Posted: 2021-07-07 11:26 PM . Last Modified: 2024-02-29 11:56 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:26 PM . Last Modified: 2024-02-29 11:56 PM
Hello there,
We have a SMART UPS 3000 2U that is continuing to issue the follow alerts;
Critical - UPS: The battery power is too low to continue to support the load
Informational - UPS: A discharged battery condition no longer exists.
These occur within minutes of each other, and loop around in what seems to be a vicious circle.
The batteries were recently replaced, but the issue was still present prior to the change.
Is there anyone that could help me to rectify the issue? I can post all necessary information required, I'm just not sure what to start with!
Thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:26 PM . Last Modified: 2024-02-29 11:56 PM
The model number you posted (AP9617) is for the network management card. From the serial number on that card, at least the NMC is over 8 years old, so I would expect the UPS to be of a similar age. As an end user, my rule-of-thumb is to expect to replace the batteries after the unit is 2-3 years old, then replace the whole UPS after the replacement batteries fail after another 2 years or so. On the smaller UPS models, it isn't normally cost-effective to keep putting batteries in them after that point.
Having said that, your UPS may be fine and just need the calibration key as Angela suggested.
The most recent screenshot you posted said "Unacceptable utility voltage rate of change" which is unrelated to the batteries.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:26 PM . Last Modified: 2024-02-29 11:56 PM
Hi James,
Could you post the exact model number and serial number of the unit to begin? Also is the battery you replaced a genuine APC battery that is meant for this model UPS? Are you getting these alerts via an email from your NMC? Are you using any PowerChute software? Could you post your event and data logs to this post please?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:26 PM . Last Modified: 2024-02-29 11:56 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:26 PM . Last Modified: 2024-02-29 11:56 PM
Hi Jordan,
Thank you for your reply. Please find the requested details, below.
---------------------------------------------------------------------------------------------------------------------
Could you post the exact model number and serial number of the unit to begin?
Model No. AP9617
Serial No. ZA0639017580
Also is the battery you replaced a genuine APC battery that is meant for this model UPS?
No.
Are you getting these alerts via an email from your NMC?
Yes. The alerts come through to our helpdesk. The alerts are also displayed on the UPS webmin.
Are you using any PowerChute software?
No.
Data Logs
Date Time Event
08/19/2015 10:40:32 System: Web user 'admin' logged in from 10.50.4.37.
08/18/2015 09:48:00 System: Web user 'admin' logged out from 10.50.4.37.
08/18/2015 09:42:59 System: Web user 'admin' logged in from 10.50.4.37.
08/18/2015 09:11:39 System: Web user 'admin' logged out from 10.50.4.37.
08/18/2015 09:06:39 UPS: A discharged battery condition no longer exists.
08/18/2015 09:06:35 System: Web user 'admin' logged in from 10.50.4.37.
08/18/2015 09:06:19 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
08/18/2015 09:06:16 UPS: A discharged battery condition no longer exists.
08/18/2015 09:05:39 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
08/18/2015 09:05:35 UPS: A discharged battery condition no longer exists.
08/18/2015 09:05:34 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
08/18/2015 09:05:33 UPS: A discharged battery condition no longer exists.
08/18/2015 09:05:30 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
08/18/2015 09:05:20 UPS: A discharged battery condition no longer exists.
08/18/2015 09:05:09 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
08/18/2015 09:05:08 UPS: A discharged battery condition no longer exists.
08/18/2015 09:05:05 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
08/18/2015 09:05:04 UPS: A discharged battery condition no longer exists.
08/18/2015 09:04:54 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
08/18/2015 09:04:52 UPS: A discharged battery condition no longer exists.
08/18/2015 09:04:33 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
08/18/2015 09:04:23 UPS: A discharged battery condition no longer exists.
08/18/2015 09:04:18 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
08/18/2015 09:04:14 UPS: A discharged battery condition no longer exists.
08/18/2015 09:04:01 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
08/18/2015 09:03:46 UPS: A discharged battery condition no longer exists.
08/18/2015 09:03:42 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
08/18/2015 09:03:38 UPS: A discharged battery condition no longer exists.
08/18/2015 09:03:36 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
08/18/2015 09:03:28 UPS: A discharged battery condition no longer exists.
08/18/2015 09:02:19 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
08/18/2015 09:02:16 UPS: A discharged battery condition no longer exists.
08/18/2015 09:02:14 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
08/18/2015 09:02:10 UPS: A discharged battery condition no longer exists.
08/18/2015 08:55:48 System: Web user 'admin' logged out from 10.50.4.37.
08/18/2015 08:51:15 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
08/18/2015 08:51:15 UPS: Completed a runtime calibration.
08/18/2015 08:45:40 UPS: Started a runtime calibration.
08/18/2015 08:45:14 System: Configuration change. User link 2 name.
08/18/2015 08:45:14 System: Configuration change. User link 2 display name.
08/18/2015 08:44:38 System: Configuration change. User link 2 name.
08/18/2015 08:44:38 System: Configuration change. User link 2 display name.
08/18/2015 08:39:02 System: Web user 'admin' logged in from 10.50.4.37.
08/18/2015 08:31:49 System: Web user 'admin' logged out from 10.50.4.37.
08/18/2015 08:22:56 System: Web user 'admin' logged in from 10.50.4.37.
Event Logs
Smart-UPS 3000 RM
Date Time Vmin Vmax Vout Iout %Wout Freq %Cap Vbat TupsC %VAout
08/19/2015 10:41:59 243.3 243.3 243.3 4.40 35.1 50.00 100.0 55.35 22.9 36.4
08/19/2015 10:31:59 243.3 244.8 243.3 4.40 35.1 50.00 100.0 55.35 22.9 35.1
08/19/2015 10:21:59 243.3 243.3 243.3 4.40 37.0 50.00 100.0 55.35 23.4 35.1
08/19/2015 10:11:59 243.3 244.8 243.3 4.62 35.1 50.00 100.0 55.35 23.4 35.1
08/19/2015 10:01:59 244.8 244.8 244.8 4.40 35.7 50.25 100.0 55.35 22.9 37.0
08/19/2015 09:51:59 243.3 244.8 244.8 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/19/2015 09:41:59 244.8 244.8 244.8 4.40 35.1 50.00 100.0 55.35 22.9 37.0
08/19/2015 09:31:59 243.3 244.8 244.8 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/19/2015 09:21:59 243.3 244.8 244.8 4.40 36.4 50.00 100.0 55.35 22.9 35.1
08/19/2015 09:11:59 243.3 244.8 243.3 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/19/2015 09:01:59 243.3 244.8 244.8 4.40 35.1 50.00 100.0 55.35 22.9 35.1
08/19/2015 08:51:59 243.3 244.8 244.8 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/19/2015 08:41:59 244.8 244.8 244.8 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/19/2015 08:31:59 244.8 244.8 244.8 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/19/2015 08:21:59 244.8 244.8 244.8 4.40 35.1 50.00 100.0 55.35 22.9 35.1
08/19/2015 08:11:59 244.8 246.2 244.8 4.40 36.4 50.00 100.0 55.35 22.9 35.1
08/19/2015 08:01:59 246.2 246.2 246.2 4.40 35.7 50.25 100.0 55.35 22.9 35.1
08/19/2015 07:51:59 246.2 252.0 246.2 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/19/2015 07:41:59 249.1 250.5 250.5 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/19/2015 07:31:59 249.1 250.5 249.1 4.40 35.1 50.00 100.0 55.08 22.9 35.7
08/19/2015 07:21:59 249.1 250.5 249.1 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/19/2015 07:11:59 247.6 249.1 249.1 4.40 35.1 50.00 100.0 55.35 22.5 35.7
08/19/2015 07:01:59 241.9 249.1 249.1 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/19/2015 06:51:59 243.3 244.8 243.3 4.40 35.1 50.00 100.0 55.35 22.9 35.1
08/19/2015 06:41:59 244.8 246.2 244.8 4.40 35.1 50.00 100.0 55.35 22.9 35.1
08/19/2015 06:31:58 243.3 246.2 246.2 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/19/2015 06:21:58 243.3 244.8 243.3 4.40 35.1 50.00 100.0 55.35 22.9 35.1
08/19/2015 06:11:58 241.9 244.8 243.3 4.40 35.1 50.00 100.0 55.35 22.9 35.1
08/19/2015 06:01:58 244.8 244.8 244.8 4.40 35.1 50.00 100.0 55.35 22.9 37.0
08/19/2015 05:51:58 244.8 244.8 244.8 4.62 35.1 50.00 100.0 55.35 22.9 35.1
08/19/2015 05:41:58 244.8 246.2 244.8 4.40 35.1 50.00 100.0 55.35 22.9 35.1
08/19/2015 05:31:58 246.2 247.6 247.6 4.40 35.1 50.00 100.0 55.35 22.9 35.1
08/19/2015 05:21:58 247.6 247.6 247.6 4.40 35.7 50.00 100.0 55.35 22.9 37.0
08/19/2015 05:11:58 244.8 247.6 247.6 4.62 35.7 50.00 100.0 55.08 22.9 35.7
08/19/2015 05:01:58 246.2 247.6 246.2 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/19/2015 04:51:58 246.2 247.6 246.2 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/19/2015 04:41:58 247.6 247.6 247.6 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/19/2015 04:31:58 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/19/2015 04:21:58 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/19/2015 04:11:58 247.6 249.1 247.6 4.40 36.4 50.00 100.0 55.35 22.9 35.7
08/19/2015 04:01:58 247.6 249.1 249.1 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/19/2015 03:51:58 247.6 249.1 249.1 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/19/2015 03:41:58 247.6 249.1 247.6 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/19/2015 03:31:58 247.6 249.1 249.1 4.40 36.4 50.00 100.0 55.35 23.4 35.7
08/19/2015 03:21:58 249.1 249.1 249.1 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/19/2015 03:11:58 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/19/2015 03:01:58 247.6 249.1 249.1 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/19/2015 02:51:58 247.6 249.1 249.1 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/19/2015 02:41:58 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/19/2015 02:31:58 247.6 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/19/2015 02:21:58 247.6 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/19/2015 02:11:58 247.6 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/19/2015 02:01:58 247.6 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/19/2015 01:51:58 247.6 247.6 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/19/2015 01:41:58 246.2 247.6 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/19/2015 01:31:58 247.6 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/19/2015 01:21:58 247.6 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/19/2015 01:11:58 247.6 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/19/2015 01:01:58 247.6 247.6 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/19/2015 00:51:58 247.6 247.6 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/19/2015 00:41:57 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/19/2015 00:31:57 247.6 249.1 249.1 4.40 37.0 50.00 100.0 55.35 23.4 35.7
08/19/2015 00:21:57 247.6 249.1 249.1 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/19/2015 00:11:57 247.6 247.6 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/19/2015 00:01:57 247.6 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/18/2015 23:51:57 247.6 249.1 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/18/2015 23:41:57 247.6 249.1 249.1 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/18/2015 23:31:57 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/18/2015 23:21:57 247.6 249.1 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/18/2015 23:11:57 247.6 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/18/2015 23:01:57 246.2 247.6 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/18/2015 22:51:57 246.2 249.1 246.2 4.40 35.1 50.00 100.0 55.35 23.4 35.1
08/18/2015 22:41:57 247.6 249.1 247.6 4.40 36.4 50.25 100.0 55.35 23.4 35.7
08/18/2015 22:31:57 247.6 252.0 247.6 4.40 35.1 50.00 100.0 55.35 23.4 37.0
08/18/2015 22:21:57 250.5 252.0 252.0 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/18/2015 22:11:57 250.5 250.5 250.5 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/18/2015 22:01:57 249.1 250.5 250.5 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/18/2015 21:51:57 247.6 249.1 249.1 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/18/2015 21:41:57 246.2 247.6 247.6 4.40 36.4 50.00 100.0 55.35 23.4 35.7
08/18/2015 21:31:57 246.2 247.6 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/18/2015 21:21:57 246.2 252.0 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/18/2015 21:11:57 250.5 252.0 250.5 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/18/2015 21:01:57 249.1 250.5 250.5 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/18/2015 20:51:57 247.6 249.1 249.1 4.62 35.7 50.25 100.0 55.35 23.4 35.7
08/18/2015 20:41:57 244.8 249.1 249.1 4.40 35.1 50.25 100.0 55.35 23.4 35.7
08/18/2015 20:31:57 244.8 247.6 244.8 4.40 35.1 50.00 100.0 55.35 23.4 35.1
08/18/2015 20:21:57 244.8 246.2 246.2 4.40 35.1 50.00 100.0 55.35 23.4 35.1
08/18/2015 20:11:57 246.2 249.1 246.2 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/18/2015 20:01:57 249.1 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/18/2015 19:51:57 249.1 250.5 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/18/2015 19:41:57 247.6 249.1 249.1 4.40 36.4 50.00 100.0 55.35 23.4 35.7
08/18/2015 19:31:57 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/18/2015 19:21:57 249.1 250.5 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/18/2015 19:11:57 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/18/2015 19:01:57 247.6 249.1 249.1 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/18/2015 18:51:56 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.4 37.7
08/18/2015 18:41:56 247.6 249.1 249.1 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/18/2015 18:31:56 247.6 247.6 247.6 4.40 36.4 50.00 100.0 55.35 23.4 35.7
08/18/2015 18:21:56 246.2 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/18/2015 18:11:56 246.2 247.6 247.6 4.40 36.4 50.00 100.0 55.35 23.4 37.0
08/18/2015 18:01:56 246.2 247.6 246.2 4.40 35.1 50.00 100.0 55.35 23.4 35.1
08/18/2015 17:51:56 247.6 249.1 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/18/2015 17:41:56 247.6 249.1 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/18/2015 17:31:56 247.6 247.6 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/18/2015 17:21:56 246.2 250.5 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/18/2015 17:11:56 249.1 250.5 250.5 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/18/2015 17:01:56 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/18/2015 16:51:56 247.6 249.1 249.1 4.40 35.1 50.25 100.0 55.35 23.4 35.7
08/18/2015 16:41:56 247.6 249.1 249.1 4.40 36.4 50.00 100.0 55.35 23.4 37.0
08/18/2015 16:31:56 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/18/2015 16:21:56 247.6 252.0 247.6 4.62 35.1 50.00 100.0 55.35 23.4 35.7
08/18/2015 16:11:56 249.1 252.0 252.0 4.40 35.7 50.00 100.0 55.35 23.8 35.7
08/18/2015 16:01:56 249.1 250.5 250.5 4.40 35.1 50.00 100.0 55.35 23.8 35.7
08/18/2015 15:51:56 249.1 250.5 250.5 4.40 35.7 50.00 100.0 55.35 23.8 35.7
08/18/2015 15:41:56 249.1 250.5 249.1 4.40 35.7 50.00 100.0 55.35 23.8 35.7
08/18/2015 15:31:56 249.1 250.5 250.5 4.40 35.7 50.00 100.0 55.35 23.8 35.7
08/18/2015 15:21:56 249.1 250.5 249.1 4.40 35.1 50.00 100.0 55.35 23.8 35.7
08/18/2015 15:11:56 249.1 250.5 250.5 4.40 35.1 50.25 100.0 55.35 23.8 35.7
08/18/2015 15:01:56 249.1 249.1 249.1 4.40 35.1 50.00 100.0 55.35 23.8 35.7
08/18/2015 14:51:56 249.1 249.1 249.1 4.40 35.1 50.00 100.0 55.35 23.8 35.7
08/18/2015 14:41:56 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.8 35.7
08/18/2015 14:31:56 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 24.3 35.7
08/18/2015 14:21:56 247.6 249.1 247.6 4.40 35.1 50.00 100.0 55.35 23.8 35.7
08/18/2015 14:11:56 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.8 35.7
08/18/2015 14:01:56 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 23.8 35.7
08/18/2015 13:51:56 247.6 249.1 249.1 4.40 36.4 50.00 100.0 55.35 24.3 35.7
08/18/2015 13:41:56 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 24.3 35.7
08/18/2015 13:31:56 247.6 249.1 247.6 4.40 37.0 50.00 100.0 55.35 24.3 35.7
08/18/2015 13:21:56 247.6 249.1 247.6 4.40 35.1 50.00 100.0 55.35 24.3 35.7
08/18/2015 13:11:56 247.6 249.1 247.6 4.40 36.4 50.00 100.0 55.35 24.3 35.7
08/18/2015 13:01:56 247.6 249.1 247.6 4.62 36.4 50.00 100.0 55.35 24.3 35.7
08/18/2015 12:51:55 247.6 249.1 247.6 4.62 35.7 50.00 100.0 55.35 24.3 37.0
08/18/2015 12:41:55 247.6 249.1 247.6 4.62 35.7 50.00 100.0 55.35 24.7 35.7
08/18/2015 12:31:55 246.2 247.6 247.6 4.40 36.4 50.00 100.0 55.35 24.7 35.7
08/18/2015 12:21:55 246.2 247.6 247.6 4.62 36.4 50.00 100.0 55.35 24.7 37.0
08/18/2015 12:11:55 246.2 247.6 246.2 4.40 35.7 50.00 100.0 55.35 24.7 37.0
08/18/2015 12:01:55 246.2 247.6 246.2 4.62 36.4 50.00 100.0 55.35 24.7 37.0
08/18/2015 11:51:55 244.8 246.2 246.2 4.40 36.4 50.00 100.0 55.35 25.2 37.0
08/18/2015 11:41:55 246.2 246.2 246.2 4.62 37.7 50.00 100.0 55.35 25.2 37.0
08/18/2015 11:31:55 244.8 246.2 246.2 4.40 35.7 50.00 100.0 55.35 25.2 35.1
08/18/2015 11:21:55 246.2 246.2 246.2 4.62 36.4 50.00 100.0 55.35 25.2 37.0
08/18/2015 11:11:55 244.8 246.2 246.2 4.40 36.4 50.00 100.0 55.35 25.6 37.0
08/18/2015 11:01:55 244.8 246.2 246.2 4.62 35.7 50.00 100.0 55.35 25.6 35.1
08/18/2015 10:51:55 244.8 246.2 246.2 4.62 36.4 50.00 100.0 55.35 25.6 35.1
08/18/2015 10:41:55 244.8 246.2 244.8 4.62 37.0 50.00 100.0 55.35 25.6 37.0
08/18/2015 10:31:55 244.8 246.2 246.2 4.62 36.4 50.00 100.0 55.35 26.1 35.1
08/18/2015 10:21:55 244.8 246.2 244.8 4.40 36.4 50.00 96.0 55.35 26.1 37.0
08/18/2015 10:11:55 241.9 246.2 246.2 4.62 36.4 50.00 90.0 55.35 26.1 37.0
08/18/2015 10:01:55 241.9 243.3 241.9 4.62 35.7 50.00 82.0 55.35 26.1 36.4
08/18/2015 09:51:55 243.3 243.3 243.3 4.62 36.4 50.00 75.0 55.35 26.1 35.1
08/18/2015 09:41:55 243.3 244.8 243.3 4.62 35.7 50.25 68.0 55.35 25.6 36.4
08/18/2015 09:31:55 241.9 243.3 243.3 4.62 36.4 50.00 61.0 55.35 25.6 36.4
08/18/2015 09:21:55 241.9 243.3 241.9 4.62 35.7 50.00 54.0 55.35 25.2 36.4
08/18/2015 09:11:55 241.9 243.3 241.9 4.62 35.7 50.00 47.0 55.35 24.7 36.4
08/18/2015 09:01:55 241.9 243.3 241.9 4.62 36.4 50.00 40.0 54.81 23.8 36.4
08/18/2015 08:51:55 241.9 244.8 243.3 4.62 36.4 50.25 33.0 52.11 23.4 36.4
08/18/2015 08:41:55 241.9 244.8 243.3 4.62 35.7 50.00 100.0 55.35 22.5 37.0
08/18/2015 08:31:55 241.9 243.3 243.3 4.62 37.0 50.00 100.0 55.35 22.5 36.4
08/18/2015 08:21:55 243.3 244.8 243.3 4.40 35.7 50.00 100.0 55.35 22.5 36.4
08/18/2015 08:11:54 243.3 244.8 243.3 4.62 35.7 50.00 100.0 55.35 22.5 36.4
08/18/2015 08:01:54 241.9 244.8 244.8 4.62 37.0 50.00 100.0 55.35 22.5 37.0
08/18/2015 07:51:54 241.9 243.3 243.3 4.62 35.7 50.00 100.0 55.35 22.5 36.4
08/18/2015 07:41:54 241.9 243.3 243.3 4.40 35.7 50.00 100.0 55.35 22.5 35.1
08/18/2015 07:31:54 243.3 244.8 243.3 4.62 36.4 50.00 100.0 55.35 22.5 36.4
08/18/2015 07:21:54 244.8 244.8 244.8 4.40 35.7 50.00 100.0 55.35 22.5 35.1
08/18/2015 07:11:54 244.8 246.2 244.8 4.62 35.7 50.00 100.0 55.35 22.5 35.1
08/18/2015 07:01:54 244.8 246.2 244.8 4.40 35.7 50.00 100.0 55.35 22.5 35.1
08/18/2015 06:51:54 243.3 246.2 246.2 4.62 35.7 50.00 100.0 55.35 22.5 35.1
08/18/2015 06:41:54 243.3 244.8 244.8 4.40 35.7 50.00 100.0 55.35 22.5 35.1
08/18/2015 06:31:54 241.9 246.2 244.8 4.40 35.1 50.00 100.0 55.35 22.5 35.1
08/18/2015 06:21:54 243.3 243.3 243.3 4.40 35.7 50.00 100.0 55.35 22.9 36.4
08/18/2015 06:11:54 243.3 244.8 243.3 4.40 35.7 50.00 100.0 55.35 22.9 37.0
08/18/2015 06:01:54 243.3 244.8 244.8 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/18/2015 05:51:54 244.8 244.8 244.8 4.40 35.7 50.00 100.0 55.35 22.9 37.0
08/18/2015 05:41:54 244.8 247.6 244.8 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/18/2015 05:31:54 246.2 247.6 247.6 4.40 35.1 50.25 100.0 55.35 22.9 35.7
08/18/2015 05:21:54 247.6 247.6 247.6 4.40 35.1 50.25 100.0 55.35 22.9 35.7
08/18/2015 05:11:54 246.2 247.6 247.6 4.62 35.7 50.00 100.0 55.35 22.9 35.7
08/18/2015 05:01:54 246.2 247.6 246.2 4.40 35.1 50.00 100.0 55.35 22.9 35.1
08/18/2015 04:51:54 247.6 247.6 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/18/2015 04:41:54 246.2 247.6 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/18/2015 04:31:54 247.6 247.6 247.6 4.40 35.7 50.00 100.0 55.35 22.9 37.0
08/18/2015 04:21:54 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/18/2015 04:11:54 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/18/2015 04:01:54 247.6 249.1 247.6 4.40 36.4 50.00 100.0 55.35 22.9 35.7
08/18/2015 03:51:54 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.08 22.9 35.7
08/18/2015 03:41:54 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/18/2015 03:31:53 247.6 249.1 247.6 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/18/2015 03:21:53 247.6 249.1 247.6 4.40 36.4 50.00 100.0 55.35 22.9 35.7
08/18/2015 03:11:53 247.6 249.1 249.1 4.40 36.4 50.25 100.0 55.35 22.9 35.7
08/18/2015 03:01:53 247.6 249.1 247.6 4.40 36.4 50.25 100.0 55.35 23.4 35.7
08/18/2015 02:51:53 247.6 249.1 247.6 4.40 36.4 50.00 100.0 55.35 22.9 35.7
08/18/2015 02:41:53 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/18/2015 02:31:53 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/18/2015 02:21:53 249.1 250.5 249.1 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/18/2015 02:11:53 249.1 250.5 249.1 4.40 35.7 50.00 100.0 55.35 22.9 37.7
08/18/2015 02:01:53 249.1 249.1 249.1 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/18/2015 01:51:53 249.1 249.1 249.1 4.40 36.4 50.00 100.0 55.35 22.9 35.7
08/18/2015 01:41:53 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/18/2015 01:31:53 247.6 249.1 247.6 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/18/2015 01:21:53 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/18/2015 01:11:53 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/18/2015 01:01:53 247.6 249.1 249.1 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/18/2015 00:51:53 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/18/2015 00:41:53 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/18/2015 00:31:53 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/18/2015 00:21:53 247.6 249.1 249.1 4.40 35.7 50.25 100.0 55.35 22.9 35.7
08/18/2015 00:11:53 247.6 249.1 247.6 4.40 36.4 50.25 100.0 55.35 22.9 35.7
08/18/2015 00:01:53 247.6 249.1 247.6 4.40 35.7 50.25 100.0 55.35 22.9 35.7
08/17/2015 23:51:53 247.6 249.1 249.1 4.40 35.7 50.25 100.0 55.35 23.4 35.7
08/17/2015 23:41:53 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 23:31:53 247.6 252.0 247.6 4.62 35.1 50.25 100.0 55.35 22.9 35.7
08/17/2015 23:21:53 250.5 252.0 252.0 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/17/2015 23:11:53 250.5 252.0 252.0 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/17/2015 23:01:53 249.1 250.5 250.5 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 22:51:53 249.1 252.0 250.5 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 22:41:53 249.1 252.0 252.0 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 22:31:53 247.6 249.1 249.1 4.40 36.4 50.00 100.0 55.35 22.9 35.7
08/17/2015 22:21:53 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 22:11:53 246.2 247.6 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 22:01:53 246.2 247.6 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 21:51:53 244.8 246.2 246.2 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/17/2015 21:41:52 244.8 246.2 246.2 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/17/2015 21:31:52 244.8 246.2 244.8 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/17/2015 21:21:52 244.8 246.2 246.2 4.40 36.4 50.00 100.0 55.35 22.9 35.1
08/17/2015 21:11:52 244.8 244.8 244.8 4.40 35.1 50.00 100.0 55.35 22.9 35.1
08/17/2015 21:01:52 243.3 244.8 244.8 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/17/2015 20:51:52 243.3 244.8 243.3 4.62 35.7 50.00 100.0 55.35 22.9 36.4
08/17/2015 20:41:52 241.9 243.3 243.3 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/17/2015 20:31:52 241.9 243.3 241.9 4.62 35.7 50.00 100.0 55.35 22.9 36.4
08/17/2015 20:21:52 241.9 244.8 243.3 4.40 35.7 50.00 100.0 55.35 22.9 36.4
08/17/2015 20:11:52 244.8 244.8 244.8 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/17/2015 20:01:52 244.8 244.8 244.8 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/17/2015 19:51:52 244.8 244.8 244.8 4.40 35.1 50.00 100.0 55.35 23.4 35.1
08/17/2015 19:41:52 244.8 244.8 244.8 4.62 36.4 50.00 100.0 55.35 23.4 35.1
08/17/2015 19:31:52 244.8 244.8 244.8 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/17/2015 19:21:52 244.8 244.8 244.8 4.62 36.4 50.00 100.0 55.35 22.9 37.0
08/17/2015 19:11:52 244.8 244.8 244.8 4.62 35.7 50.00 100.0 55.35 22.9 35.1
08/17/2015 19:01:52 244.8 244.8 244.8 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/17/2015 18:51:52 244.8 246.2 244.8 4.40 35.1 50.00 100.0 55.35 23.4 35.1
08/17/2015 18:41:52 244.8 246.2 246.2 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/17/2015 18:31:52 244.8 246.2 244.8 4.40 35.1 50.00 100.0 55.35 23.4 35.1
08/17/2015 18:21:52 240.4 246.2 246.2 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/17/2015 18:11:52 246.2 247.6 246.2 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/17/2015 18:01:52 246.2 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/17/2015 17:51:52 246.2 247.6 247.6 4.40 36.4 50.00 100.0 55.35 23.4 35.7
08/17/2015 17:41:52 246.2 249.1 247.6 4.40 35.7 50.25 100.0 55.35 23.4 35.7
08/17/2015 17:31:52 249.1 250.5 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/17/2015 17:21:52 247.6 249.1 249.1 4.62 36.4 50.00 100.0 55.35 23.4 35.7
08/17/2015 17:11:52 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 17:01:52 246.2 247.6 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 16:51:52 247.6 247.6 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 16:41:52 246.2 247.6 247.6 4.62 35.7 50.00 100.0 55.35 23.4 35.7
08/17/2015 16:31:52 246.2 252.0 246.2 4.40 36.4 50.00 100.0 55.08 23.4 35.1
08/17/2015 16:21:52 249.1 250.5 250.5 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 16:11:52 250.5 250.5 250.5 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 16:01:52 249.1 250.5 250.5 4.40 35.1 50.00 100.0 55.08 22.9 35.7
08/17/2015 15:51:51 249.1 250.5 249.1 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/17/2015 15:41:51 249.1 250.5 249.1 4.40 35.1 50.25 100.0 55.35 22.9 35.7
08/17/2015 15:31:51 249.1 249.1 249.1 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 15:21:51 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 15:11:51 247.6 249.1 249.1 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/17/2015 15:01:51 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 14:51:51 247.6 249.1 249.1 4.62 35.7 50.00 100.0 55.35 22.9 37.7
08/17/2015 14:41:51 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 14:31:51 247.6 249.1 249.1 4.40 36.4 50.00 100.0 55.35 22.9 35.7
08/17/2015 14:21:51 247.6 249.1 247.6 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/17/2015 14:11:51 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 14:01:51 247.6 249.1 249.1 4.40 36.4 50.00 100.0 55.35 22.9 35.7
08/17/2015 13:51:51 247.6 249.1 247.6 4.40 36.4 50.00 100.0 55.35 22.9 35.7
08/17/2015 13:41:51 247.6 247.6 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 13:31:51 247.6 247.6 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 13:21:51 247.6 247.6 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 13:11:51 247.6 249.1 247.6 4.40 36.4 50.00 100.0 55.35 22.9 35.7
08/17/2015 13:01:51 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 12:51:51 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 12:41:51 246.2 247.6 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 12:31:51 246.2 247.6 247.6 4.40 35.7 50.00 100.0 55.35 22.9 37.0
08/17/2015 12:21:51 244.8 246.2 246.2 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/17/2015 12:11:51 244.8 246.2 246.2 4.40 36.4 50.00 100.0 55.35 22.9 35.1
08/17/2015 12:01:51 244.8 246.2 244.8 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/17/2015 11:51:51 244.8 244.8 244.8 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/17/2015 11:41:51 244.8 246.2 244.8 4.62 35.7 50.00 100.0 55.35 22.9 35.1
08/17/2015 11:31:51 244.8 246.2 244.8 4.40 36.4 50.00 100.0 55.35 22.9 35.1
08/17/2015 11:21:51 244.8 246.2 244.8 4.40 35.7 50.00 100.0 55.35 22.9 37.0
08/17/2015 11:11:51 244.8 246.2 244.8 4.62 35.1 50.00 100.0 55.08 22.9 35.1
08/17/2015 11:01:51 244.8 246.2 246.2 4.40 35.7 50.00 100.0 55.35 22.9 37.0
08/17/2015 10:51:51 244.8 246.2 246.2 4.62 35.7 50.00 100.0 55.35 22.9 35.1
08/17/2015 10:41:51 244.8 246.2 246.2 4.62 36.4 50.00 100.0 55.35 22.9 37.0
08/17/2015 10:31:51 244.8 246.2 246.2 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/17/2015 10:21:51 244.8 246.2 244.8 4.62 35.7 50.00 100.0 55.35 22.9 37.0
08/17/2015 10:11:51 244.8 246.2 246.2 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/17/2015 10:01:51 244.8 246.2 246.2 4.62 36.4 50.00 100.0 55.35 22.9 35.1
08/17/2015 09:51:50 244.8 246.2 244.8 4.62 36.4 50.00 100.0 55.35 22.9 35.1
08/17/2015 09:41:50 246.2 246.2 246.2 4.62 37.7 50.00 100.0 55.35 22.9 37.0
08/17/2015 09:31:50 244.8 246.2 246.2 4.40 36.4 50.00 100.0 55.35 22.9 35.1
08/17/2015 09:21:50 246.2 247.6 246.2 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/17/2015 09:11:50 246.2 247.6 246.2 4.40 35.7 50.25 100.0 55.35 22.9 35.1
08/17/2015 09:01:50 246.2 247.6 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 08:51:50 247.6 247.6 247.6 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/17/2015 08:41:50 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 08:31:50 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/17/2015 08:21:50 249.1 249.1 249.1 4.40 35.7 50.25 100.0 55.35 22.9 35.7
08/17/2015 08:11:50 246.2 249.1 249.1 4.40 36.4 50.00 100.0 55.35 22.9 35.7
08/17/2015 08:01:50 246.2 247.6 246.2 4.62 35.7 50.25 100.0 55.35 22.9 35.1
08/17/2015 07:51:50 241.9 247.6 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.1
08/17/2015 07:41:50 241.9 243.3 241.9 4.62 35.7 50.00 100.0 55.35 22.9 36.4
08/17/2015 07:31:50 243.3 244.8 243.3 4.40 35.1 50.25 100.0 55.35 22.9 35.1
08/17/2015 07:21:50 243.3 244.8 244.8 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/17/2015 07:11:50 244.8 246.2 244.8 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/17/2015 07:01:50 244.8 246.2 244.8 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/17/2015 06:51:50 243.3 244.8 244.8 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/17/2015 06:41:50 241.9 244.8 244.8 4.40 35.7 50.00 100.0 55.35 22.9 37.0
08/17/2015 06:31:50 244.8 246.2 244.8 4.40 35.7 50.25 100.0 55.35 22.9 35.1
08/17/2015 06:21:50 241.9 246.2 246.2 4.40 36.4 50.00 100.0 55.35 22.9 35.1
08/17/2015 06:11:50 243.3 244.8 243.3 4.62 36.4 50.00 100.0 55.35 22.9 36.4
08/17/2015 06:01:50 244.8 244.8 244.8 4.40 35.1 50.00 100.0 55.35 22.9 35.1
08/17/2015 05:51:50 244.8 244.8 244.8 4.62 35.7 50.00 100.0 55.35 23.4 35.1
08/17/2015 05:41:50 244.8 247.6 244.8 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/17/2015 05:31:50 247.6 247.6 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/17/2015 05:21:50 247.6 247.6 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/17/2015 05:11:50 246.2 247.6 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/17/2015 05:01:49 246.2 247.6 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/17/2015 04:51:49 247.6 247.6 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/17/2015 04:41:49 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/17/2015 04:31:49 249.1 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/17/2015 04:21:49 249.1 250.5 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/17/2015 04:11:49 249.1 250.5 249.1 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/17/2015 04:01:49 249.1 250.5 250.5 4.40 35.7 50.25 100.0 55.35 23.4 35.7
08/17/2015 03:51:49 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/17/2015 03:41:49 247.6 249.1 249.1 4.62 35.7 50.00 100.0 55.35 23.4 35.7
08/17/2015 03:31:49 247.6 249.1 247.6 4.40 36.4 50.00 100.0 55.35 23.4 35.7
08/17/2015 03:21:49 247.6 249.1 247.6 4.40 36.4 50.00 100.0 55.35 23.4 35.7
08/17/2015 03:11:49 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/17/2015 03:01:49 247.6 249.1 247.6 4.40 36.4 50.00 100.0 55.35 23.4 35.7
08/17/2015 02:51:49 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/17/2015 02:41:49 247.6 247.6 247.6 4.62 37.0 50.00 100.0 55.35 23.4 35.7
08/17/2015 02:31:49 247.6 249.1 247.6 4.40 36.4 50.00 100.0 55.08 23.4 37.0
08/17/2015 02:21:49 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.4 37.7
08/17/2015 02:11:49 246.2 249.1 247.6 4.62 37.0 50.00 100.0 55.35 23.4 35.7
08/17/2015 02:01:49 247.6 247.6 247.6 4.62 36.4 50.00 100.0 55.35 23.4 35.7
08/17/2015 01:51:49 247.6 247.6 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/17/2015 01:41:49 247.6 249.1 247.6 4.40 36.4 50.00 100.0 55.35 23.4 37.7
08/17/2015 01:31:49 247.6 249.1 247.6 4.40 35.7 50.25 100.0 55.35 23.4 35.7
08/17/2015 01:21:49 247.6 247.6 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/17/2015 01:11:49 247.6 247.6 247.6 4.62 37.7 50.00 100.0 55.35 23.4 37.0
08/17/2015 01:01:49 247.6 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/17/2015 00:51:49 247.6 247.6 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/17/2015 00:41:49 247.6 247.6 247.6 4.40 36.4 50.00 100.0 55.35 23.4 37.0
08/17/2015 00:31:49 247.6 249.1 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/17/2015 00:21:48 247.6 249.1 247.6 4.62 36.4 50.00 100.0 55.35 23.4 35.7
08/17/2015 00:11:48 247.6 247.6 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/17/2015 00:01:48 247.6 250.5 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/16/2015 23:51:48 247.6 249.1 249.1 4.40 35.1 50.00 100.0 55.35 23.4 37.7
08/16/2015 23:41:48 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/16/2015 23:31:48 247.6 247.6 247.6 4.62 35.1 50.00 100.0 55.35 23.4 37.0
08/16/2015 23:21:48 247.6 249.1 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 23:11:48 247.6 252.0 247.6 4.40 35.7 50.00 100.0 55.35 23.4 37.0
08/16/2015 23:01:48 250.5 252.0 252.0 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/16/2015 22:51:48 250.5 252.0 250.5 4.40 35.1 50.25 100.0 55.35 23.4 35.7
08/16/2015 22:41:48 249.1 250.5 250.5 4.62 35.7 50.00 100.0 55.35 23.4 35.7
08/16/2015 22:31:48 249.1 250.5 249.1 4.40 35.1 50.25 100.0 55.35 23.4 35.7
08/16/2015 22:21:48 249.1 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/16/2015 22:11:48 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/16/2015 22:01:48 246.2 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 21:51:48 246.2 253.4 246.2 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/16/2015 21:41:48 250.5 252.0 252.0 4.40 35.7 50.25 100.0 55.35 23.4 36.4
08/16/2015 21:31:48 250.5 252.0 250.5 4.40 34.4 50.00 100.0 55.35 23.4 35.7
08/16/2015 21:21:48 249.1 250.5 250.5 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 21:11:48 249.1 250.5 249.1 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 21:01:48 249.1 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/16/2015 20:51:48 247.6 249.1 249.1 4.40 35.7 50.25 100.0 55.35 23.4 35.7
08/16/2015 20:41:48 247.6 249.1 249.1 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 20:31:48 247.6 249.1 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 20:21:48 249.1 250.5 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/16/2015 20:11:48 249.1 250.5 249.1 4.62 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 20:01:48 249.1 250.5 250.5 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/16/2015 19:51:48 250.5 252.0 252.0 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 19:41:48 250.5 252.0 250.5 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/16/2015 19:31:48 250.5 252.0 250.5 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 19:21:48 250.5 252.0 252.0 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 19:11:48 250.5 252.0 250.5 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 19:01:48 249.1 250.5 250.5 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 18:51:48 250.5 250.5 250.5 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 18:41:47 249.1 250.5 250.5 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/16/2015 18:31:47 249.1 250.5 250.5 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 18:21:47 249.1 250.5 249.1 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 18:11:47 249.1 250.5 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/16/2015 18:01:47 249.1 250.5 249.1 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 17:51:47 249.1 250.5 250.5 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 17:41:47 249.1 250.5 249.1 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 17:31:47 249.1 250.5 250.5 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/16/2015 17:21:47 249.1 250.5 249.1 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 17:11:47 249.1 250.5 249.1 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 17:01:47 249.1 250.5 249.1 4.40 34.4 50.00 100.0 55.35 23.4 35.7
08/16/2015 16:51:47 249.1 250.5 250.5 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/16/2015 16:41:47 249.1 250.5 250.5 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 16:31:47 249.1 250.5 250.5 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/16/2015 16:21:47 250.5 252.0 250.5 4.40 35.1 50.25 100.0 55.35 23.4 35.7
08/16/2015 16:11:47 249.1 250.5 250.5 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 16:01:47 250.5 250.5 250.5 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/16/2015 15:51:47 250.5 250.5 250.5 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 15:41:47 250.5 250.5 250.5 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 15:31:47 250.5 250.5 250.5 4.40 36.4 50.00 100.0 55.35 23.4 35.7
08/16/2015 15:21:47 250.5 250.5 250.5 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 15:11:47 250.5 250.5 250.5 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 15:01:47 249.1 250.5 250.5 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/16/2015 14:51:47 250.5 250.5 250.5 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 14:41:47 250.5 250.5 250.5 4.40 36.4 50.00 100.0 55.35 23.4 35.7
08/16/2015 14:31:47 250.5 250.5 250.5 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 14:21:47 250.5 250.5 250.5 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 14:11:47 250.5 250.5 250.5 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 14:01:47 249.1 250.5 250.5 4.40 36.4 50.00 100.0 55.35 23.4 35.7
08/16/2015 13:51:47 249.1 250.5 249.1 4.40 34.4 50.00 100.0 55.35 23.4 35.7
08/16/2015 13:41:47 249.1 250.5 249.1 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 13:31:47 249.1 249.1 249.1 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 13:21:47 247.6 249.1 249.1 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 13:11:47 247.6 249.1 249.1 4.40 36.4 50.00 100.0 55.35 22.9 35.7
08/16/2015 13:01:47 247.6 249.1 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 12:51:47 247.6 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 12:41:46 246.2 247.6 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/16/2015 12:31:46 246.2 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 12:21:46 246.2 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 12:11:46 246.2 247.6 246.2 4.62 35.7 50.00 100.0 55.35 22.9 35.1
08/16/2015 12:01:46 246.2 247.6 247.6 4.40 35.1 50.00 100.0 55.35 22.9 35.1
08/16/2015 11:51:46 246.2 247.6 246.2 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/16/2015 11:41:46 246.2 247.6 246.2 4.40 35.1 50.00 100.0 55.08 23.4 35.1
08/16/2015 11:31:46 246.2 247.6 246.2 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 11:21:46 246.2 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 11:11:46 246.2 247.6 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/16/2015 11:01:46 247.6 247.6 247.6 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/16/2015 10:51:46 246.2 247.6 247.6 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/16/2015 10:41:46 246.2 246.2 246.2 4.40 35.1 50.00 100.0 55.35 23.4 35.1
08/16/2015 10:31:46 246.2 247.6 246.2 4.40 34.4 50.00 100.0 55.35 23.4 35.1
08/16/2015 10:21:46 246.2 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 10:11:46 246.2 247.6 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/16/2015 10:01:46 246.2 247.6 247.6 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/16/2015 09:51:46 246.2 247.6 247.6 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/16/2015 09:41:46 246.2 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 09:31:46 246.2 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 09:21:46 246.2 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 09:11:46 247.6 249.1 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 09:01:46 241.9 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/16/2015 08:51:46 243.3 243.3 243.3 4.40 35.1 50.00 100.0 55.35 23.4 35.1
08/16/2015 08:41:46 243.3 244.8 243.3 4.40 35.1 50.00 100.0 55.35 23.4 35.1
08/16/2015 08:31:46 243.3 244.8 244.8 4.40 35.7 50.25 100.0 55.35 23.4 35.1
08/16/2015 08:21:46 243.3 244.8 243.3 4.40 35.1 50.00 100.0 55.35 23.4 35.1
08/16/2015 08:11:46 244.8 244.8 244.8 4.40 35.1 50.00 100.0 55.35 23.4 35.1
08/16/2015 08:01:46 244.8 244.8 244.8 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/16/2015 07:51:46 244.8 246.2 244.8 4.40 37.0 50.00 100.0 55.35 23.4 35.1
08/16/2015 07:41:46 243.3 246.2 246.2 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/16/2015 07:31:46 243.3 244.8 243.3 4.40 35.1 50.00 100.0 55.35 23.8 35.1
08/16/2015 07:21:46 243.3 244.8 244.8 4.40 34.4 50.00 100.0 55.35 23.8 35.1
08/16/2015 07:11:46 244.8 244.8 244.8 4.62 37.0 50.00 100.0 55.35 23.8 35.1
08/16/2015 07:01:46 244.8 244.8 244.8 4.40 35.1 50.00 100.0 55.35 23.8 35.1
08/16/2015 06:51:45 244.8 246.2 244.8 4.40 34.4 50.00 100.0 55.35 23.8 35.1
08/16/2015 06:41:45 244.8 247.6 244.8 4.40 35.7 50.00 100.0 55.35 23.8 35.1
08/16/2015 06:31:45 246.2 247.6 246.2 4.40 35.7 50.00 100.0 55.35 23.8 35.7
08/16/2015 06:21:45 247.6 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.8 35.7
08/16/2015 06:11:45 247.6 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.8 35.7
08/16/2015 06:01:45 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 23.8 35.7
08/16/2015 05:51:45 247.6 249.1 249.1 4.40 35.1 50.00 100.0 55.35 23.8 35.7
08/16/2015 05:41:45 247.6 249.1 247.6 4.40 35.1 50.00 100.0 55.35 23.8 35.7
08/16/2015 05:31:45 249.1 249.1 249.1 4.40 35.1 50.00 100.0 55.35 23.8 35.7
08/16/2015 05:21:45 249.1 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.8 35.7
08/16/2015 05:11:45 249.1 250.5 249.1 4.40 35.7 50.00 100.0 55.35 23.8 35.7
08/16/2015 05:01:45 249.1 250.5 250.5 4.40 35.1 50.25 100.0 55.35 23.8 35.7
08/16/2015 04:51:45 249.1 250.5 249.1 4.40 34.4 50.00 100.0 55.35 23.8 35.7
08/16/2015 04:41:45 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.8 35.7
08/16/2015 04:31:45 249.1 250.5 249.1 4.40 35.1 50.00 100.0 55.35 23.8 35.7
08/16/2015 04:21:45 249.1 250.5 249.1 4.40 35.1 50.00 100.0 55.35 23.8 35.7
08/16/2015 04:11:45 249.1 250.5 249.1 4.40 35.1 50.00 100.0 55.35 23.8 35.7
08/16/2015 04:01:45 249.1 250.5 249.1 4.40 35.7 50.00 100.0 55.35 24.3 35.7
08/16/2015 03:51:45 249.1 250.5 249.1 4.40 35.1 50.00 100.0 55.35 23.8 35.7
08/16/2015 03:41:45 249.1 249.1 249.1 4.40 35.1 50.00 100.0 55.35 23.8 35.7
08/16/2015 03:31:45 249.1 250.5 249.1 4.40 35.1 50.00 100.0 55.35 24.3 35.7
08/16/2015 03:21:45 249.1 249.1 249.1 4.40 34.4 50.00 100.0 55.35 24.3 35.7
08/16/2015 03:11:45 249.1 249.1 249.1 4.40 36.4 50.00 100.0 55.35 24.3 35.7
08/16/2015 03:01:45 249.1 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.8 35.7
08/16/2015 02:51:45 249.1 250.5 249.1 4.40 35.1 50.00 100.0 55.35 23.8 35.7
08/16/2015 02:41:45 249.1 249.1 249.1 4.40 35.7 50.00 100.0 55.35 24.3 35.7
08/16/2015 02:31:45 249.1 249.1 249.1 4.40 36.4 50.00 100.0 55.35 24.3 35.7
08/16/2015 02:21:45 249.1 250.5 249.1 4.62 36.4 50.25 100.0 55.35 23.8 35.7
08/16/2015 02:11:45 249.1 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.8 35.7
08/16/2015 02:01:45 249.1 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.8 37.7
08/16/2015 01:51:45 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.8 35.7
08/16/2015 01:41:45 247.6 250.5 249.1 4.62 36.4 50.00 100.0 55.35 23.8 35.7
08/16/2015 01:31:45 247.6 250.5 249.1 4.62 35.1 50.25 100.0 55.35 23.8 35.7
08/16/2015 01:21:45 247.6 249.1 249.1 4.40 36.4 50.25 100.0 55.35 23.8 35.7
08/16/2015 01:11:45 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 23.8 35.7
08/16/2015 01:01:44 249.1 250.5 249.1 4.40 35.7 50.25 100.0 55.35 23.8 37.7
08/16/2015 00:51:44 249.1 250.5 250.5 4.40 35.7 50.00 100.0 55.35 23.8 37.7
08/16/2015 00:41:44 249.1 250.5 249.1 4.40 35.7 50.00 100.0 55.35 23.8 35.7
08/16/2015 00:31:44 249.1 250.5 250.5 4.62 36.4 50.25 100.0 55.35 23.8 35.7
08/16/2015 00:21:44 249.1 249.1 249.1 4.40 36.4 50.00 100.0 55.35 23.4 35.7
08/16/2015 00:11:44 247.6 249.1 249.1 4.40 36.4 50.00 100.0 55.35 23.4 35.7
08/16/2015 00:01:44 249.1 250.5 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/15/2015 23:51:44 247.6 249.1 249.1 4.40 36.4 50.00 100.0 55.35 23.8 35.7
08/15/2015 23:41:44 247.6 253.4 247.6 4.40 36.4 50.00 100.0 55.08 23.8 37.0
08/15/2015 23:31:44 252.0 252.0 252.0 4.40 36.4 50.00 100.0 55.35 23.8 35.7
08/15/2015 23:21:44 250.5 252.0 252.0 4.40 35.7 50.00 100.0 55.35 23.8 35.7
08/15/2015 23:11:44 250.5 250.5 250.5 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/15/2015 23:01:44 250.5 250.5 250.5 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/15/2015 22:51:44 249.1 250.5 250.5 4.40 36.4 50.00 100.0 55.35 23.4 35.7
08/15/2015 22:41:44 249.1 250.5 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/15/2015 22:31:44 247.6 250.5 250.5 4.62 35.7 50.25 100.0 55.35 23.4 35.7
08/15/2015 22:21:44 247.6 249.1 249.1 4.62 36.4 50.00 100.0 55.35 23.4 35.7
08/15/2015 22:11:44 246.2 247.6 247.6 4.40 36.4 50.00 100.0 55.35 23.4 37.0
08/15/2015 22:01:44 246.2 247.6 247.6 4.40 36.4 50.00 100.0 55.35 23.4 35.1
08/15/2015 21:51:44 246.2 246.2 246.2 4.40 36.4 50.00 100.0 55.35 23.4 35.1
08/15/2015 21:41:44 246.2 246.2 246.2 4.40 35.7 50.00 100.0 55.35 23.4 37.0
08/15/2015 21:31:44 244.8 246.2 246.2 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/15/2015 21:21:44 244.8 246.2 246.2 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/15/2015 21:11:44 244.8 246.2 246.2 4.40 35.1 50.25 100.0 55.35 23.4 35.1
08/15/2015 21:01:44 244.8 244.8 244.8 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/15/2015 20:51:44 244.8 244.8 244.8 4.40 35.1 50.00 100.0 55.35 23.8 35.1
08/15/2015 20:41:44 244.8 244.8 244.8 4.62 35.1 50.00 100.0 55.35 23.8 37.0
08/15/2015 20:31:44 244.8 244.8 244.8 4.40 35.7 50.00 100.0 55.35 23.8 35.1
08/15/2015 20:21:44 244.8 246.2 244.8 4.40 35.1 50.00 100.0 55.08 23.4 35.1
08/15/2015 20:11:44 246.2 247.6 246.2 4.40 35.1 50.00 100.0 55.35 23.4 35.1
08/15/2015 20:01:44 246.2 246.2 246.2 4.40 35.7 50.00 100.0 55.35 23.8 35.1
08/15/2015 19:51:44 246.2 247.6 246.2 4.40 35.1 50.00 100.0 55.35 23.8 35.1
08/15/2015 19:41:44 246.2 247.6 247.6 4.40 35.7 50.00 100.0 55.35 23.8 35.7
08/15/2015 19:31:43 246.2 247.6 247.6 4.40 35.7 50.00 100.0 55.35 23.8 35.7
