Symmetra PX 30 kW 208V - In Forced Bypass

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra PX 30 kW 208V - In Forced Bypass
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
140
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:50 AM

0 Likes
3
1755
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:50 AM

Symmetra PX 30 kW 208V - In Forced Bypass

We have a Symmetra PX 30 kW that has been sitting for about a year and a half due to building issues (old switch gear and asbestos concerns). We finally got the work done needed to connect our unit, and after fixing a phase issue, and locating the power modules that were in another building we finally fired everything up to get a UPS in Forced Bypass State message. I checked that the switch module wasn't in forced bypass, and we don't have an external bypass, and everything looks ok from that end. I try to put the UPS online, but it comes back with Cannot Perform Function on the display.

Is there anything I'm missing, or do I have a bad switch module? How do I test it?

Thanks,

John

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:49 AM

0 Likes
0
1752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:49 AM

ok, great!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:50 AM

0 Likes
0
1752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:50 AM

Thanks for the information. It turned out the jumper was on 13+14. I also noticed the ribbon cable connected to the board was loose, and re seated the connection. Everything looks good now and UPS is online.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:49 AM

0 Likes
0
1754
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:49 AM

hi john,

i asked one of our 3 phase power techs and here is what he said:

Besides the forced bypass switch (which you have already checked - thank you), the only other thing likely to keep a system in forced bypass is if the UPS thinks the Q3 breaker of a Maintenance Bypass Panel is closed.

The sensing for a Q3 breaker is located on the Maintenance Bypass Interface Board located behind the lower rear panel of the UPS. (Since this is behind a UPS panel, you should perform this work while the UPS is de-energized, with the DC breaker off, and have the system enable switch off). On the Maintenance Bypass Interface board, there is a row of 14 jumper blocks. A standard configuration would have jumpers in pins 5+6, and 13+14. 5+6 are a normally closed sensor for Q3 switch position, and 13+14 are to indicate the presence of switch gear. Since you have no external bypass, you would want to ensure there is a jumper in 5+6, and remove the jumper in 13+14.

Once the jumpers have been changed, re apply power (AC, DC, System Enable), and your forced bypass alarm will likely be cleared. You will then likely be able to command the UPS online.

If this does not solve your issue, or you have any questions along the way please call into our three phase support team 1-800-800-4272 opt 5, then opt 4.

Lastly, I strongly suggest you work towards getting a Maintenance Bypass Panel for this UPS. While your standard repairs to the UPS (replacing batteries and power modules) do not require external bypass, or completely turning the UPS off, some things do. For example, if this is a 40K UPS frame, the static switch is not a hot-swappable module, if it ever had to be replaced or serviced, you would likely need to schedule downtime for your UPS and the connected equipment.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:49 AM

0 Likes
0
1753
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:49 AM

ok, great!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore