Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:02 PM . Last Modified: 2024-03-07 12:01 AM
Hi! I've always noticed that the runtime on the NMC and Hyperterminal will not always be equal to the actual runtime of a UPS. I have an SURT2000RMXLI, One external battery pack and an NMC (AP9630). The Load is at 90% (I used a load bank set to PFC=1) and the runtime show by the NMC and Hyperterminal is at 18minutes. When I run a pull plug test, it took 24 minutes until the UPS turned off. I would like to know if this is normal and how accurate is NMC and UPS in calculating the runtime?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:02 PM . Last Modified: 2024-03-07 12:01 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:02 PM . Last Modified: 2024-03-07 12:01 AM
The NMC has nothing to do with calculating runtime, it simply reports what the UPS tells it. The runtime estimation is performed by the UPS, and it is an estimation rather than a calculation. The problem is the runtime will vary depending on battery age, condition, and even temperature on the day. The UPS does a fairly good job of tracking battery condition over life and it can put together a reasonable estimate of runtime performance, but if you understood the variables involved you'd see it's all very handwavy. One thing it does try very hard to do is not overestimate runtime, so it'll always try to err on the conservative side.
It's not an exact science and the behaviour of SLA batteries (particularly under extreme loads) can be fairly hard to accurately model, particularly as they age.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:02 PM . Last Modified: 2024-03-07 12:01 AM
Hi Brad,
Thank you for helping out in my query.
Kind regards,
JC