SERIOUSLY? Does APC UPS RM series have NO SHORT CIRCUIT protection at all?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SERIOUSLY? Does APC UPS RM series have NO SHORT CIRCUIT protection at all?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:10 AM . Last Modified: ‎2024-03-07 03:27 AM

0 Likes
3
2313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:10 AM . Last Modified: ‎2024-03-07 03:27 AM

SERIOUSLY? Does APC UPS RM series have NO SHORT CIRCUIT protection at all?

Hi. 

Yesterday I experience a very traumatic situation with a rack mounted APC Smart-UPS 1500 RM installation that I would love to share and understand.

An apparently faulty power supply interlock cable, doubtfully rated 10A, started to seriously spark, smoke and then burn the PVC interlock isolator. 

Almost immediately mains differential circuit breaker was triggered, what interrupted UPS mains but NO PROTECTION WAS TRIGGERED FROM THE UPS, which continued to provide electricity to the already sparked, smoked and burnt cable. 

izm1YmjfBSKW8puULCC8BQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpegizm1YmjfBSKW8puULCC8BQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

I was lucky enough to be nearby and saw the whole thing from a 2 meters distance, I doubt for at least 5 seconds trying to understand what was going on and jumped to the UPS front siding panel to MANUALLY INTERRUPT UPS OPERATION!

I'm totally sure the interlock cable was to blame here, maybe acting as a fuse or just faulty, but I was more than extremely worried about NO F. PROTECTION WAS TRIGGERED BY THE UPS itself until it could either burn the whole place down to ashes or run out of battery juice.

I have several monitoring services through the APC UPS data port and, even though I understand they are not updated on-second-basis, power consumption does not show any kind of trend that would imply a dramatic load increase anywhere. UPS Load was under the 15%

I have had an implied understanding that UPS, APC or not, do have internal short circuit protections, overload protection and such kind of security features, but clearly It does not appear to. 

What am I missing here?   

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:10 AM . Last Modified: ‎2024-03-07 03:26 AM

0 Likes
0
2311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:10 AM . Last Modified: ‎2024-03-07 03:26 AM

Hi Robert - 

You do not mention which Smart-UPS 1500 rackmount you are using, but yes, all Smart-UPS feature either breakers or internal fuses on the output of the UPS in case of an overload or short circuit scenario.

On this SMT1500RM2U for instance, you will see a pop out circuit breaker labeled "Push to Reset" to the left of the outlets: 

46w%2BPPrDfpDYc6Q80cSIYw%3D%3D.jpeg46w%2BPPrDfpDYc6Q80cSIYw%3D%3D.jpeg

In addition, larger units will have multiple output breakers as well as an input breaker. All Smart-UPS are UL listed and are designed to meet local and national electric code. Line Interactive units (SU, SUA, SMT, SMC, SMX, etc) also feature an equipment protection policy in case the UPS is somehow unable to protect an attached load from damage due to a power event.

Without knowing the exact sequence of events and configuration, I can't give you a definitive answer as to why your breaker did not trip. Given the severity of the issue, I would recommend contacting our tech support team for further assistance.

thanks

Liam

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:10 AM . Last Modified: ‎2024-03-07 03:27 AM

0 Likes
0
2311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:10 AM . Last Modified: ‎2024-03-07 03:27 AM

Let's drive this on a different direction:

In case a power supply fails and gets shorted, which had happened to me several times in the past and gets to rarely occur nowadays, which UPS protection should be triggered? 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:10 AM . Last Modified: ‎2024-03-07 03:26 AM

0 Likes
0
2312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:10 AM . Last Modified: ‎2024-03-07 03:26 AM

Hi Robert - 

You do not mention which Smart-UPS 1500 rackmount you are using, but yes, all Smart-UPS feature either breakers or internal fuses on the output of the UPS in case of an overload or short circuit scenario.

On this SMT1500RM2U for instance, you will see a pop out circuit breaker labeled "Push to Reset" to the left of the outlets: 

46w%2BPPrDfpDYc6Q80cSIYw%3D%3D.jpeg46w%2BPPrDfpDYc6Q80cSIYw%3D%3D.jpeg

In addition, larger units will have multiple output breakers as well as an input breaker. All Smart-UPS are UL listed and are designed to meet local and national electric code. Line Interactive units (SU, SUA, SMT, SMC, SMX, etc) also feature an equipment protection policy in case the UPS is somehow unable to protect an attached load from damage due to a power event.

Without knowing the exact sequence of events and configuration, I can't give you a definitive answer as to why your breaker did not trip. Given the severity of the issue, I would recommend contacting our tech support team for further assistance.

thanks

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

yori
yori
Cadet

Posted: ‎2024-08-26 08:21 AM

0 Likes
0
934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-26 08:21 AM

Hi @BillP 

 

I got my UPS BVX120LI-MS last week. does it have short circuit or overload protection? I don't see any circuit breaker button on my UPS

 

And if it does, what will the model do if short circuit or overload happens?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of