Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Smart-UPS 3000 RM on battery load is 3 times higher than on power supply load?
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3009:01 PM. Last Modified: 2024-03-0712:01 AM
Smart-UPS 3000 RM on battery load is 3 times higher than on power supply load?
Hi all I have an old Smart-UPS 3000 RM. I replaced the battery and tried to perform a self test. The ups shut down immediately with the events UPS: The load exceeds 100% of rated capacity | UPS: The output power is turned off.The output power is turned off due to an overload.
I reduced the load down to 27% (starting from 50%) and now the ups passes the self test. During the self test the load goes up to 100% and the overload led sometimes flashes.
Is it normal this behaviour i.e. 27% when plugged and 100% when on battery? It does not make any sense to me: the reported Runtime Remaining could be 3 time higher than expected! If I see 27% load on supply I would expect almost the same when on battery.
Can someone explain me why when the ups on battery the load is 100% while when plugged into mains the load is 27%? Or maybe my ups is damaged?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3009:02 PM. Last Modified: 2024-03-0712:01 AM
Hi,
The UPS is not reading the load properly when on battery indicates an internal fault. Based on the serial number the UPS is 12 years old so our recommendation is to replacing the UPS.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3009:02 PM. Last Modified: 2024-03-0712:01 AM
Hi,
The UPS is not reading the load properly when on battery indicates an internal fault. Based on the serial number the UPS is 12 years old so our recommendation is to replacing the UPS.