SMC1500 external battery pack (extended run)??

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMC1500 external battery pack (extended run)??
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

0 Likes
4
7663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

SMC1500 external battery pack (extended run)??

I have Googled as well as searched all over the APC site.  What is the part number for the external battery pack  for an SMC1500?   I can find them for other models (like the BR series), but none that claim to fit the SMC1500.   All the SMC1500 writeups mention the fact that one exists but nowhere have I seen a part number.

Thanks!

Les

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

0 Likes
0
7660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

No problem. Yes, I figured either we had a mistake somewhere or you may have seen mention of the quick battery disconnect and thought that may be the extended battery back connector. 

Let us know if you have any further questions on the extended run models after you take a look at the different options. SMX is probably the closest to SMC1500 features and cost though it is a different form factor. SRT/SURT are larger online UPS models that are not really similar to SMC in way of application, cost, etc. An older SUAxxxXL is very close but we just don't manufacture them anymore so you'd have to go used at your own risk. You also don't get the newer style unit with LCD. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

0 Likes
0
7660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

Hi Les,

SMC1500 only has an internal battery pack (RBC6). There is no extended run option. There is also no extended battery pack connection on the rear unfortunately. See below  

DvMFX0kt99RIz6tQCSn6PQ%3D%3D.jpegDvMFX0kt99RIz6tQCSn6PQ%3D%3D.jpeg

Can you show us any reference you found to extended run for this UPS model so we can see if something needs to be corrected?

Smart-UPS models with extended run options include those with the following prefix: SMX, SRT, SURT, and then the older SUA with XL at the end of the SKU. 

P.S. thanks for flagging the spam on the forum here. 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

0 Likes
0
7660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

Going back and reading carefully, in a lot of ads (example)

https://www.cdw.com/shop/products/APC-Smart-UPS-C-1500VA-LCD-UPS-900-Watt-1500-VA/2715152.aspx?pfm=s...

It mentions "The extended run models accept external battery packs for long runtime", while it doesnt say this unit is, I 'assumed' it was because the rear picture shows a battery plug.  Now that I have searched "smc1500 battery connector"  I do see that that is actually a disconnect and not an external plug. 

Thanks for the quick reply and sanity check!   Will look at the models you mentioned above.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

0 Likes
0
7661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

No problem. Yes, I figured either we had a mistake somewhere or you may have seen mention of the quick battery disconnect and thought that may be the extended battery back connector. 

Let us know if you have any further questions on the extended run models after you take a look at the different options. SMX is probably the closest to SMC1500 features and cost though it is a different form factor. SRT/SURT are larger online UPS models that are not really similar to SMC in way of application, cost, etc. An older SUAxxxXL is very close but we just don't manufacture them anymore so you'd have to go used at your own risk. You also don't get the newer style unit with LCD. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Delmar
Delmar
Cadet

Posted: ‎2022-07-09 07:29 PM . Last Modified: ‎2022-07-09 07:34 PM

0 Likes
0
7221
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-09 07:29 PM . Last Modified: ‎2022-07-09 07:34 PM

If you replace the INTERNAL batteries with larger capacity batteries will the SMC continue to run until low voltage shutdown, or ignore the battery voltage and shutdown based on time & load? I purchased a BR1000MS and it will ignore battery voltage and shutdown.

 

I have multiple XL units (love them!) but they are getting scarcer to find. I don’t care if the battery display is correct, just that the run time is extended. I run the UPS well under rated load and can add additional cooling to the H-bridge.

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore