Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Symmetra PX All-In-One 48kW, 400V Externa "'Non Smart" Battery Pack

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra PX All-In-One 48kW, 400V Externa "'Non Smart" Battery Pack
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Brukutu
Crewman Brukutu
Crewman

Posted: ‎2022-07-04 05:04 AM

1 Like
3
1427
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-04 05:04 AM

Symmetra PX All-In-One 48kW, 400V Externa "'Non Smart" Battery Pack

HI all.

 

I have installed "non smart" batteries into this UPS.  

UPS_BAT.jpeg

THe bank is made of 32x 105AmpH batteries.   +, CT, - connect to UPS.

 

All working very well. However I am not sure what to put into the External Battery Cabit capacity setting.

 

Common sense would tell me to put in 105amh. However, although the bank is 384 nominal Voltage DC, the UPS seems to report Center Tap voltage. Ie 221 fully charged (442V) or 192 fully discharged (384V).  This makes me think that it threats the top and botom as 2 banks,. ie. My amp hour should be 105 + 105 = 210. 

 

However, after reading a extract on this forum, i am VERY confused. If i had to follow this, my amph would be 32x 105 = 3360ampH which is most definatelly not correct. 

 

Quote:  (https://www.apc.com/us/en/faqs/FA156609/) 

"
In order to setup the external battery packs, please key in as (Ah of battery) x (total number of batteries).

Example 1:   If there are 16pcs of 5Ah battery in series (for 5kVA), the total Ah number is 5Ahx16pcs=80Ah.
Example 2:   If there are 16 pcs of 100 AH batteries in series(for 5 KVA), the total AH number is 100 AH x 16 pcs=1600 AH
Example 3:   If there are 2 strings of 16pcs of 5Ah battery in series (for 5kVA), the total Ah number is 5Ahx16pcsx2 strings=160Ah.
  
The 80Ah inside the table is the default setting for 5kVA/6kVA (1 EXB: 16pcs of 5Ah battery)
The default setting for 8kVA is 140Ah (1 EXB: 20pcs of 7Ah battery)
The default setting for 10kVA is 180Ah (1 EXB: 20pcs of 9Ah battery).
  
If “Ext total battery Ah” is set as 0, it means there is no external battery connected. "

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
SESA85534
SESA85534 Cadet
Cadet

Posted: ‎2022-07-06 03:48 AM

0 Likes
2
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-06 03:48 AM

Hello,

 

You are not the only person to be a bit confused with this. The high value seems strange but the calculation is straightforward.

Basically, it is is 32x 105 = 3360Ah which may seem high but it is correct. After all this UPS can provide up to 48KW so on full load we would have over 100A on full load so you should expect about the 3 hours runtime depending on the state of the batteries.

What can be confusing is when you think that this will deliver 1A for 3360 hours. However that would be at 12V but the DC Bus in a Symmetra is about 400V DC so when that is considered it makes more sense. 

 

For set up with non Schneider Electric batteries, refer to the manufacturers spec for the 3rd party batteries and program in the AHR into the “Ext Bat Cap: 0000Ah” menu.  

 

I hope this clarifies the issue.

 

Regards,

Joseph King

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Brukutu
Crewman Brukutu
Crewman

Posted: ‎2022-07-07 01:53 PM

In response to SESA85534
0 Likes
1
1360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-07 01:53 PM

Thank you for the response. 

I was working under the assumption the ampH value requested is relative to the bus voltage being 384. Ie. 105Ah at 384v.

 

i would calculate 480000W at 400V equals current of 120A. 120A draw on 400v dc making 52 minutes runtime assuming discharge to 0%. Please correct me if I am wrong here.  

however if what is asking is ampH relative to a 12V, then it makes sense to say 3360Ah

 

please clarify above. 

thank you. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

SESA85534
SESA85534 Cadet
Cadet

Posted: ‎2022-07-11 07:19 AM

In response to Brukutu
0 Likes
0
1319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-11 07:19 AM

 

Hello,

Apologies, my error.  Yes, you are right, 52 min is correct, however as the batteries get older this would reduce a bit.

I hope this clarifies the issue.  Thanks.

Regards,

Joseph King

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore