AP9617 card, seems to work intermittantly. Serial and network up/down.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9617 card, seems to work intermittantly. Serial and network up/down.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:40 AM

0 Likes
11
2011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:40 AM

AP9617 card, seems to work intermittantly. Serial and network up/down.

Yesterday is suddenly got a series of UPS online/Warmstart alerts in my email from my AP9617 in a Matrix 5000.

Now the AP9617 unit is not staying online (using network or serial) for longer than a few minutes at a time.
Most of the time it's down. (green light off during these times too)

Is this the kind of behavior that a bad battery would produce?
I have the latest firmware on all my AP9617 cards.

I even have configured them using the INI upload utility, and merely changed thier name and IP address.
All settigns therefore are identical.

Any thoughts from anyone on why this AP9617 would flap like this?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • ap9617
  • connectivity
  • down
  • green
  • light
  • network
  • no
  • serial
  • unavailable
  • unreachable
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:39 AM

0 Likes
0
2011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:39 AM

Yesterday is suddenly got a series of UPS online/Warmstart alerts in my email from my AP9617 in a Matrix 5000.

Now the AP9617 unit is not staying online (using network or serial) for longer than a few minutes at a time.
Most of the time it's down. (green light off during these times too)

Is this the kind of behavior that a bad battery would produce?
I have the latest firmware on all my AP9617 cards.

I even have configured them using the INI upload utility, and merely changed thier name and IP address.
All settigns therefore are identical.

Any thoughts from anyone on why this AP9617 would flap like this?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:40 AM

0 Likes
0
2011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:40 AM

Re-flashing to either restore the same aos/sumx rev or upgrade to 3.7.3/3.7.2 was going to be my suggestion - Gustavoc36 kindly beat me too it !

And yes if the firmware is very old (prior to 2.1.0 or something) you have to do it in stages. Older firmware revs are still available at APC's ftp site. ftp://ftp.apcc.com/apc/public/hardware/

Another thought that came to mind, is that if this is a very old Matrix ( IE 1993/94/95) they had an issue where the nmc card would sometimes starve the controller of power , so the recommendation was to install it in an AP9600 chassis with external power adapter. We still have a few Matrixes this old in service - amazing longevity !

...Dave

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:40 AM

0 Likes
0
2011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:40 AM

Serial is
ZA0602004442

I cannot gett event.txt becuase it wont stay up long enough. 😞

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:40 AM

0 Likes
0
2008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:40 AM

These can be replaced how?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:40 AM

0 Likes
0
2008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:40 AM

can you tell me the first few digits of the serial number on this AP9617? something like BA0834?

Also, can you please provide the event.txt for us to look at? that will give me some insight. you can download it via [this method|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=9321] if you are unsure of how to do it.

also, [this knowledgebase article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=2572] explains what a warmstart is and what can cause it, FYI.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:40 AM

0 Likes
0
2011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:40 AM

hmm ok. do you think you could reseat the card - meaning pull it out of the UPS for about 30 secs to a min and reinsert it into the slot? proper procedure on a Matrix is to put the UPS in bypass, reseat it, then take the UPS out of bypass. from my experience though, you should be just fine to reseat it though without going to bypass if you don't want to.

you said the status LED goes out when it does this - do you see it flashing rapidly indicating its definitely rebooting? i just want to make sure youre definitely looking at the LED with the X or checkmark next to it versus the 10/100 link LED, correct?

if you do a constant ping on the card, about how many ping responses will it stay up for?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:40 AM

0 Likes
0
2011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:40 AM

Definately looking at the righthand led.
It stats off all the time, not rebooting.

Pings shoe it's up for about 30-60 seconds, then dies.
Serial follows shortly after.

Card never recovers unless it reseat it. Then it repeats.

I have almost 6 of these. This is the only bad one so far.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:40 AM

0 Likes
0
2011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:40 AM

yeah its not normal, just wondering how we can fix it. if you cant catch the event log via FTP, can you gain serial or telnet access long enough to hit CTRL and L to view the event log and see what its doing? it sounds like it is an unrecoverable firmware error to be honest with you and may need to be replaced pending what you find in the event log. πŸ˜•

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:40 AM

0 Likes
0
2011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:40 AM

what do you mean? i mean getting (purchasing) a new/used AP9617 or a new, current AP9630.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:40 AM

0 Likes
0
2011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:40 AM

Ah, yes, well...

I was hoping to avoid that.
Let me see what i can do about being fast enough to get the event log.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:40 AM

0 Likes
0
2011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:40 AM

ok πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:39 AM

0 Likes
0
2012
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:35 AM . Last Modified: β€Ž2024-03-14 12:39 AM

Yesterday is suddenly got a series of UPS online/Warmstart alerts in my email from my AP9617 in a Matrix 5000.

Now the AP9617 unit is not staying online (using network or serial) for longer than a few minutes at a time.
Most of the time it's down. (green light off during these times too)

Is this the kind of behavior that a bad battery would produce?
I have the latest firmware on all my AP9617 cards.

I even have configured them using the INI upload utility, and merely changed thier name and IP address.
All settigns therefore are identical.

Any thoughts from anyone on why this AP9617 would flap like this?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore