Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

SMART UPS RT 2000 - SURT2000XLI

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMART UPS RT 2000 - SURT2000XLI
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:12 PM

0 Likes
10
2143
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:12 PM

SMART UPS RT 2000 - SURT2000XLI

Hello,

I do via APC PowerChute calibration batteries. I do that calibrations on 2years old batteries in UPS. I simulate 33% load on UPS.

Then I start calibration via APC PowerChute. When calibration stop all is looks like normal. But when I simulete more then 33% load UPS start discharging batteries. And I dont know why? Mains is present and in UPS range.

Please tell me where can be problem.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:39 AM . Last Modified: ‎2024-03-12 11:11 PM

0 Likes
0
2143
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:39 AM . Last Modified: ‎2024-03-12 11:11 PM

From the screenshot, I can tell the UPS is not on battery power, it is just indicating discharged, versus discharging or on battery. I need to know under battery status, what the reported runtime is when you put this load on the UPS?

I have a feeling that with the load, the UPS runtime is low and is within 2 minutes of a low battery signal time (which by default is two minutes and I cannot find a way you would've changed it via PowerChute). So, when the UPS is online and the runtime is very low, it would say discharged as shown in your screenshot.

The batteries are two years old so it is feasible they are beginning to have a reduced capacity.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:12 PM

0 Likes
0
2143
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:12 PM

OK, so yes, your problem is low runtime which is why you are getting the discharged message. What was the runtime before the calibration?

The other thing that you could do, if possible, is remove AC power from the UPS to see if it actually lasts longer than 2 minutes while running on battery power. The 2 minutes is an estimate so if the estimate is incorrect and the UPS runs for more like 30 minutes, then we have a different problem that we'll need to address. If the UPS runs for 2-3 minutes, then I'd say it is time to replace the batteries.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:12 PM

0 Likes
0
2142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:12 PM

I dont know what runtime before calibration because I dont looking for that.

I tray disconnect mains and UPS work on battery about 8 minutes on 850W load.

What problem I have now ? smile

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:12 PM

0 Likes
0
2142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:12 PM

Well, I know its a pain but one thing I want to point out is that since the batteries are two years old, be careful with the amount of discharges your doing on the batteries because then you're going to need to replace them anyway because of all of this testing. Deep discharges on a battery are not good.

I assume the runtime did not update at all after this last test? There is a manual calibration procedure but I don't really want to suggest that because by the time the runtime gets updated, it will be time for new batteries because of all of the testing.

Did you watch the runtime as it ran on battery too in order to see if it 'jumped' around and became more accurate while on battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:39 AM . Last Modified: ‎2024-03-12 11:12 PM

0 Likes
0
2142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:39 AM . Last Modified: ‎2024-03-12 11:12 PM

Okay I replace batteries and do runtime calibration via PowerChute.

Batteries is new. But UPS still flashing batteries leds and show me low runtime (2-4 minutes).

Please can you tell me where can be problem ?

I see in others forums: Maybe I need reset battery constant in UPS. But I dont know how.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:39 AM . Last Modified: ‎2024-03-12 11:12 PM

0 Likes
0
2142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:39 AM . Last Modified: ‎2024-03-12 11:12 PM

We cannot give battery constants out here anymore. You can try contacting your local support to see if they will but the calibration should address it. How long did the UPS run for with the software calibration?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:39 AM . Last Modified: ‎2024-03-12 11:11 PM

0 Likes
0
2143
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:39 AM . Last Modified: ‎2024-03-12 11:11 PM

Okay I try contacting local support.

I not remember exactly but it is about 25-35 minutes on 35% load.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:39 AM . Last Modified: ‎2024-03-12 11:11 PM

0 Likes
0
2143
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:39 AM . Last Modified: ‎2024-03-12 11:11 PM

Hello,

I do via APC PowerChute calibration batteries. I do that calibrations on 2years old batteries in UPS. I simulate 33% load on UPS.

Then I start calibration via APC PowerChute. When calibration stop all is looks like normal. But when I simulete more then 33% load UPS start discharging batteries. And I dont know why? Mains is present and in UPS range.

Please tell me where can be problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:39 AM . Last Modified: ‎2024-03-12 11:11 PM

0 Likes
0
2143
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:39 AM . Last Modified: ‎2024-03-12 11:11 PM

How can you tell the UPS is discharging its batteries? What indicator is telling you that? What is the reported runtime on the UPS after the calibration and when you simulate the 33% load afterwards?

Could you provide your log files from PowerChute during these tests for us to review?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:39 AM . Last Modified: ‎2024-03-12 11:11 PM

0 Likes
0
2143
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:39 AM . Last Modified: ‎2024-03-12 11:11 PM

When PowerChute calibration is complet ( I see it is complete because PowerChute have wrote complete in results) I let recharge batteries. When is full recharge i simulate on UPS 850W load ( bulb ). And then batteries indicator is flashing and when I go in PowerChute to the bookmark Status UPS. I see UPS is discharging but mains is present and it is UPS range.  please see picture I meake print screen from PowerChute.

1366_.jpg

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:39 AM . Last Modified: ‎2024-03-12 11:11 PM

0 Likes
0
2144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:39 AM . Last Modified: ‎2024-03-12 11:11 PM

From the screenshot, I can tell the UPS is not on battery power, it is just indicating discharged, versus discharging or on battery. I need to know under battery status, what the reported runtime is when you put this load on the UPS?

I have a feeling that with the load, the UPS runtime is low and is within 2 minutes of a low battery signal time (which by default is two minutes and I cannot find a way you would've changed it via PowerChute). So, when the UPS is online and the runtime is very low, it would say discharged as shown in your screenshot.

The batteries are two years old so it is feasible they are beginning to have a reduced capacity.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore