Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

SC420 does NOT beep

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SC420 does NOT beep
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
cpufan_apc
Crewman cpufan_apc
Crewman

Posted: ‎2021-06-30 10:29 PM

0 Likes
1
660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 10:29 PM

SC420 does NOT beep

This was originally posted on APC forums on 4/23/2016


Hi guys,

a complete UPS noob here - I am working with computers for more than 20 years but never needed a UPS up till now. I am setting up a FreeNAS and I've just bought today a used SC420I. I know it's on the small side but it was cheap and the battery seems to be brand new.

I was reading stuff on this site and others, downloaded the PowerChute sw, also the manual and looked for a smart signalling cable. So I am pretty much equipped 😉

When I've got home with this beauty I cleaned it, checked the battery connections and the voltage (13.2V) and it seemed quite a new battery. I also powered up the unit and hooked up a PC I am currently servicing. All good 'online' LED is green. After cutting off the power it is still good and it happily runs on battery for more than half an hour (it didn't go flat I just got bored and switched the power back on).

The problem is when on battery the unit does NOT beep. Is it right? It supposed to beep according what I've read. Could it be that it switched off through PowerChute?

And this leads us to my second question. If I want to test the UPS through my ThinkPad (server is not running yet) and check the settings then which PowerChute would I need? Agent/Server/Console? I mean just to connect and see the settings on the UPS (and not administering other PCs or servers)

Question #3 Which cable should I use between the laptop and the UPS and how to connect them? On the site there is the 940-0024 which is quite straightforward - apart from the fact that on the TP there is no serial port - but what to do with the AP940-1525A? Does the serial bit go to the UPS and the RJ45 to the TP or vice versa? I reckon it is the latter which case I still don't have a serial port on the TP.

I know they seem to be pretty dumb questions for a UPS pro but they are not covered in the user manual embarassed

I would appreciate any help, thanks guys.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
UnexpectedBill_apc
Captain UnexpectedBill_apc
Captain

Posted: ‎2021-06-30 10:29 PM

0 Likes
0
659
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 10:29 PM

This was originally posted on APC forums on 4/24/2016


The SC420 supports having its alarm beeper shut off in software and someone may have done exactly that. Pressing the power button should produce a short beep as a response. By default it would beep when running on the battery.

If you don't get that short beep, it's possible that someone physically removed the beeper from inside the UPS.

Regarding monitoring software, you have a few options. Despite its low end status, the SC420 is still a Smart-UPS and as such, it speaks the widely supported UPSlink (or "APC Smart") protocol. You can use any of apcupsd, the long ago discontinued PowerChute Plus, or PowerChute Personal Edition to monitor, test and control the UPS. Or you can simply communicate with the unit by using the UPSlink protocol from within a terminal emulator, which might be the best thing to do if all you want to do is test it out. (The settings to use are a 2400 bit per second communication rate, 8 data bits, no parity, one stop bit and no flow control. Hyperterminal as included with Windows XP and prior works fine. If you are running a newer version of Windows that does not include Hyperterminal, you can use a program such as PuTTY instead.)

APC has documentation covering UPSlink very well on their web site. A quick search ought to turn up a fairly comprehensive PDF manual explaining all the commands.

Since you are just getting started, I would recommend PowerChute Personal Edition or PowerChute Plus (if you can find it -- I believe it's still on the APC FTP site somewhere).

When you get your FreeNAS running, I believe they still package software to monitor your UPS and ensure a safe shutdown of the server. The original FreeNAS (now known as NAS4Free) definitely included such software and it was very easy to configure.

Another program you may want to look up is APCfix. Despite the name, this is not an official APC utility. Its primary purpose is to reset a value known as the "battery constant". If you are sure your unit has a new battery, you will want to do this. That way you can be sure the unit won't shut down before the battery has truly become empty. This program's web site is in Russian, but it's still pretty easy to figure out what to download. (The program itself runs in English.)

The cable you want to use is the 940-0024. Variants with a letter suffix such as A, B, C or D are simply revisions to this cable and will work in the same way. If your laptop hasn't got an RS232 serial port, a USB to serial adapter will generally work just fine. The 940-1525 cable is for a different application and won't work with your SC420. You can buy the cable from APC, make one yourself, buy a cable from a third party or buy a used cable.

I have a much older Smart UPS 420 and it is an excellent UPS. I use it to back up power to my connectivity equipment, something that it will easily do for more than an hour and a half.

Hopefully this post has been helpful. Please feel free to mark it as such if that is the case. And don't hesitate to ask any other questions you might have.

See Answer In Context

Reply
Share
Reply 1
UnexpectedBill_apc
Captain UnexpectedBill_apc
Captain

Posted: ‎2021-06-30 10:29 PM

0 Likes
0
660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 10:29 PM

This was originally posted on APC forums on 4/24/2016


The SC420 supports having its alarm beeper shut off in software and someone may have done exactly that. Pressing the power button should produce a short beep as a response. By default it would beep when running on the battery.

If you don't get that short beep, it's possible that someone physically removed the beeper from inside the UPS.

Regarding monitoring software, you have a few options. Despite its low end status, the SC420 is still a Smart-UPS and as such, it speaks the widely supported UPSlink (or "APC Smart") protocol. You can use any of apcupsd, the long ago discontinued PowerChute Plus, or PowerChute Personal Edition to monitor, test and control the UPS. Or you can simply communicate with the unit by using the UPSlink protocol from within a terminal emulator, which might be the best thing to do if all you want to do is test it out. (The settings to use are a 2400 bit per second communication rate, 8 data bits, no parity, one stop bit and no flow control. Hyperterminal as included with Windows XP and prior works fine. If you are running a newer version of Windows that does not include Hyperterminal, you can use a program such as PuTTY instead.)

APC has documentation covering UPSlink very well on their web site. A quick search ought to turn up a fairly comprehensive PDF manual explaining all the commands.

Since you are just getting started, I would recommend PowerChute Personal Edition or PowerChute Plus (if you can find it -- I believe it's still on the APC FTP site somewhere).

When you get your FreeNAS running, I believe they still package software to monitor your UPS and ensure a safe shutdown of the server. The original FreeNAS (now known as NAS4Free) definitely included such software and it was very easy to configure.

Another program you may want to look up is APCfix. Despite the name, this is not an official APC utility. Its primary purpose is to reset a value known as the "battery constant". If you are sure your unit has a new battery, you will want to do this. That way you can be sure the unit won't shut down before the battery has truly become empty. This program's web site is in Russian, but it's still pretty easy to figure out what to download. (The program itself runs in English.)

The cable you want to use is the 940-0024. Variants with a letter suffix such as A, B, C or D are simply revisions to this cable and will work in the same way. If your laptop hasn't got an RS232 serial port, a USB to serial adapter will generally work just fine. The 940-1525 cable is for a different application and won't work with your SC420. You can buy the cable from APC, make one yourself, buy a cable from a third party or buy a used cable.

I have a much older Smart UPS 420 and it is an excellent UPS. I use it to back up power to my connectivity equipment, something that it will easily do for more than an hour and a half.

Hopefully this post has been helpful. Please feel free to mark it as such if that is the case. And don't hesitate to ask any other questions you might have.

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc