Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Symmetra lx battery frame fault error code e0

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra lx battery frame fault error code e0
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 09:02 PM . Last Modified: ‎2024-03-07 12:01 AM

0 Likes
4
3207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:02 PM . Last Modified: ‎2024-03-07 12:01 AM

Symmetra lx battery frame fault error code e0

I have Symmetra lx 16k with 1 xr frame. When I replace all xr frame battery, xr frame fault with e0.
After that I replace all battery inside main unit and connect the xr frame again. But the error code e0 came again on xr frame. The UPS shown the actual dc voltage is148v. Any suggestion? Pls help

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • code
  • e
  • error
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 09:02 PM . Last Modified: ‎2024-03-07 12:01 AM

0 Likes
0
3205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:02 PM . Last Modified: ‎2024-03-07 12:01 AM

Hi Simon, 

What I would like to have you do is swap the batteries between the main UPS frame and the XR frame and then measure the voltage. If the voltage changes, then we can most likely say one of the batteries is causing this and can start pulling batteries one at a time until we find the culprit. If the voltage stays the same then we know it is another issue, most likely the XR frame itself. In that case, we would want to disconnect all the batteries in the XR frame and the frame should stay lit. If the frame goes dark then we know the frame is not connected properly to the main UPS frame. It's just process of elimination at this point. 

Also, about the IMs. The way the LEDs work is as follows, from left to right:

Green-IM in control, Red-Fault, Yellow-System Ok, Green-Bypass, Green-Power On. 

The main intelligence module is actually the bottom module, and the redundant is the one on top. So are you saying the UPS is reporting the RIM is in control? 

Nicole 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 09:02 PM . Last Modified: ‎2024-03-07 12:01 AM

0 Likes
0
3205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:02 PM . Last Modified: ‎2024-03-07 12:01 AM

Hello, 

An E0 error on the Symmetra LX battery frame occurs when the battery bus voltage measured by the main intelligence module and the battery bus voltage measured by the XR communication card in the XR frame differ by more than 3 volts DC. 

Possible causes of this are: faulty fuses on the XR frame, bent/broken pins on the battery power cable connecting to the XR frame, the power cable not be installed fully or not connected properly, a problem with the DC bus of the XR frame or the main UPS frame, or incorrect readings by the main intelligence module or the XR frame comm card. 

Please provide me with the following information so we can try to figure out the issue:

What is the battery voltage readings reported by the UPS in the status menu when the XR frame is connected and when it is disconnected? 

If you have a volt meter, what is the voltage measured at the Anderson connector at the end of the power cable of the XR frame? Voltage of the Anderson connector on the UPS frame?

Do you have any other XR frames connected to this UPS? 

Check the Anderson connector for any bent pins.

Reseat the communication card on the XR frame. 

Regards, 

Nicole 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 09:02 PM . Last Modified: ‎2024-03-07 12:01 AM

0 Likes
0
3205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:02 PM . Last Modified: ‎2024-03-07 12:01 AM

Nicole,

Voltage 149.2 which connect xr frame

Voltage 149.4 which disconnect xr frame

Actual voltage I measure :

UPS frame is 136.6v, xr frame is 137v

MIM LED status from left to right : off, orange with flash, green

RIM LED status from left to right : green, orange, green

Thx

Simon

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 09:02 PM . Last Modified: ‎2024-03-07 12:01 AM

0 Likes
0
3205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:02 PM . Last Modified: ‎2024-03-07 12:01 AM

Should be RIM LED status from left to right : green, orange with flash,green

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 09:02 PM . Last Modified: ‎2024-03-07 12:01 AM

0 Likes
0
3206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:02 PM . Last Modified: ‎2024-03-07 12:01 AM

Hi Simon, 

What I would like to have you do is swap the batteries between the main UPS frame and the XR frame and then measure the voltage. If the voltage changes, then we can most likely say one of the batteries is causing this and can start pulling batteries one at a time until we find the culprit. If the voltage stays the same then we know it is another issue, most likely the XR frame itself. In that case, we would want to disconnect all the batteries in the XR frame and the frame should stay lit. If the frame goes dark then we know the frame is not connected properly to the main UPS frame. It's just process of elimination at this point. 

Also, about the IMs. The way the LEDs work is as follows, from left to right:

Green-IM in control, Red-Fault, Yellow-System Ok, Green-Bypass, Green-Power On. 

The main intelligence module is actually the bottom module, and the redundant is the one on top. So are you saying the UPS is reporting the RIM is in control? 

Nicole 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore