Hi! can someone help me with this logs? What do this following means and the causes... I hope I can be enlightened.. I see our ups goes down not completely shut off but the message in the lcd is DC Charging: STOP, something like that.
Low dc warning
11.09.13 17.08,13
Logged mode:
Normal operation 11.09.13 17.08,11
Logged mode:
Stand by 11.09.13 17.08,11
Low dc shutdown
11.09.13 17.08,09
Low dc warning
11.09.13 17.08,08
System
Turned On 11.09.13 17.08,07
Logged mode:
Normal operation 11.09.13 17.08,07
Inverter voltage
error 11.09.13 17.08,06
Logged mode:
System off 11.09.13 17.07,00
Low dc warning
11.09.13 17.06,52
Low dc shutdown
11.09.13 17.06,52
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:27 AM . Last Modified: 2024-03-19 12:49 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:27 AM . Last Modified: 2024-03-19 12:49 AM
dear sir
i face the same problem with my apc silcon ups, did you resolved yours? how?
thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:27 AM . Last Modified: 2024-03-19 12:49 AM
Its hard to tell exactly what is going on, however Low DC Warning means that the UPS is running on battery and it is nearing the low voltage shutdown point. Low DC shutdown means exactly that, the UPS has reached its end of battery and shuts off the inverter. Did you have any utility disturbances at this time? How old are your batteries?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:27 AM . Last Modified: 2024-03-19 12:49 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:27 AM . Last Modified: 2024-03-19 12:49 AM
no there are no power disturbances, the batteries are just a year old.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:27 AM . Last Modified: 2024-03-19 12:49 AM
Hi Sir,
If you need assistance on your APC Silcon UPS, don't hesitate to call Clixlogic Inc. - The Authorized APC Service Center in the Philippines.
Here's our contact numbers:
Q.C Office - (02) 951-9661
Makati Office - (02) 553-4500
Cebu Office - (032) 239-7914
Davao Office - (082) 224-0238
Cagayan De Oro Office - (088) 309-0142
APC Service Center 24/7 Hotline - 0922-UPSHELP (8774357) / 09399157312
Just look for Giovanni.
Thanks,E
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:27 AM . Last Modified: 2024-03-19 12:49 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:27 AM . Last Modified: 2024-03-19 12:49 AM
dear sir
i face the same problem with my apc silcon ups, did you resolved yours? how?
thanks in advance