hello , you need to use an original APC cable , the part number is 940-0144 , then you can Run a terminal program (such as HyperTerminal®) and configure the selected port for 9600 bps, 8 data bits, no parity, 1 stop bit, no flow control.
you cant do it with another communication cable.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:26 AM . Last Modified: 2024-02-14 10:21 PM
hello , you need to use an original APC cable , the part number is 940-0144 , then you can Run a terminal program (such as HyperTerminal®) and configure the selected port for 9600 bps, 8 data bits, no parity, 1 stop bit, no flow control.
you cant do it with another communication cable.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-06 12:59 AM
I am using the correct cables (with a USB adapter) on a pair of AP8959 units. I can connect to both units, but all I get is weird symbols at random intervals. It's basically as if the baud rate or serial parameters are wrong, but I am definitely using 57600,cs8,-parenb,-ixon,-ixany,-crtscts and the system definitely defaults to 1 stop bit (screen on a Linux system).
I've tried other baud rates as well with no luck. (2400, 4800, 9600, 19200, 38400, 57600, 115200, 230400).
Any other suggestions?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-06 08:45 PM
The correct hyperterminal settings are 9600 8 1 none none.
If that doesn't work then you most likely have a bad cable.