08/15/2015 19:21:43 246.2 246.2 246.2 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/15/2015 19:11:43 244.8 246.2 246.2 4.40 35.1 50.00 100.0 55.35 23.4 35.1
08/15/2015 19:01:43 244.8 244.8 244.8 4.40 35.1 50.00 100.0 55.35 23.8 35.1
08/15/2015 18:51:43 244.8 244.8 244.8 4.40 36.4 50.00 100.0 55.35 23.8 35.1
08/15/2015 18:41:43 244.8 244.8 244.8 4.62 35.1 50.00 100.0 55.35 23.8 35.1
08/15/2015 18:31:43 244.8 244.8 244.8 4.40 35.1 50.00 100.0 55.35 23.8 35.1
08/15/2015 18:21:43 244.8 244.8 244.8 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/15/2015 18:11:43 244.8 244.8 244.8 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/15/2015 18:01:43 244.8 244.8 244.8 4.62 35.7 50.00 100.0 55.35 23.4 35.1
08/15/2015 17:51:43 244.8 244.8 244.8 4.40 35.1 50.00 100.0 55.35 23.4 35.1
08/15/2015 17:41:43 244.8 244.8 244.8 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/15/2015 17:31:43 244.8 244.8 244.8 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/15/2015 17:21:43 243.3 244.8 244.8 4.40 35.1 50.00 100.0 55.35 23.4 35.1
08/15/2015 17:11:43 243.3 244.8 243.3 4.62 35.7 50.00 100.0 55.35 23.4 35.1
08/15/2015 17:01:43 244.8 244.8 244.8 4.40 35.1 50.00 100.0 55.35 23.4 35.1
08/15/2015 16:51:43 243.3 244.8 244.8 4.40 35.1 50.00 100.0 55.35 23.4 35.1
08/15/2015 16:41:43 244.8 244.8 244.8 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/15/2015 16:31:43 244.8 244.8 244.8 4.62 35.1 50.00 100.0 55.35 23.4 35.1
08/15/2015 16:21:43 244.8 246.2 244.8 4.40 36.4 50.00 100.0 55.35 23.4 37.0
08/15/2015 16:11:43 244.8 246.2 244.8 4.40 35.1 50.25 100.0 55.35 23.4 35.1
08/15/2015 16:01:43 244.8 246.2 244.8 4.40 35.1 50.00 100.0 55.35 23.4 35.1
08/15/2015 15:51:43 244.8 246.2 244.8 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/15/2015 15:41:43 244.8 246.2 244.8 4.40 35.1 50.00 100.0 55.35 23.4 35.1
08/15/2015 15:31:43 246.2 246.2 246.2 4.40 35.1 50.00 100.0 55.35 23.4 35.1
08/15/2015 15:21:43 246.2 247.6 246.2 4.40 35.1 50.00 100.0 55.08 23.4 35.1
08/15/2015 15:11:43 246.2 247.6 246.2 4.40 35.7 50.00 100.0 55.35 23.4 35.1
08/15/2015 15:01:43 247.6 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/15/2015 14:51:43 246.2 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/15/2015 14:41:43 246.2 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/15/2015 14:31:43 246.2 247.6 246.2 4.40 35.1 50.00 100.0 55.35 23.4 35.1
08/15/2015 14:21:43 247.6 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/15/2015 14:11:43 247.6 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/15/2015 14:01:43 247.6 247.6 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/15/2015 13:51:43 247.6 252.0 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/15/2015 13:41:43 252.0 252.0 252.0 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/15/2015 13:31:42 252.0 252.0 252.0 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/15/2015 13:21:42 250.5 252.0 252.0 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/15/2015 13:11:42 250.5 250.5 250.5 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/15/2015 13:01:42 249.1 250.5 250.5 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/15/2015 12:51:42 249.1 250.5 250.5 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/15/2015 12:41:42 249.1 250.5 250.5 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/15/2015 12:31:42 249.1 249.1 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/15/2015 12:21:42 247.6 249.1 249.1 4.40 36.4 50.00 100.0 55.35 23.4 35.7
08/15/2015 12:11:42 249.1 250.5 249.1 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/15/2015 12:01:42 249.1 250.5 249.1 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/15/2015 11:51:42 249.1 250.5 249.1 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/15/2015 11:41:42 249.1 249.1 249.1 4.40 35.1 50.00 100.0 55.35 22.9 35.7
08/15/2015 11:31:42 247.6 249.1 249.1 4.40 35.7 50.00 100.0 55.35 22.9 35.7
08/15/2015 11:21:42 247.6 249.1 247.6 4.40 35.1 50.00 100.0 55.35 23.4 35.7
08/15/2015 11:11:42 247.6 249.1 247.6 4.40 35.7 50.00 100.0 55.35 23.4 35.7
08/15/2015 11:01:42 247.6 247.6 247.6 4.40 35.1 50.00 100.0 55.08 22.9 35.7
08/15/2015 10:51:42 246.2 247.6 247.6 4.40 35.7 50.00 100.0 55.35 22.9 35.7
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:26 PM . Last Modified: 2024-02-29 11:56 PM
What does the UPS report the runtime as? You probably need to do a runtime calibration if you just replaced the batteries or the batteries were old and the runtime didn't update properly upon putting the new ones in.
You get this alarm when the runtime remaining is within 2 minutes of the low battery duration value. Low battery duration is by default 2 minutes itself and is when the UPS deems a low battery. It is trying to tell you that your runtime is low essentially.
http://www.schneider-electric.us/support/index?page=content&country=US〈=en&locale=en_US&id=FA156538 has some information which you probably have flashing battery bar graph LEDs on the front panel of the UPS.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:26 PM . Last Modified: 2024-02-29 11:56 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:26 PM . Last Modified: 2024-02-29 11:56 PM
Hi James,
OK, I'd proceed with trying to issue a runtime calibration under UPS->Diagnostics menu within your management card and see what happens. Let me know if it does not work, then we'd explore a manual calibration or then obtaining a calibration key from tech support to fix the runtime reported by the UPS (knowing these are legit fresh batteries).
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:26 PM . Last Modified: 2024-02-29 11:56 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:26 PM . Last Modified: 2024-02-29 11:56 PM
Hi Angela,
Following a calibration shortly before I left work on Friday, the UPS fired plenty of alerts to our helpdesk during the weekend. Below is a screenshot of the admin panel as of Monday morning...
Ij05IWRgWPfYMTuFWtJC8Q%3D%3D.png
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:26 PM . Last Modified: 2024-02-29 11:56 PM
The model number you posted (AP9617) is for the network management card. From the serial number on that card, at least the NMC is over 8 years old, so I would expect the UPS to be of a similar age. As an end user, my rule-of-thumb is to expect to replace the batteries after the unit is 2-3 years old, then replace the whole UPS after the replacement batteries fail after another 2 years or so. On the smaller UPS models, it isn't normally cost-effective to keep putting batteries in them after that point.
Having said that, your UPS may be fine and just need the calibration key as Angela suggested.
The most recent screenshot you posted said "Unacceptable utility voltage rate of change" which is unrelated to the batteries.
Link copied. Please paste this link to share this article on your social media post.