLP3U EPO draining battery?

We had a case on a test rack where we disconnected the power and had the EPO button on and the battery died over the weekend. Does the EPO button being set drain the battery when the unit is powered off? Its possible maybe the battery was going bad but I just wanted to see if the EPO would have anything to do with it?

Also how long can you leave the UPS unplugged assuming a fully charged battery can you leave the UPS off and un-powered?
  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Spock Teken
Spock

Posted: ‎2024-02-06 07:17 AM

0 Likes
0
446
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-06 07:17 AM

The EPO can be wired in two ways Normally Open (N.O.) or Normally Closed (N.C.). The preferred way is N.O. wiring configuration as N.C uses the UPS internal 24 VDC power circuit all the time. You can confirm which EPO wiring method is being used by looking at the (green, blue, grey) phoenix connector on the rear of the UPS EPO port.

 

If there is a jumper wire inserted in the screw ports it’s wired as N.C. You’ll want to validate the same on the EPO Switch in case they placed the jumper in there instead which isn’t very common but validate to be sure! ☝️

 

All battery cells lose power (self discharge) when at rest and depends on the chemistry, technology, temperature, age, and usage. You can look up the battery specifications and see what percentage of charge is lost simply by sitting idle. Keeping in mind those values and specs are based on a brand new cell.

 

You can get a rough idea of the battery cells in the UPS by completing a self test. If it fails immediately after being fully charged they need to be replaced. A more accurate method is to measure the internal resistance of the individual cells with a conductance tester. Measuring surface (voltage) charge is not accurate. 

A true test is loading the battery with a defined current draw and see if it reflects the specifications from the battery maker. Combined with measuring the internal resistance of the cell you can than know how good, bad, the cell is.

 

All we want to see is reasonable operation runtime based on a defined connected load. If it was 30 minutes when new and now it’s 1 minute it’s easy to decide. If the the runtime is 25 minutes that’s up to the company to decide balancing cost, uptime, reliability, and risk!

 

Regardless, batteries are consumable’s and should be budgeted for replacement like any other maintenance item in the business. The industry average is 3-5 years of service based on ideal conditions. 

 

 

 

 

 

 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

tpangburn
tpangburn
Cadet

Posted: ‎2024-02-06 01:03 PM

0 Likes
1
446
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-06 01:03 PM

So, I did find this answer in the FAQ (below) for that said your unplugging the UPS for over 24 hours you should unplug the batteries. That being said are the batteries disconnected when they are shipped to us when we buy them? I haven't gotten an answer from my end yet, so I am curious.

 

With SmartUPS RT (1kva to 10kva):

Any time a SmartUPS RT (1kva to 10kva) will be turned off without input power present, or allowed to operate in bypass for over 24 hours, the battery modules should be disconnected to prevent unnecessary discharge. Depending on the health of the batteries, they can discharge below start-up voltage (approximately 85vDC) within 72 hours if the UPS is not operating normally.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: ‎2024-02-07 05:24 AM

In response to tpangburn
0 Likes
0
435
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-07 05:24 AM

All units ship with the battery disconnected from the main system. Often times the ends of the connector is covered in a bright yellow caution tape.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of