APC UPS Symmetra 16kv XR1 Vacant Batteries

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC UPS Symmetra 16kv XR1 Vacant Batteries
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:50 AM

0 Likes
7
1426
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:50 AM

APC UPS Symmetra 16kv XR1 Vacant Batteries

Wondering if this is an easy answer,
Just replaced 3 dead batteries in the XR1 Frame of this UPS system and it still shows as vacant batteries. Do I give it more time its been over an hour or how long does it take to show up? Do I need to do a reset?

Just ran a UPS Self test and it passed,
The UPS did register the new Charge and Run Time numbers,
looks good on that end. Thank you for the help!

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
  • Tags:
  • apc
  • battery
  • hardware
  • management
  • network
  • network_management_card
  • smart-ups
  • snmp
  • software
  • symmetra
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:50 AM

0 Likes
0
1426
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:50 AM

Like I have been trying to say...

I replaced the entire SYBT5 module

3 out of 7 entire battery SYBT5 modules were replaced

1 out of 3 are now showing OK status because of MIM reset,

Very strange issue, Thanks for trying to help...

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:50 AM

0 Likes
0
1426
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:50 AM

which symmetra 16k is this? the beige unit or the Symmetra LX? where did you get the batteries and how did you replace them? open the module and replace individual batteries or replace the entire module?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:50 AM

0 Likes
0
1426
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:50 AM

LX

Refurbish batteries, in which the individual batteries inside the case, I am assuming this means the whole module... they are encased in a frame and therefore replaced 3 module out of 7 because they were dead.

APC SYBT5 Symmetra LX Battery Module

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:50 AM

0 Likes
0
1426
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:50 AM

i'd see if you can confirm for sure what was replaced and from where - did they open the case and replace the individual batts or get a entirely new SYBT5. it would definitely help so we can see what's going on here.

do you have the serial number off of the refurbished module? the first few digits? something like QD0234?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:50 AM

0 Likes
0
1426
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:50 AM

I got one to state OK status

did this by getting lucky with resetting the MIM...

no one else seems to have such issues, It stumped the tech support rep.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:50 AM

0 Likes
0
1426
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:50 AM

ok, i guess i misunderstood when you said "modules." sorry.

What slots on the right hand side are the units that are not working in versus the ones that are? did you have a case number or ticket # from support so i could take a look and see if there's anything else we can try?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:50 AM

0 Likes
0
1426
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:50 AM

well, each IM does manage some of the batteries. that could be an issue. you should have replaced the entire SYBT5 module and not just batteries inside of it since the SYBT5 has intelligence. if that was not replaced, it could cause a similar issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:50 AM

0 Likes
0
1427
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:26 AM . Last Modified: ‎2024-03-19 12:50 AM

Like I have been trying to say...

I replaced the entire SYBT5 module

3 out of 7 entire battery SYBT5 modules were replaced

1 out of 3 are now showing OK status because of MIM reset,

Very strange issue, Thanks for trying to help...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore