SMART-UPS SRT 3000 Outlet 2 error Weird Errors

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMART-UPS SRT 3000 Outlet 2 error Weird Errors
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:27 AM

0 Likes
4
2108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:27 AM

SMART-UPS SRT 3000 Outlet 2 error Weird Errors

Good Morning,

We installed this unit a couple of weeks ago, and unfortunetly emailing logs was missed during the intial config. Now that we have the taken care of we are getting informational messages:

Date : 09/07/2017

Time : 13:52:50

Code : 0x0101

 Informational - UPS: Restored the local network management interface-to-UPS communication.

---------------------------------------------------------

Date : 09/07/2017

Time : 13:52:50

Code : 0x0185

 Informational - UPS: The power for switched outlet group 1, Outlet Group 1, is on.

-----------------------------------------------------------

Date : 09/07/2017

Time : 13:52:50

Code : 0x0185

Informational - UPS: The power for switched outlet group 2, Outlet Group 2, is on.

----------------------------------------------------------

Any thoughts, i can send screen shots with come guidance.

Thank You

MIke

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:26 AM

0 Likes
0
2106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:26 AM

I will work on getting the tar file.

Regarding the events i did check and those emails are from the same unit.

The time issue was due to a improper time config. I changed the NTP server and time zone. Which is why the logs are off.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:27 AM

0 Likes
0
2106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:27 AM

Hi Mike,

Can you extract the full event.txt log from your SRT? I think for SRT you probably have a newer Network Management Card firmware so if you can extract the .tar file mentioned, that is ideal. Instructions on doing log downloads are outlined here via a few different methods (depending on firmware)-> http://www.apc.com/us/en/faqs/FA156131 

It will be helpful to see the full event log because I have a feeling there is more to what is causing the messages you've posted so far.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:27 AM

0 Likes
0
2106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:27 AM

Here you go.

Thank You for the assistance.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:26 AM

0 Likes
0
2108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:26 AM

Hi Mike,

Here is what I see.

1.) You're at firmware 6.4.0. This is a few years old now. I don't think it is necessarily causing the problem I'll explain below but you may want to consider upgrading for bug fixes and enhancements, especially for the SRT UPS type you have.

2.) In the log, we have the below blurb. I'll paste the series of the events here and then explain what is occurring. This happens a few times in recent days:

09/06/2017	07:37:21	Device	UPS: Restored the local network management interface-to-UPS communication.	0x0101
09/06/2017	07:37:14	Device	Environment: Restored the local network management interface-to-integrated Environmental Monitor (Universal I/O at Port 1) communication.	0x0344
09/06/2017	07:37:11	System	Network service started. IPv6 address FE80::2C0:B7FF:FEDD:9451 assigned by link-local autoconfiguration.	0x0007
09/06/2017	07:37:09	System	Network service started. System IP is 10.10.1.19 from manually configured settings.	0x0007
09/06/2017	07:37:05	System	Network Interface restarted.

So, time wise, read events from bottom to top. Your SRT's embedded Network Management Card (NMC) is restarting its interface. We'll need to find out why that is and to do so, I need the full .tar file OR the individual debug.txt and dump.txt files. These files aid in telling us why the network interface restarted. There is an FAQ here (http://www.apc.com/us/en/faqs/FA156063) that talks a little bit about why we know the NMC reboots - sometimes it is expected, like after a major configuration change. Other times it is not expected or obvious and can be related to a failsafe mechanism. I see in your log there is no clear reason, hence the need for debug.txt and dump.txt. Depending on what I see in these files, I may suggest a firmware upgrade to monitor performance.

Back to the events and what they mean. The NMC network interface reboots (soft reboot), and then the rest of the events are normal status update messages that occur after a restart. Network service starts for IPv4 and IPv6 protocols. Then the environmental Universal I/O port initializes and establishes comm (if a temperature sensor or similar is connected). And then the NMC establishes communication with the UPS itself.

I do NOT see the following event types in the log file you pasted in your original message at the given time.. is it possible it is from a different UPS? The time is also 1300 hours for Sept 7th but your event log does not go that far ahead that yet into the afternoon?

Date : 09/07/2017
Time : 13:52:50
Code : 0x0185
 Informational - UPS: The power for switched outlet group 1, Outlet Group 1, is on

Date : 09/07/2017
Time : 13:52:50
Code : 0x0185
Informational - UPS: The power for switched outlet group 2, Outlet Group 2, is on.

Without seeing them in the log, these are other status messages that can occur after the UPS and its outlet groups turn on for one reason or another. In older firmwares, they used to show after a network interface soft restart like we are discussing here but it was misleading because people thought the outlet groups/UPS turned off when really it was just being reported as a current status message, like those others that I explained. Thus, I thought we had resolved that.

Timing aside, I do see outlet group on/off messages earlier in May, June, and August where your UPS was turning on and off and having power issues seemingly so those do seem normal and expected at those times.

Hope this helps!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:26 AM

0 Likes
0
2107
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:26 AM

I will work on getting the tar file.

Regarding the events i did check and those emails are from the same unit.

The time issue was due to a improper time config. I changed the NTP server and time zone. Which is why the logs are off.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of