APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-29 12:35 AM . Last Modified: 2024-03-14 12:39 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:35 AM . Last Modified: 2024-03-14 12:39 AM
Hello to everyone, I'm Alex from Italy. First time posting here I hope someone help me.
I've two Smart UPS 750VA and I've seen that one of these ups started to blinking the RIGHT LOAD Led at the same time...
The pdf manual doesn't give no info about it...
Thanks for your replay
Message was edited by: masterzone
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:36 AM . Last Modified: 2024-03-14 12:39 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:36 AM . Last Modified: 2024-03-14 12:39 AM
Hello to everyone, I'm Alex from Italy. First time posting here I hope someone help me.
I've two Smart UPS 750VA and I've seen that one of these ups started to blinking the RIGHT LOAD Led at the same time...
The pdf manual doesn't give no info about it...
Thanks for your replay
Message was edited by: masterzone
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:36 AM . Last Modified: 2024-03-14 12:39 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:36 AM . Last Modified: 2024-03-14 12:39 AM
Hi J, thanks for your replay, attached here you can find my serials takes by my camera.
1: the only devices attached here is my MacPro quadCore and two monitors, I'm around 50% of total load.
2: I don't know how long I've this kind of blinking because I placed it on the floor 😞
But why the manual does't give this kind of error?
Thanks
Alex
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:36 AM . Last Modified: 2024-03-14 12:39 AM
Is it the right most LED's that you are seeing flashing? The one that has a battery icon/ battery charge or the one that has the computer/ load icon?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:36 AM . Last Modified: 2024-03-14 12:39 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:36 AM . Last Modified: 2024-03-14 12:39 AM
Hi J, thanks for your time...I noticed blinking only the right (charghed battery leds) leds...all at the same time....not every time, but some time I see it blinking for some minutes...
alex
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:36 AM . Last Modified: 2024-03-14 12:39 AM
Alex,
If you are seeing flashing battery bar graph on your UPS it means that the runtime is within 2 minutes before the low battery signal. Have you added new things on your UPS? What is the current runtime that your UPS is showing? Have you replaced the battery? If not, when was the last time that you have replaced it? For troubleshooting I suggest that you run a software runtime calibration using PCBE (PowerChute Business Edition) or the network management card.
JonPro
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:36 AM . Last Modified: 2024-03-14 12:39 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:36 AM . Last Modified: 2024-03-14 12:39 AM
unfortunately I'm unable to see from PQ...because it doesn't run on Osx machine...so try to watch this video taken from my UPS.
Alex
http://www.c4dzone.it/IMG_0091.MOV
Message was edited by: masterzone
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:36 AM . Last Modified: 2024-03-14 12:39 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:36 AM . Last Modified: 2024-03-14 12:39 AM
Hello to everyone, I'm Alex from Italy. First time posting here I hope someone help me.
I've two Smart UPS 750VA and I've seen that one of these ups started to blinking the RIGHT LOAD Led at the same time...
The pdf manual doesn't give no info about it...
Thanks for your replay
Message was edited by: masterzone
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.