Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

Suggestions for debugging power quality issues?

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Suggestions for debugging power quality issues?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:36 AM

0 Likes
4
535
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 02:36 AM

Suggestions for debugging power quality issues?

This question was originally posted by Paul on APC forums on 4/4/2011


I have two SMT1500's... one that has been running fine and a second in another room (the office) that suddenly started switching on and off of line power Friday. The logs indicate "Power Failed" and then "Power Restored" a short time later, and by the time I got home to investigate the attached computer had shut down due to low battery and the UPS was switching back and forth every second, indicating 60Hz or 0Hz as it did, with voltage right in the normal range (between 118 and 122V). The data logs show nothing unusual all day, other than battery voltage decreasing and temperature increasing as the UPS battery drained.

I moved the UPS to another room today and it's happily charging... so there seems to be a power quality issue in the office, but nothing evident from the data logs, and nothing I can see with my trusty old multimeter. Other than dragging an oscilloscope home... any other ideas? I suppose I could hook up a resistor divider to a sound card input for a poor-man's o'scope, but that's not my first choice.

Edit: After being offline for the weekend (I unplugged it to stop the constant switching on and off) I charged it back up in another room and tried it again in the office tonight... "Good" power quality setting and no complaints... I disabled the audio alarms and I'm just going to let it sit for a day logging to see if the problem recurs.

Message was edited by: pmiranda

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:36 AM

0 Likes
0
535
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 02:36 AM

This reply was originally posted by Angela on APC forums on 4/5/2011


yes, that is a good idea. relay weld is no good 😞

See Answer In Context

Reply
Share
Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:36 AM

0 Likes
0
535
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 02:36 AM

This reply was originally posted by Angela on APC forums on 4/5/2011


alrighty. thats a good start to adjust power quality/sensitivity settings.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:36 AM

0 Likes
0
535
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 02:36 AM

This reply was originally posted by Paul on APC forums on 4/5/2011


I think this particular UPS might just be having trouble. After a couple quiet hours last night it started switching on and off then threw a "AVR Relay Weld" fault and refuses to do anything new, so when I get a chance I'll call the 800 number and get an RMA.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:36 AM

0 Likes
0
536
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 02:36 AM

This reply was originally posted by Angela on APC forums on 4/5/2011


yes, that is a good idea. relay weld is no good 😞

Reply
Share
cwholgm
cwholgm
Cadet

Posted: ‎2022-07-08 03:55 PM

0 Likes
0
450
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2022-07-08 03:55 PM

My issues are exactly as the OP describes but it is not a Relay weld. 

 

We have  UPS that switch  on and off battery intermittently.  This happens occasionally several times a minute but usually a couple times an hour.  IT happens  for a couple of days and then it goes away for a week or two.   

 

In our situation,   the switching on and off  happens across multiple UPS devices spread across the office on devices like a brand new Back-ups 1000 and 10 year old (new batteries!)  Back-UPS 1500 .  They do not click on and off all at the same time,  a click here and a click/beep there.   However it does not happen on ALL the UPSes... The one under my desk, a BackUps -750 of intermediate age is fine...   

 

First I thought it was bad batteries, nope.  Then, I thought it was the age of the UPSs  but new ones do the same thing.  I have tried adjusting sensitivity where that feature is available and that may help but not always.    We had an electrical contractor who does local industrial work come and shut down power for a day and do a "clean and torque" but that did not solve it either.  The electricians did find some loose neutral wires and it does seem like their visit might have improved the problem but has not solved it. 

 

I have watched the switching  happen with a multimeter connected to the line and there is no visible voltage drop or spike.  The power company lineman has come out and looked at the lines into the building and torqued those connections.  He saw nothing with a multimeter on the main service lines. 

 

For background, the building is light industrial with a delta high leg.  It used to be a laundromat and then a bakery.  We are light fabrication with  only 2  3 phase pieces of equipment  and the use of those does not seem to correlate with the issue.  We did install solar many years ago but shutting off the solar backfeed does not seem to affect the problem.  This problem started last fall and prior to that we had no problems for the previous 8-10 years we have been in the building.   No new major equipment was installed that would correspond to this problem starting. 

 

Any suggestions are tremendously appreciated.  It is driving us crazy! 

 

Many thanks!

Charles 

  • Tags:
  • english
Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.