APC Silcon 60kW - What do all the abbreviations mean? e.g. Vbp1, %Wout...

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Silcon 60kW - What do all the abbreviations mean? e.g. Vbp1, %Wout...
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-26 05:26 AM . Last Modified: β€Ž2024-03-19 12:49 AM

0 Likes
5
2090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 05:26 AM . Last Modified: β€Ž2024-03-19 12:49 AM

APC Silcon 60kW - What do all the abbreviations mean? e.g. Vbp1, %Wout...

Hi,

I have a APC Silcon DP360E - 60kW 400V UPS in the DC and get the stats as data.txt via FTP. Now I would like to analyze the data, especially the efficiency and loss of the UPS. What do all the abbreviations mean? I made up a list, please correct me where I am wrong and explain it better:

Vmin - Voltage minimum (whats this, input, output, battery status?)
Vmax - Voltage maximum
Vbp - Bias Voltage? Whats that?
lin - L is a Live wire, so one value for each Live wire. Is it kW or % or what?
Vout - Voltage out
lout - Live wire out
%Wout -
kVA out - Apparent power out
Vbat - The actual Voltage of the batteries
lbat -

Besides the last two entries every value is there 3 times (e.g. Vmin1, Vmin2, Vmin3) for the three Live wires. When do I have to add the values and when do I have to calculate the average? As you can see I am not a electrician πŸ™‚

Help would be nice, thanks!

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-26 05:27 AM . Last Modified: β€Ž2024-03-19 12:49 AM

0 Likes
0
2090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 05:27 AM . Last Modified: β€Ž2024-03-19 12:49 AM

You are great! Thank you very much!

Thanks to your answer I now have more questions... πŸ™‚

On the display of the UPS is says "Load: 32%". Just this single value. But in the data.txt the 3 values for %Wout are always about 21 or 22 each. Why is that?

Iin and Iout are only integer values. Is that enough as a measurement or is it possible to get more precise values (with comma)?

For Ibat there are only the values 0.0 and 1.0. What does that mean? Does 0.0 mean that the batteries where not charged in the last 10 minutes and 1.0 means that they got charged a little bit?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: β€Ž2021-06-26 05:27 AM . Last Modified: β€Ž2024-03-19 12:49 AM

0 Likes
0
2091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 05:27 AM . Last Modified: β€Ž2024-03-19 12:49 AM

You are great! Thank you very much!

Thanks to your answer I now have more questions... πŸ™‚

On the display of the UPS is says "Load: 32%". Just this single value. But in the data.txt the 3 values for %Wout are always about 21 or 22 each. Why is that?

Iin and Iout are only integer values. Is that enough as a measurement or is it possible to get more precise values (with comma)?

For Ibat there are only the values 0.0 and 1.0. What does that mean? Does 0.0 mean that the batteries where not charged in the last 10 minutes and 1.0 means that they got charged a little bit?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-26 05:27 AM . Last Modified: β€Ž2024-03-19 12:49 AM

0 Likes
0
2090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 05:27 AM . Last Modified: β€Ž2024-03-19 12:49 AM

hi

i dont know much about 3 phase UPSs specifically but i do know the management card.


Vmin - this is the minimum input line voltage that the UPS saw within the logging interval (defaults to 10 minutes in most applications) - you might see a value for 1, 2, 3 for each phase
Vmax - this is the maximum input line voltage that the UPS saw within the logging interval (defaults to 10 minutes in most applications) - you might see a value for 1, 2, 3 for each phase
Vbp - these values will be your bypass mode voltages.
lin - the first letter is the letter "i" is a universal indicator for Current. This is your input current on each phase.
Vout - Voltage out for each phase
lout - This is actually an "i" so this is current out for each phase if you see a Iout1, 2 and 3.
*%Wout* - percentage of wattage out. this is based on the unit's rated capacity.
kVA out - Apparent power out - yes, thousands of volt amps. so if it says 1.4, thats 1400 volt amps out.
Vbat - The actual Voltage of the batteries
lbat - battery current. again, the letter is an 'i'.


as far as i know, none of these values need calculation unless you want to switch the % values out based on the unit's rated capacity and calculate and actual wattage value.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-26 05:27 AM . Last Modified: β€Ž2024-03-19 12:49 AM

0 Likes
0
2091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 05:27 AM . Last Modified: β€Ž2024-03-19 12:49 AM

well, let me tell you what I can based on my limited experience with these units.

On the display of the UPS is says "Load: 32%". Just this single value. But in the data.txt the 3 values for %Wout are always about 21 or 22 each. Why is that?
i believe that the front display is just telling you the load across all of the phases and then you'll see in the data log the values for each phase load. do you see anywhere in the web under the UPS tab the 32%?
Iin and Iout are only integer values. Is that enough as a measurement or is it possible to get more precise values (with comma)?
you're best bet will be to check a few SNMP OIDs for the values. they won't populate in the data log. So either the web UI or SNMP might provide decimal. I can help you with OIDs if you can use SNMP.
For Ibat there are only the values 0.0 and 1.0. What does that mean? Does 0.0 mean that the batteries where not charged in the last 10 minutes and 1.0 means that they got charged a little bit?
on units like this, this relates to the battery current. if the UPS is not running on battery, then the batteries are not outputting current, only the UPS inverter is. you should only see values populated here when the batteries are in use providing the output power and you are having a power event. this is not the battery charge.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-26 05:27 AM . Last Modified: β€Ž2024-03-19 12:49 AM

0 Likes
0
2091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 05:27 AM . Last Modified: β€Ž2024-03-19 12:49 AM

Thanks again, you are a great help!

However, I am a bit puzzled regarding the different numbers. I want to know how many kW go in and how many kW go out (and whats the loss).
Here are the average numbers in my example:

Vmin = 3 * ~402V
Vmax = 3 * ~404V
Vbp = 3 * ~403V
Iin = 3 * ~26A
Vout = 3 * ~398V
Iout = 3 * ~25A
%Wout = 3 * 22%
kVAout = 3 * ~6kVA
Vbat = ~435V
Ibat = +0.0 or +1.0

I guess one way would be to look at the %Wout values. All three phases are at about 22% (of 60kW?), which would mean 13 kW * 3 = 37 kW. Or is it just 13 kW altogether?

A second value that could be the answer is kVAout. Its 3 * ~6kVA, so about 18kW?

On the display of the UPS I see a "Load: 32%". If that means 32% of 60 kW that would be 19,2kW.

Another way for the input would be to use the average between Vmin1,2,3 and Vmax1,2,3 * Iin * 3 Phases = 32 kW
Output: Average of Vout1,2,3 * Average Iout * 3 Phases = 30 kW

In my opinion the values of the last calculation look good. 32kW go in and 30kW go out, there is a loss of about 2 kW. But whats the right calculation? Why are the others wrong and give completely different values?

Message was edited by: bugmenot20080812

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-26 05:27 AM . Last Modified: β€Ž2024-03-19 12:49 AM

0 Likes
0
2091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 05:27 AM . Last Modified: β€Ž2024-03-19 12:49 AM

hi,

i asked someone more familiar with the UPS and here is what he said:

I guess one way would be to look at the %Wout values. All three phases are at about 22% (of 60kW?), which would mean 13 kW * 3 = 37 kW. Or is it just 13 kW altogether?
The %Wout is the kW per phase - the total load% is the sum of all three phases: 22 L1 + 22 L2 +22 L3, in this case
A second value that could be the answer is kVAout. Its 3 * ~6kVA, so about 18kW?
Given the kVAout is ~6kVA, the total kVAout is ~18. Assuming the load is completely linear, the kVA = kW = ~18

On the display of the UPS I see a "Load: 32%". If that means 32% of 60 kW that would be 19,2kW.
The total load% as shown by the display is the calculated load% based on measured current supplied to the load only from the highest measured phase. For example, if L1=23%, L2=21%, and L3= 22%, the display will show "Load 23%".
Another way for the input would be to use the average between Vmin1,2,3 and Vmax1,2,3 * Iin * 3 Phases = 32 kW
Output: Average of Vout1,2,3 * Average Iout * 3 Phases = 30 kW
In my opinion the values of the last calculation look good. 32kW go in and 30kW go out, there is a loss of about 2 kW. But whats the right calculation? Why are the others wrong and give completely different values?
A more accurate way to determine the average total power consumption would be to calculate the kW per phase:

kW = (Vin x Iin x Power Factor x 1.73) / 1000, where power factor is 1 for linear loads

The value for the above equation can be x3 to give the total power used. The Vmin/max and Imin/max can be substituted, however, this will show a range of operation, not the average.

hope that helps

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of